    convert geo to air ?

    I have a long time customer. High acid well water is all he has for the geo units. Most often the failures have been heat exchangers failing due to the water. He refuses to treat anything but the domestic use water for acid.

    The crawlspace unit isn't so much a problem but the attic unit has failed twice and flooded the house. No wait; only one was a HX failure - the other was a polybutylene tubing failure.

    The present attic unit is 15 years old and fortunately the latest HX failure was in - flooded the compressor and not the house.

    I would prefer to replace with air cooled and reduce the customer's risk.

    His question is: what air cooled HP's efficiency rating would most closely duplicate the efficiency / cost of operation of the geo system?

    So that is my question too. <g>
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  2. #2
    Join Date
    Oct 2014
    Location
    Columbus, Ohio
    Posts
    1,507
    Post Likes
    The only thing that comes remotely close to open loop geo in terms of efficiency is ductless inverter. Unless you want to hook his geo units up to a cooling tower instead, but then you still need water treatment.

  3. #3
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Thread Starter
    Sure; but the point is to get the water out of his second floor attic. The last time it leaked the repair cost was over $100K <g>

    PHM
    ------



    Quote Originally Posted by rjk_cmh View Post
    The only thing that comes remotely close to open loop geo in terms of efficiency is ductless inverter. Unless you want to hook his geo units up to a cooling tower instead, but then you still need water treatment.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  4. #4
    Join Date
    Oct 2014
    Location
    Columbus, Ohio
    Posts
    1,507
    Post Likes
    Another option would be to use a water-cooled condensing unit in the basement or crawlspace, and pipe the refrigerant up to the attic, if he wants to keep the geothermal aspect. Like so: https://www.carrier.com/residential/...heat-pumps/gz/ or perhaps https://www.bosch-climate.us/product...del-split.html
    It seems odd that he wouldn't want to treat the water, and instead spend big bucks on HX replacements every several years.

  5. #5
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Thread Starter
    Thanks! That is an excellent idea!

    And, except for the added cost of a lineset, the equipment costs are about the same.

    PHM
    -------




    Quote Originally Posted by rjk_cmh View Post
    Another option would be to use a water-cooled condensing unit in the basement or crawlspace, and pipe the refrigerant up to the attic, if he wants to keep the geothermal aspect. Like so: https://www.carrier.com/residential/...heat-pumps/gz/ or perhaps https://www.bosch-climate.us/product...del-split.html
    It seems odd that he wouldn't want to treat the water, and instead spend big bucks on HX replacements every several years.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  6. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Can you hook up a Heat Pump condensing unit outside? Forget SEER ratings they wont apply.

  7. #7
    Join Date
    May 2018
    Location
    Phoenix Az.
    Posts
    9
    Post Likes
    Have you thought about adding a small flat plate heat exchanger. The heat exchangers are typically made out of 316 stainless steel so the acidic water should not affect the integrity of the heat exchanger. Then all you would need is a small Taco or B&G circulating pump for the secondary side. Just a thought...

  8. #8
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Thread Starter
    I have to consider that this entire job will be done with me working though someone else's hands. <g> My associate is not me - and apparently does not want to become me.

    I love your idea and would happily use it - but anything out of the ordinary makes my associate get 'deer in the headlights' look on his face. Hell; just the idea of replacing a geo unit has him pretty freaked out. <g>

    And besides: don't the geo makers generally use what used to be called 'marine grade' heat exchangers these days?

    PHM
    -------




    Quote Originally Posted by DewMac View Post
    Have you thought about adding a small flat plate heat exchanger. The heat exchangers are typically made out of 316 stainless steel so the acidic water should not affect the integrity of the heat exchanger. Then all you would need is a small Taco or B&G circulating pump for the secondary side. Just a thought...
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  9. #9
    Join Date
    May 2018
    Location
    Phoenix Az.
    Posts
    9
    Post Likes
    Now you got me curious about marine grade HEX. You mentioned that the HEX failed, what was the HEX made of and was that marine grade ?

  10. #10
    Join Date
    Oct 2014
    Location
    Columbus, Ohio
    Posts
    1,507
    Post Likes
    I assume "marine grade" might be titanium, or maybe cupro-nickel, both of which would usually be an upgrade option over the factory stainless or copper options. Some might include it by default, don't know for sure though.

  11. #11
    Join Date
    May 2006
    Location
    Raleigh,NC.
    Posts
    573
    Post Likes
    considering the amount of possible future damage, closed loop, if he wants high efficiency!
    Got to spend some money somewhere !!!
    remember, with electronics; when its brown,its cooking and when its black, its done!!!

  12. #12
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    The guy who just paid 100k in water damage is worried about the efficiency disparity between geothermal and air source heat pumps? :grin:

    Sent from my SCH-I545 using Tapatalk

  13. Likes rjk_cmh liked this post.
  14. #13
    Join Date
    Oct 2014
    Location
    Columbus, Ohio
    Posts
    1,507
    Post Likes
    Quote Originally Posted by shellkamp View Post
    The guy who just paid 100k in water damage is worried about the efficiency disparity between geothermal and air source heat pumps? :grin:

    Sent from my SCH-I545 using Tapatalk
    Correction, the guy who's insurance most likely paid for the damage...

  15. #14
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Thread Starter
    I wish I knew.

    I install the now-failed FHP unit about 15 years ago. In about the same time frame I remember some long talks with FHP Sales and with FHP Engineering about this exact issue.

    Because I replaced the previous unit due to a failed HX. <g>

    Way-back-when the "marine grade" HX's (which I think were cupronickel) were an option on FHP units. But apparently contractors did not often choose the option because it increased their equipment cost - so FHP decided to make All their units with the better HX to better serve their reputation and warranty costs.

    And there is said to be no M/S # on the unit - so I can't check that way either.

    PHM
    --------


    Quote Originally Posted by DewMac View Post
    Now you got me curious about marine grade HEX. You mentioned that the HEX failed, what was the HEX made of and was that marine grade ?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  16. #15
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes

    convert geo to air ?

    What would the seer rating be for an older geo unit? 20-24 seer? He could get atleast 19seer with air to air


    Sent from my iPhone using Tapatalk

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •