    Instead of a practical exam if an engineer wants to be certified he should be required to balance jobs and submit a balance report on the jobs. They could lie and submit a report someone else did but if ask a few questions it wouldn't be too hard to figure out if they knew what they were doing.
    I would have told the engineer to go get a can of soda so we could try his idea and while he was gone would have sped the fan up.
    No man can be both ignorant and free.
    Thomas Jefferson

  2. #22
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,780
    Post Likes
    Quote Originally Posted by bradluke0 View Post
    In my opinion the practical exam is very necessary , as one purpose of the CP is to be able to teach others how to balance . I know many engineers who could pass the AABC exam and the written portion of the NEBB exam who couldn't balance a dog house . Funny engineer story …..we were 20% low on air on a decent size AHU . The engineer wanted us to prop the fan access door open with a soda can ( end to end ) and see how much it would increase . I said "so what is this going to prove?" He said " then we will know if we can get the air or not ". I said , "So if we get the airflow are we leaving the soda can here or is someone going to stand here and hold the door open?" .
    Without fan test data, here's a guess of the engineers intent...

    Opening the fan access door is a quick way to find out two possibilities...
    1) if the upstream (to the fan) ahu dampers, ra fans, ductwork, inlets are restrictive
    2) And if restrictive can the present configuration downstream (from fan) provide design cfm.

    And opening the fan access door is a quick, low labor cost way to determine if speeding up the fan will help.

  3. #23
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    If you know the airflow and fan RPM you can easily calculate the new fan speed needed to obtain the desired airflow. All you find out by opening the door is if the fan will move more air with less total static pressure. Of course it will but the total static pressure will go up as fan speed is increased not down. The engineer didn't know what he was talking about.
    No man can be both ignorant and free.
    Thomas Jefferson

  4. #24
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,780
    Post Likes
    Quote Originally Posted by WAYNE3298 View Post
    If you know the airflow and fan RPM you can easily calculate the new fan speed needed to obtain the desired airflow. All you find out by opening the door is if the fan will move more air with less total static pressure. Of course it will but the total static pressure will go up as fan speed is increased not down. The engineer didn't know what he was talking about.
    As I said, not knowing fan data, I gave possibilities.

    If the airflow to the fan is restricted, the open door would/may provide design cfm due to reduced TSP.
    Perfect world is to know design TSP as calculated.
    Again, we are talking about a very quick test.
    Also, what if the door is opened and no change is noted? Possible restriction in SA somewhere...fire damper partially closed, system effect due to creative duct transitions that are an abortion.
    If these are present, changing fan speed will not solve the problem.
    Jogas
    Four wheel therapy, my 1968 Camaro is gone and will be missed

  5. #25
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Static pressure profiles will tell you if you have a restriction and where if you know how to do them. Part of air balance is obtaining fan date. If you open the door fan airflow will increase but that doesn't tell you if or where you have a restriction. If you have a fan curve that dips and recovers and you open the door you don't know which side of the dip in the curve you were on before you opened the door and which side you are on after you opened the door. Opening the door could also put the fan in it's unstable region or in some cases take a fan out of that region.
    Opening the door is a cheap way to screw up.
    No man can be both ignorant and free.
    Thomas Jefferson

  6. #26
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,780
    Post Likes
    Quote Originally Posted by WAYNE3298 View Post
    Static pressure profiles will tell you if you have a restriction and where if you know how to do them. Part of air balance is obtaining fan date. If you open the door fan airflow will increase but that doesn't tell you if or where you have a restriction. If you have a fan curve that dips and recovers and you open the door you don't know which side of the dip in the curve you were on before you opened the door and which side you are on after you opened the door. Opening the door could also put the fan in it's unstable region or in some cases take a fan out of that region.
    Opening the door is a cheap way to screw up.
    Agree to disagree.
    Jogas
    Four wheel therapy, my 1968 Camaro is gone and will be missed

  7. #27
    Join Date
    Aug 2019
    Location
    Central Florida
    Posts
    113
    Post Likes
    The problem with the unit was that the coil had a little higher than design pressure drop at 20-25% low of design . We first thought the coil wasn't protected properly during construction and was impacted but that wasn't the case . The coil had more fins per inch than was specified . We told the engineer the coil was the problem but he didn't buy it , hence the crazy field visit by him and the soda can debacle . I am always totally against testing things in a way that is not consistent with the intended conditions . This includes holding the fan door open , testing with dirty filters , testing with slipping belts , etc . I am also not a fan ( no pun intended ) of just traversing a unit or testing the flow on a pump and not obtaining all data on that piece of equipment . I had a guy tell me all he wanted me to do was traverse the unit as he believes he is low and he just wanted to know how much low . If he already believes he is low why wouldn't he want to know what to do next ? Without all the data you cant . Cheers .

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •