    Trane EXV tech view

    I'm currently working on a series R chiller I had a bad TXV take out a lot of my binded sensors I got back my sensors but exv failed. I believe I have downloaded the correct Tech View off of trains website. The exv is different the old type is the black Global wire and Sporlan valve. There's been a change now Sporlan with a yellow wire module. When I try to bind I get a message exv not selected. Does the tech view select the right one? Or is there a drop-down menu or driver I need to install?

  2. #2
    Join Date
    Apr 2018
    Posts
    25
    Post Likes
    You have to access the configuration menu and select the new type of EXV.