Results 1 to 12 of 12
    Nov 2015
    CA
    Question BACnet IP Discover issue
    My current setup is a Jace at 4.2 and I'm my own LAN using a switch.
    I'm trying to discover a couple KMC flexstat controllers(BAC-120063CEW) the issue I'm having is they won't automatically discover. The only way I can discover them is for me to manually add them using their ip address and adding :0xBAC0 at the end. The devices are all on the same subnet for whatever reason they won't populate.
    Newbie let me know if i need to provide more information.
    Jan 2003
    Likely they are slave devices, can't auto discover them unless you get a router that does slave proxy.
    You'll have to fat finger in the device instance and mac on them or get something that can proxy them.
    Jan 2003
    This guy can act as a slave proxy.
    http://www.hvacrcontrol.com/bacnet-router/
    or are these the bacnet/ip version flexstat?
    Dec 2006
    What? Who? Where?
    IP BACnet Slaves? Never heard of such a thing.
    I would use another BACnet application to attempt a discovery. If they populate I would start looking on the Tridium side, if they don't check the configuration in the KMC devices. A Wireshark capture may shed a little light on the situation as well.
    https://hvac.io/docs/wacnet
    https://www.ccontrols.com/sd/bdt.htm
    http://www.inneasoft.com/index.php/e...ember_54892063
    http://www.chipkin.com/products/soft...cnet-explorer/
    kontrol out
    "Good" - Jocko
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Interoperability? You can't handle interoperability!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora Watch it here!
  5. Likes stanbyyourword liked this post
  6. #5
    Jan 2003
    Quote Originally Posted by kontrolphreak View Post
    lol me either. Pretty sure the ms/tp version of these are slaves.
    digging into the part number these are the IP version, so its not that
  7. #6
    Jan 2003
    Check your subnet mask on everything and make sure they all match if they are on the same subnet. That can screw up discovery but still work when directly accesed.
  8. Likes stanbyyourword liked this post
  9. #7
    May 2016
    Idk if they are like the new conquest ethernet controllers, but these new ones have an option to make them talk ethernet or to bacnet/ip. I change them to bacnet ip.
    Sent from my VS987 using Tapatalk
  10. #8
    May 2016
    Sorry cant edit my post, but heres a link to the kmc site. Then select operation guide for flexstat. Then in that pdf to pg 14. Looks as though it can be IP, Ethernet, Foreign. Id think you want it to be IP. As these ethernet ones cannot be found when Im using my bacnet ip bacstac, only found by changing it to ethernet, when they are found I change em to IP and my bacnet Ip can find all mstp stuff with a router and the regular Ip too stuff.
    Also even though they have unique IP macs, I think they still need unique Instances.
    http://www.kmccontrols.com/component...=bac-120063cew
  11. #9
    Dec 2006
    What? Who? Where?
    Quote Originally Posted by CavemanTitan View Post
    Yes they will.
    kontrol out
    "Good" - Jocko
  12. #10
    Nov 2015
    CA
    Quote Originally Posted by orion242 View Post
    I spoke to Tech Support and they aren't slave devices they said it should automatically populate I'm now waiting a call from their niagara specialist. Everything is on the same subnet mask
    Jace- 192.168.1.224 /24
    gateway: 192.168.1.1
    Kmc controller 1: 192.168.1.222 /24
    Device ID: 66
    UDP:47808
    Kmc controller 2: 192.168.1.223 /24
    Device ID:65
    UDP:47808
    I've even turned off my firewall to avoid any discrepancies.
  13. #11
    Nov 2015
    CA
    Had to delet your link due to my insuffiecient posts lol
    They have been enabled to IP.
  14. #12
    May 2019
    Hi,
    Yes Inneasoft BACnet Explorer free version (InneaBACnetExplorer) allows you to discover & explore your BACnet / IP network.
    Automatic discovery of all the BACnet/IP devices, objects and properties of your network and display all the devices and their objects in a tree view with a direct access to all their properties. Graphically display calendars and schedules.
    With the pro version (price removed) you can change the value of the properties (valve opening, switch on/off light, etc…), view and acknowledge your alarms, modify your calendars and schedules (ex: heating or cooling schedule) + Graphically display your trends...
Tags for this Thread