    True roll in cooler, new condensing unit. Compressor not starting everytime

    This single door true Roll in cooler has had numerous compressor changes from another company and cap tube replacements.
    Owner wanted problem fixed permanently and gone.

    I quoted to replace condensing unit, flush evap and go with a TXV instead.
    Replaced the 134a and crap tube with new condensing unit with receiver... an AE4440Z-AA1AGB, and 1/4 ton danfoss TUA TXV valve.

    Works and cools great, superheat at compressor is 23F. Problem...
    The AE4440Z has trouble restarting sometimes after the off cycle. (Off cycle is usually 8 to 10 mins) compressor pops overload.
    Usually after the 3rd attempt it fires right up with no issue.
    Start cap is good at 300uf and well within range.
    Pulls current, 10a thru start cap when trying to start.
    Checked for voltage drop, there is 5 volt drop from 120 to 115V when attempting to start...

    Very weird.. I'm ordering new starting components under warranty anyhow but.
    What do you guys think?
    It should start everytime, its a high start torque model with the 1st 4 in the model #.

    Any ideas?Name:  20170323_135921.jpg
Views: 613
Size:  41.0 KB
    Name:  20170323_170119.jpg
Views: 654
Size:  88.7 KB
    Name:  20170323_170550.jpg
Views: 592
Size:  65.3 KB

    Sent from my SM-N920V using Tapatalk

  2. #2
    Join Date
    Mar 2008
    Location
    kansas
    Posts
    2,521
    Post Likes
    How are the points on the tstat
    Honeywell you can buy better but you cant pay more

    I told my wife when i die to sell my fishing stuff for what its worth not what i told her i paid for it

  3. #3
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    You could install a LL solenoid and make it a pump down system - that will make starting easier on the compressor.

    Sent from my SCH-I545 using Tapatalk

  4. Likes Shootskee, larryjason1972, icemeister liked this post.
  5. #4
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Is the TUA valve a hard shut off?

    Sent from my SCH-I545 using Tapatalk

  6. #5
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Thread Starter
    Quote Originally Posted by crazzycajun View Post
    How are the points on the tstat
    A12 700 was installed with the condensing unit

    Sent from my SM-N920V using Tapatalk

  7. #6
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Thread Starter
    Quote Originally Posted by shellkamp View Post
    Is the TUA valve a hard shut off?

    Sent from my SCH-I545 using Tapatalk
    No sir, I have used this valve on many other applications.

    Ive used it on an old r12 reach in that was controlled thru low pressure and it worked fine.

    Sent from my SM-N920V using Tapatalk

  8. #7
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by UmmScott View Post
    No sir, I have used this valve on many other applications.

    Ive used it on an old r12 reach in that was controlled thru low pressure and it worked fine.

    Sent from my SM-N920V using Tapatalk
    Yeah, I know, it SHOULD work fine; but it doesn't, does it? :grin:

    My gut tells me a pump down solenoid or hard shut off valve would solve this problem for sure. There may be some migration going on



    Sent from my SCH-I545 using Tapatalk

  9. Likes UmmScott liked this post.
  10. #8
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Are you controlling on a constant cut-in stat? That YOU KNOW for a true-fact is a constant cut-in thermostat?

    PHM
    --------


    Quote Originally Posted by UmmScott View Post
    This single door true Roll in cooler has had numerous compressor changes from another company and cap tube replacements.
    Owner wanted problem fixed permanently and gone.

    I quoted to replace condensing unit, flush evap and go with a TXV instead.
    Replaced the 134a and crap tube with new condensing unit with receiver... an AE4440Z-AA1AGB, and 1/4 ton danfoss TUA TXV valve.

    Works and cools great, superheat at compressor is 23F. Problem...
    The AE4440Z has trouble restarting sometimes after the off cycle. (Off cycle is usually 8 to 10 mins) compressor pops overload.
    Usually after the 3rd attempt it fires right up with no issue.
    Start cap is good at 300uf and well within range.
    Pulls current, 10a thru start cap when trying to start.
    Checked for voltage drop, there is 5 volt drop from 120 to 115V when attempting to start...

    Very weird.. I'm ordering new starting components under warranty anyhow but.
    What do you guys think?
    It should start everytime, its a high start torque model with the 1st 4 in the model #.

    Any ideas?Name:  20170323_135921.jpg
Views: 613
Size:  41.0 KB
    Name:  20170323_170119.jpg
Views: 654
Size:  88.7 KB
    Name:  20170323_170550.jpg
Views: 592
Size:  65.3 KB

    Sent from my SM-N920V using Tapatalk
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  11. #9
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Thread Starter
    Quote Originally Posted by shellkamp View Post
    Yeah, I know, it SHOULD work fine; but it doesn't, does it? :grin:

    My gut tells me a pump down solenoid or hard shut off valve would solve this problem for sure. There may be some migration going on



    Sent from my SCH-I545 using Tapatalk
    Wait...sorry i think i misunderstood.
    Yes, it is a hard shut off. It does Not have a bleed port or anything inside it.

    Thats what i meant to say.

    And PHM yes its an a12 700.

    Sent from my SM-N920V using Tapatalk

  12. #10
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    Are you controlling on a constant cut-in stat? That YOU KNOW for a true-fact is a constant cut-in thermostat?

    PHM
    --------
    Alright; where are you going with this?

    The only way I could relate this issue to thermostat type would be a too-short of an off-cycle.

    Sent from my SCH-I545 using Tapatalk

  13. #11
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Thread Starter
    Quote Originally Posted by shellkamp View Post
    Alright; where are you going with this?

    The only way I could relate this issue to thermostat type would be a too-short of an off-cycle.

    Sent from my SCH-I545 using Tapatalk
    The off cycle is around 10 mins usually with an empty box.
    Thats plenty of off time in my opinion.

    Plus...if i unplug/plug in...unplug/plug in a few times every 5 seconds...
    Theres times when it will start and theres times when it won't

    Sent from my SM-N920V using Tapatalk

  14. #12
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by UmmScott View Post
    The off cycle is around 10 mins usually with an empty box.
    Thats plenty of off time in my opinion.

    Plus...if i unplug/plug in...unplug/plug in a few times every 5 seconds...
    Theres times when it will start and theres times when it won't

    Sent from my SM-N920V using Tapatalk
    Then I'd be looking solely at the starting components

    Sent from my SCH-I545 using Tapatalk

  15. #13
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    No concerns with that head?
    Compressor must be starting back up after it cools off a little more.

  16. #14
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes

    True roll in cooler, new condensing unit. Compressor not starting everytime

    I'll never understand the fascination with 404 as a Med Temp refrigerant as a conversion anymore. But anyway.

    What's the pressures when trying to start? Equalized? Does it always do it on short cycle or will it do it after sitting a while too? As said before, contacts on temp control ok?

    Sounds more like either a voltage or starting against pressure.

    295? That's what. 115 SCT?

    May be a big part of your issue. Things get hot, they get a little tight, a little harder to start? Cool off starts right up?

    Hrm. Ok. You converted. I don't see a receiver. Is that a receiver/drier?

    I'm wondering if you removed a little refrigerant, which will raise superheat, cause you to open valve to lower superheat and all that will lower discharge.

    What's subcooling?







    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  17. #15
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by CRussell1975 View Post
    I'll never understand the fascination with 404 as a Med Temp refrigerant as a conversion anymore. But anyway.

    What's the pressures when trying to start? Equalized? Does it always do it on short cycle or will it do it after sitting a while too? As said before, contacts on temp control ok?

    Sounds more like either a voltage or starting against pressure.

    295? That's what. 115 SCT?

    May be a big part of your issue. Things get hot, they get a little tight, a little harder to start? Cool off starts right up?

    Hrm. Ok. You converted. I don't see a receiver. Is that a receiver/drier?

    I'm wondering if you removed a little refrigerant, which will raise superheat, cause you to open valve to lower superheat and all that will lower discharge.

    What's subcooling?







    Sent from my iPhone using Tapatalk
    How will removing refrigerant help? He has a reciever.

    Sent from my SCH-I545 using Tapatalk

  18. #16
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    With out a pump down it is possible your getting liquid slugging

  19. #17
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by shellkamp View Post
    How will removing refrigerant help? He has a reciever.

    Sent from my SCH-I545 using Tapatalk
    I just stated "I don't see a receiver,Is that a receiver drier?"

    So.

    Still can be overcharged with a receiver.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  20. Likes Core_d liked this post.
  21. #18
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Thread Starter
    Quote Originally Posted by CRussell1975 View Post
    I just stated "I don't see a receiver,Is that a receiver drier?"

    So.

    Still can be overcharged with a receiver.


    Sent from my iPhone using Tapatalk
    Only put in 1Lbs 4 oz.

    Pumpdown capacity is 2.5lbs.


    Its 85F in the room kinda warm yes.
    Pretty sure this is starting components. Everything else checks out ok.

    Sent from my SM-N920V using Tapatalk

  22. #19
    Join Date
    Dec 2015
    Location
    TN
    Posts
    355
    Post Likes
    That head looks a bit high to me. I don't know the ambient however


    Sent from my iPhone using Tapatalk

  23. #20
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Thread Starter
    Sooo...

    If mine cant start with a little high head pressure..

    Then how does every other unit out there with dirty coils start fine?

    Sent from my SM-N920V using Tapatalk

+ Reply to Thread
Page 1 of 5 12345 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •