Thread: Interesting issue

  1. #21
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    I had one very similar several years ago, for me it ended up being a dirty connection between the thermocouple end where it screws into the gas valve. Dirty meaning it had some corosion in the gas valve connection. Never had a problem after cleaning the connection. I used a pipe cleaner to get in side, made sure it was good and snug into the gas valve. Tstat area stayed warmer than heater location at night. Heater near an outside wall. T stat was on a pole in the middle of the room. The only thing I could think of why it worked during the day vs going out at night is the ambient area near the heater got cooler at night, Figure the thermocouple contracted a little more at night and it lost a good solid connection.

  2. Likes DavidDeBord liked this post.
  3. #22
    Join Date
    Mar 2018
    Location
    Kansas Flatlands
    Posts
    833
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    What is the manifold gas press? What is the MV reading? Percussion problem distinguishing the pilot flame?
    Was the gas valve replaced with the exact OEM replacement? Slow open type?

  4. Likes DavidDeBord liked this post.
  5. #23
    Join Date
    May 2016
    Location
    Toronto, CAN
    Posts
    154
    Post Likes
    I d be looking the exchanger over very well. When they heat up the cracks open and blow out the pilot. I have seen that before a few times

  6. #24
    Join Date
    May 2017
    Location
    Brooklyn
    Posts
    106
    Post Likes
    I suggest a Y86 conversion kit if possible and be done with it if you factored out all other draft, or HX issues.

  7. #25
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    Verify correct inlet pressure, on a cold nigh,t when the most heaters are on, at the trouble unit.
    UA Local 32 retired as of Jan 2020

  8. Likes DavidDeBord liked this post.
  9. #26
    Join Date
    Jun 2017
    Location
    Portland, OR(Previous: Arizona, Texas, Oklahoma)
    Posts
    71
    Post Likes
    Check your manifold gas pressure on both units please

  10. #27
    Join Date
    Jun 2017
    Location
    Portland, OR(Previous: Arizona, Texas, Oklahoma)
    Posts
    71
    Post Likes
    Quote Originally Posted by buford View Post
    Verify correct inlet pressure, on a cold nigh,t when the most heaters are on, at the trouble unit.
    Agreed. While your manometer is hooked up to the inlet, turn on other gas appliances and see if it maintains pressure. Who knows maybe they did a bad load calc on their gas line?

  11. #28
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    7,304
    Post Likes
    Quote Originally Posted by joemach View Post
    No input guys? Pilot went out again last night.
    It's odd that it's only happening at night, especially " (5 times a week)".

    How is this unit Vented? From what you've supplied, I'm assuming that this is a"Standing Pilot", & not Spark, or HSI.

    Have you checked the thermocouple, as far as position, being burnt, properly mounted to the Gas Valve etc.?

    How is the Flue Terminated? What about the Flue Pipe, ... any Birds nests, or Illegal Immigrants hiding out in it?

  12. #29
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    7,304
    Post Likes
    Quote Originally Posted by Makeitcold View Post
    I’ll admit I haven’t worked on a green houses but have found with propane that you will usually find out about regulator issuses or moisture contamination once it drops below freezing at night but will work and test fine when you show up the next day( when it’s warmed up). You may have just enough pressure to run one unit at night or maybe that unit is getting moisture in it at night and freezing, snuffing the pilot. Could be a bunch of things but I like Hvac Marc’s idea best. Eliminates all the problems that go with pilot lights( including possibly your issues) and at whatever your customer pays for propane will pay for itself decently quickly. Payback is even quicker if it’s a business(florist?) and you count lost product, which I would. If nothing else you may have to show up and test the system when it’s in the 20’s and see what’s diifrent at that temp
    -------------

    I was going to say "Second Stage Regulator", but Makeitcold, kinda beat me to it.

    I've seen Second Stage Regulators Lock Up, &/or run out of wack, due to moisture that became lodged in them. I've also seen Second Stage Regulators Fail, because they were Old, & just didn't want to work very well when it got below freezing.

  13. #30
    Join Date
    Dec 2013
    Location
    TN
    Posts
    266
    Post Likes
    What all runs of propane on this property thats shared with the tank?

  14. #31
    Join Date
    Jan 2009
    Posts
    289
    Post Likes
    We have had similar problems like this for the last couple of years with Rego brand second stage regs. With no load, they creep up to 20” and higher, then when the equipment fires, they drop down below 5”, and the equipment locks out. I’m not saying this is what is going on here, but just putting it out there. We have changed many Rego regs over the last 18 months.


    Sent from my iPhone using Tapatalk
    They will soon forget how long it takes, but they will always remember the quality.

  15. Likes DavidDeBord liked this post.
+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •