Thread: cooling degree days for commercial building

  1. #1
    Join Date
    Mar 2018
    Posts
    10
    Post Likes

    cooling degree days for commercial building

    hello

    i am trying to estimate the energy savings in the interior mall , (arcade & attrum) of a shopping center from seting up the cooling setpoint thermpurture of rooftop packaged units , the zone im studing is surrounded by (conditioned)retail stores witch im not including in the study,the roofs & ground are not insulated, the internal loads & solar gains are very importante.

    So my question is can i use the variable base degree day methode to estimate the savings by reducing the cooling load when seting up cooling set point?

    I performed a regression analyses i found good correlation between HDD & the electrical consumption , but no correlation between the CDD & the Electrical consumption .

  2. #2
    Join Date
    Feb 2019
    Posts
    8
    Post Likes
    How to Calculate Cooling Degree Day (CDD)
    There are several ways to calculate CDD. The more detailed a record of temperature data, the more accurately the CDD can be calculated.

    1. Subtract 65 from the average of a day's high and low temperatures. For example, if the day's average temperature is 75o F, its CDD is 10. If that day's average is below 65, the result is set to zero. If every day in a 30-day month had an average temperature of 75o F, the month's HDD value would be 300 (10 x 30). The nominal settlement value for that month's weather derivative contract would, therefore, be $6,000 (300 x $20).

    2. Subtract 65 from each half-hourly temperature reading, with the provision that negative values be set to zero, sum the result and divide by 48 (48 half-hours in a day). Then sum that value over 30 (for a 30-day month) and multiply by $20. If a given day's value is less than or equal to zero, that day has zero CDD. But if the value is positive, that number represents the CDD on that day.

    For all methods, if the value for any given day is less than or equal to zero, that day has zero CDD. But if the value is positive, that number represents the CDD number of that day.

  3. #3
    Join Date
    Mar 2019
    Posts
    12
    Post Likes
    Are you a professional yourself or taking someone else help?

  4. #4
    Join Date
    Mar 2018
    Posts
    53
    Post Likes
    Yes, you can use degree days method.

    If you don't have good correlation between the CDD & the Electrical consumption, try and find another variable to add into the regression analysis.

  5. #5
    Join Date
    Jul 2014
    Posts
    455
    Post Likes
    Another way to go is to use a Chiller assessment tool. Contact your local JCI rep. and request them to send the Yorkworks CE software (requires registration). Yorkworks CE is a suite of software. The one to use is YorkCalc. Within YorkCalc you would select 'Unitary' then 'Rooftop'. Plug in all the data and run a model. Change to a new setpoint and run the model. Lets you know all the energy consumption + more.
    Bit a of a learning curve (like with all s/w). See attached.
    Attached Images Attached Images

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •