    Trane RTAA3704 will not start

    Checked flow switch and Remote start stop. Unit is in local mode. checked ambient sensor and it is faulty. Added 10Kohm sensor. OAT now reading 77 deg.
    Unit still will not start. This is for a high school and graduation is tomorrow.

  2. #2
    Join Date
    Apr 2014
    Location
    York PA
    Posts
    19
    Post Likes
    What code is the display showing? Is it flashing?

    Sent from my SM-G930V using Tapatalk