407c??
Green tech guy.
Supply company telling me you can add this on top of r-22, but most techs say it's a retrofit, any suggestions?
Sent from my iPhone using Tapatalk
-
-
Can be added with no TXV adjustment.
Here is another post that looks into this further.
http://hvac-talk.com/vbb/showthread....g-407C-and-R22
The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.
-
Post Likes - 2 Likes, 0 Dislikes
-
Positively not! You seem to be saying that you will mix the refrigerants.
The old refrigerant must be recovered and replaced with the new refrigerant.
*********