    33CS Carrier VVT System Outside Air Sensor Specs

    I was wondering if anyone knows what thermistor type is used for the outside air temperature on a older generation III Carrier VVT system. I am having a hard time with our vendor with locating one.

    Thanks!


    Sent from my iPhone using Tapatalk
    J. King

  2. #2
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    697
    Post Likes
    I don't know about the OA sensors, but the room and duct sensors are not thermistors.
    UA LU 562

  3. #3
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    54
    Post Likes
    carrier has been using 10k type 2 thermistors for a long time. hold tite I am looking up the docs.

  4. #4
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    54
    Post Likes
    Gen 3 should be 20k type 2 thermistors for remote sensor, duct, and oat, 3v comfort id and newer all use the 10k type 2.

  5. #5
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,052
    Post Likes
    Thread Starter
    Quote Originally Posted by Cool breeze 38 View Post
    Gen 3 should be 20k type 2 thermistors for remote sensor, duct, and oat, 3v comfort id and newer all use the 10k type 2.
    Thank you very much that helps out! I couldn’t find it anywhere in the VVT documentation I had. I appreciate it.