    Leaving IBEX, How to do so gracefully?

    Issue is: moving RTU by RTU from IBEX and I noticed that the Alerton global controller is smelling warm. Not a good sign.

    What should I be doing to keep the IBEX from crapping out before I get all the units over to the new system? Adjust voltage? Dummy resistance? or?

  2. #2
    Join Date
    Aug 2016
    Location
    Sacramento, CA
    Posts
    168
    Post Likes
    Unless you're specifically having existing devices fail the warmth of a device is not really a good indicator of potential failure unless it's too hot to touch. Especially if the devices are mounted inside the RTU instead of their own separate control cabinet.

    A few of us tech'd sites for a while and it was common for a network switch to overheat when they failed, although they'd literally be burning up. Most controllers can handle fairly extreme temperatures without possibility of failing.

  3. #3
    Join Date
    Jan 2003
    Location
    USA
    Posts
    4,869
    Post Likes
    Smelling warm...

    Once the factory smoke is released, it cannot be put back. I'd say if you can smell it, its too fricken hot and sometin amiss...
    Propagating the formula. http://www.noagendashow.com/

  4. #4
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    1,998
    Post Likes
    Thread Starter
    Normally, I'd agree on the smoke, but it was not smoking, just smelling warm, and the next day it was not smelling, but still functioning... Hmm....

    Main thing I don't want to happen is for the 26 year old head end global controller to die before I get all the systems switched over to the new system. Not overly knowledgeable on these old systems and looking for you all's wisdom to keep the old gray horse moving till I can retire her. The controller has two comm lines and by end of day tomorrow I will have one comm line, off line. Can I just disconnect that line when done and have the control still supervise the other comm line without issue?

    Appreciate any advice!

    jm

  5. #5
    Join Date
    Aug 2016
    Location
    Sacramento, CA
    Posts
    168
    Post Likes
    Controllers deal with load just like an engine would. If you put excess load on a processor (>100% capacity) and overclock it you'll wear out it out much faster than an identical unit with 30% spare capacity.

    If you can unload logic, comm lines, etc. it will put less load on the device which should extend the life.

  6. #6
    Join Date
    Feb 2005
    Location
    tracy
    Posts
    2
    Post Likes
    Alerton apex boards have a comm voltage pot for each trunk. You may need to lower pot as you reduce devices.
    Tux comm voltage works best between about 4 to 8 VDC.

  7. Likes Juan Madera liked this post
  8. #7
    Join Date
    Mar 2014
    Location
    Pittsburgh, PA
    Posts
    278
    Post Likes
    Juan,

    Alerton has a driver out for their newest global the "ACM" that allows it to communicate with IBEX controllers. You could pull out the APEX globals, install the ACMs along with their new Compass front end, and then replace the IBEX controllers with Alerton VLCs as they go bad. It would be the least painful way to phase out the IBEX controllers without emptying out your back account. This assumes that the local Alerton dealer is reputable.

    -Fish