    Ice-O-Matic

    Can you guys school me on IOMs time delay and Low pressure switch. I worked on a unit where low pressure cutout is set at 31, but does not harvest until 22 psi. If i remember correctly, if operating correctly, shouldn't the cutout send voltage to the time delay at 31 psi? And then go into defrost however many seconds are set on the time delay? Thanks for any tips

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    22,278
    Post Likes
    Reverse acting LP Control closes on fall and timer takes over.
    Reset to 22 and shorten the timer if you want.

  3. #3
    Join Date
    Feb 2004
    Location
    Western New York
    Posts
    1,195
    Post Likes
    Check out the first part of this video from IOM. Can't do a direct link, but pull up this link and then open "ICE0325 Modular Cuber-short cycling", seventh video down.

    http://www.iceomatic.com/Service-and...hnical-Videos/
    Experience is what you have an hour after you need it.

  4. #4
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,465
    Post Likes
    The easiest way to check LP switch setpoint is to reduce solid state time delay to 1 second. Unplug water pump and watch at what pressure it goes into harvest.

    I've heard you should not adjust the LP switch to change bridge thickness. It should be the "constant". The solid state timer is what should be adjusted to get a thicker bridge.

    2 tips I've learned: 1. The pressure switches tend to develop refrigerant leaks. Like, a LOT. 2. The smaller undercounter units use a LP switch that is supposed to close higher (around 45 if I recall correctly) but they often get replaced with the regular one, which leads to massively thick sheets of ice and/or freezeups.

    Sent from my SAMSUNG-SM-G890A using Tapatalk

  5. Likes jpelagio11, UmmScott liked this post
  6. #5
    Join Date
    Oct 2012
    Location
    Where we mow our own grass
    Posts
    6,673
    Post Likes
    After the LPS opens the setting on time delay is how much longer the machine will stay in freeze before harvest. Longer time delay=thicker bridge

  7. #6
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,024
    Post Likes
    Every unit has ITS OWN initiate setpoint.

    Look it up and set it.

    The older bulky Johnson controls initiates leak alot in the bellows.

    The new control made by selco is pretty good and reliable.
    Dont let ice o matic scare u