    407c??

    Green tech guy.
    Supply company telling me you can add this on top of r-22, but most techs say it's a retrofit, any suggestions?


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,856
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Can be added with no TXV adjustment.

    Here is another post that looks into this further.

    http://hvac-talk.com/vbb/showthread....g-407C-and-R22
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  3. Likes Jettinvr6sc, weezer81 liked this post.
  4. #3
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    7,473
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Positively not! You seem to be saying that you will mix the refrigerants.
    The old refrigerant must be recovered and replaced with the new refrigerant.
    AOP Rules: Rules For Equipment Owners.

    Free online load calculator: http://www.loadcalc.net/


    There = not here. Their = possessive pronoun. They're = they are
    It's = contraction of it is. Its = the possessive form of it
    Too = also. To = expressing motion. Two = 2
    Then = after that, next. Than = indicates a comparison.
    Questions should end with a question mark "?" Statements end with a period "."

  5. Likes Gunslinger, weezer81 liked this post.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Contracting Business
HPAC Engineering
EC&M
CONTRACTOR