Thread: Balancing at Registers vs Plenum Dampeners

  1. #1
    Join Date
    Mar 2017
    Location
    Houston, Tx
    Posts
    47
    Post Likes

    Question Balancing at Registers vs Plenum Dampeners

    I have heard conflicting opinions on this subject so I'd like to hear what the community has to say about it. I am in Houston so we deal with high heat, high humidity. What is the proper way to adjust air flow? Pinching back registers or pinching back dampeners at the plenum?

    I have heard that if you pinch back at the registers then this creates a potential for mold growth in the duct. Any truth to this?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,732
    Post Likes
    At the take offs.

    At the registers causes noise.

  3. Likes JaySWAT, kdean1, CHILLERSVCMAN liked this post.
  4. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,732
    Post Likes
    At the take offs.

    At the registers causes noise.

  5. #4
    Join Date
    Oct 2015
    Location
    Illinois
    Posts
    964
    Post Likes
    I agree with pecmsg
    There is only one truly right way to do something, but there are thousands of wrong ways to varying degrees to do it.
    So the question is: If you don't do it right, then how wrong is it going to be???

  6. #5
    Join Date
    Mar 2017
    Location
    Houston, Tx
    Posts
    47
    Post Likes
    Thread Starter
    Is noise the only issue?

    My main concern is if there is a higher chance for forming mold if airflow is restricted at the registers?

  7. #6
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    The mold angle is bogus. There are two reasons in residential to balance at the plenum the biggest one being they will hold set point because nobody can mess with them. The other reason is noise potential but that is rarely a problem in residential. Most residential systems are low on airflow and if not the static pressure at the diffusers is almost always below 0.1 inch.

  8. Likes JaySWAT, DavidDeBord liked this post.
  9. #7
    Join Date
    Jan 2015
    Location
    Bellevue, Washington, United States
    Posts
    2,388
    Post Likes
    It's always best to balance using dampers. If you close off registers it greatly increases your noise level in the space. Also someone else can easily adjust it again and negate the work you just did.

  10. Likes JaySWAT, DavidDeBord liked this post.
  11. #8
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Making the adjustments at the take off, also will reduce duct losses in the branch runs on systems that are less then perfectly sealed


    Sent from my iPhone using Tapatalk

  12. Likes DavidDeBord liked this post.
  13. #9
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Look at a grill/register/diffuser air flow profile and how they entrain room air. They are on manufactuer's sites. By closing them the profile will be less than idea.
    I don't remember a mold issue before this. If condensation is forming at the terminal you might need to increase the fan speed so the air is a bit warmer or find the supply duct problem.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  14. Likes DavidDeBord liked this post.
  15. #10
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    7,304
    Post Likes
    I start with the Volume dampers, then the branch dampers, then complete it with the Register Dampers, in order to balance the Air flow through out the building.
    Now, in many cases, where the Installation, was never Inspected, &/or was older than 20 years, .... I've seen many a Residential Installation with out any damper control, other than the Registers.

    Another point, is that in a Mobile Home/ Modular, & RV,... The Only Damper Control is always the Registers.

    As far as "Mold Growth"? That can largely be cured with the Building Owner having the Equipment Tuned & Cleaned on a Regular Basis, (with Evap. Pan Treatment, & Condensate Drain cleaning if required.) as well as the Contractor informing the H.O., about properly inspecting & changing the Filters.
    Hos 4:6 My people are destroyed for lack of knowledge. Because you have rejected knowledge, I will also reject you, that you may be no priest to me. Because you have forgotten your God’s law, I will also forget your children.


    "You've got to Stand for Something or You'll fall for anything" (A. Tippin)


    Mat_15:24 But he answered, “I wasn’t sent to anyone but the lost sheep of the house of Israel.”

  16. #11
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    David, like you I have also worked with systems that were not adjustable. I consider a system with just a terminal adjustment to be in that class. Of course when that's all you have that's what you adjust. Even when the terminal is adjusted the flow pattern
    is in many cases a wreak. There are combo grills like the Barber Coleman that has a volume damper directly in back of the grill that has a 4 way pattern adjustment. Pricey though but good results.

    Forget mold. If condensation is an issue tweaking a grill won't fix it. The supply air is too cold or wet air is being introduced is another way. The A/C should be able to stabilize the humidity in a short time unless there is a problem.
    The air discharge should be what the supply duct is delivering.
    There was a job on Johnson Island. It's in the middle of the Pacific and I'm told is the farthest away from everywhere. They had diffusers sweating but it was because the engineer didn't spec insulation on the outside of them. The RH there is often near 100%. Try to find the source of the humidity.
    It's the room air that was humid and the condensation was on the outside.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  17. Likes DavidDeBord liked this post.
  18. #12
    Join Date
    May 2018
    Location
    Deatsvills, Alabama
    Posts
    11
    Post Likes
    I prefer at adjust at the takeoff instead of the register. If there is not a damper at takeoff then you have no other choice.

  19. #13
    Join Date
    May 2012
    Location
    Houston, Tx
    Posts
    10
    Post Likes
    I don't know who instructed you that mold growth will magically appear when cutting at the diffuser.....but I've never seen it...and I'm in Houston too! Cutting at the spin in to the main trunk will also yield less leakage than cutting at the diffuser (your building static in less duct work). Last but not least, cutting at the diffuser is noisey. Exactly what type of system is this?

  20. #14
    Join Date
    Apr 2012
    Location
    Millsboro, DE
    Posts
    181
    Post Likes
    When a system is designed there's typically an ACCA, SMACNA and/or Code requirement for branch dampers. Balancing at the outlet is usually prohibited because of the noise issues and the fact that many devices can't be locked in position. I also don't like them because they're accessible to those "cold" or "hot" occupants.

  21. #15
    Join Date
    Apr 2012
    Location
    Millsboro, DE
    Posts
    181
    Post Likes
    I have a friend who inserts round ceiling diffuser dampers in floor diffuser boots where there're no (accessible) branch dampers, says they work fine. I believe that complies with the SMACNA requirement for locking, but the additional PD scares me.

  22. #16
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Face dampers certainly are not preferable but in some cases are necessary and are generally not noisy unless the diffuser and branch duct are oversized. Most face dampers are self locking but most used in residential floors are not.
    When I ran into a diffuser with a face damper that was short of air I could get on average about 20 CFM more by removing it and I removed several.
    No man can be both ignorant and free.
    Thomas Jefferson

  23. #17
    Join Date
    Apr 2012
    Location
    Millsboro, DE
    Posts
    181
    Post Likes
    LOL! That's my last resort when all else fails: The additional 0.03" can make a big difference.

  24. #18
    Join Date
    Apr 2012
    Location
    Millsboro, DE
    Posts
    181
    Post Likes
    With today's homes running as much as 1,350+ SF/Ton, a lot of sizing issues have arisen: Manufacturers just don't make small enough stuff.

    I wrestled with how to deliver only 12 CFM to an outlet (closing a 4" branch damper and its 2-1/4x10 floor diffuser multiblade damper still gets you 15 or 20 CFM) for hours. Then a great tech I'm working with came up with a simple solution, bless him: He uses a 2" hole saw instead of cutting a 4" hole for the 4" adhesive collar, providing the ability to dial in whatever we need.

    12 CFM being the ACCA residential balancing tolerance (10 cfm x 120%) for my specing an outlet in small rooms with limited exposures to outdoors (less than 10 CFM required, no outlet - I'm sure everyone here is OK with that).

  25. #19
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    7,304
    Post Likes
    How small is that room, that only requires 10CFM Ferd?

    Are You conditioning a broom closet?
    Hos 4:6 My people are destroyed for lack of knowledge. Because you have rejected knowledge, I will also reject you, that you may be no priest to me. Because you have forgotten your God’s law, I will also forget your children.


    "You've got to Stand for Something or You'll fall for anything" (A. Tippin)


    Mat_15:24 But he answered, “I wasn’t sent to anyone but the lost sheep of the house of Israel.”

  26. #20
    Join Date
    Apr 2012
    Location
    Millsboro, DE
    Posts
    181
    Post Likes
    The 10 CFM rooms are water closets in large bathrooms (a room housing the WC, not the fixture inself) large walkin closets, mud rooms, powder rooms, pantries, etc. all with a little exposure to outdoors. Haven't done a Broom Closet yet, but I have seen two 4x10x6 serving a small WIC with no outside walls.

    400 CFM/Ton at 1,000 to 1,350 SF/Ton = 0.40 to 0.30 CFM/SF, so 25 to 33 SF.

    Thanks for asking.

    FYI: I work with one main installer, who's buying 2-1/4x10's, 4" and 5" duct in quantity.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •