    this could be deadly

    do you think this looks like a potential problem? 460/3 unit. look closely
    Attached Images Attached Images  
    you will attract more flies with honey than with vinegar, but you can attract the most with a dead cat

  2. #2
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Doesnt look to be grounded

    Sent from my SM-G550T2 using Tapatalk

  3. Likes ga-hvac-tech liked this post.
  4. #3
    Join Date
    Mar 2005
    Location
    Portland
    Posts
    571
    Post Likes
    Thread Starter
    exactly!! liquid tight conduit and no landed ground. I found 7 units on this roof all the same way
    you will attract more flies with honey than with vinegar, but you can attract the most with a dead cat

  5. #4
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes
    Looks like line load Larry wired it

    Sent from my XT1585 using Tapatalk
    Quality and Value Service and Repair

  6. Likes GoCougs, Sentinel. liked this post.
  7. #5
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    5,155
    Post Likes
    Color code for the wires is wrong also. That is 240 color code. It kind of looks like a 240 volt disconnect too.

  8. Likes pecmsg, buttwheat liked this post.
  9. #6
    Join Date
    Mar 2005
    Location
    Portland
    Posts
    571
    Post Likes
    Thread Starter
    for some reason that white wire has 55 AC volts to ground
    you will attract more flies with honey than with vinegar, but you can attract the most with a dead cat

  10. #7
    Join Date
    Sep 2013
    Location
    Wi
    Posts
    1,026
    Post Likes
    The blue wire top right needs to be reterminated it's burnt

  11. #8
    Join Date
    May 2006
    Posts
    3,768
    Post Likes
    If you look very closely all 3 on bottom have the same brown ring at the top.

  12. #9
    Join Date
    May 2006
    Posts
    3,768
    Post Likes
    I would have the ground properly connected or refuse to work on it.

  13. #10
    Join Date
    Feb 2008
    Location
    Western Wa.
    Posts
    3,542
    Post Likes
    As said above colors are wrong for 480v it should be brown yellow orange. No way this crap was inspected
    UA Proud

    "Phfft! Facts. You can use them to prove anything." Homer Simpson

  14. #11
    Join Date
    Jun 2002
    Location
    south jersey
    Posts
    1,886
    Post Likes
    Most of the old stuff we work on is not grounded.
    You need to put the phone down and get back to work!

  15. #12
    Join Date
    Apr 2010
    Location
    ... sitting in the Hollywood Hawaiian Hotel, listening to the air conditioner hum
    Posts
    1,208
    Post Likes
    Unless something changed recently, the NEC doesn't require specific colors for 460 v 208/220. The B-O-Y is common for 460, but I don't believe there's a hard rule on phase colors WRT to voltage delivered, other than that the high leg be marked with orange.

    The great professors of the art are not immune from the malignancy of matter and the eternal cussedness of inanimate objects.

  16. Likes northeastbeast, daveallen liked this post.
  17. #13
    Join Date
    Aug 2012
    Location
    Central Virginia
    Posts
    1,022
    Post Likes
    Quote Originally Posted by Bald Menace View Post
    for some reason that white wire has 55 AC volts to ground
    Had a neutral on a job the other day that would spark a little bit every time you touched it to ground

  18. #14
    Join Date
    Nov 2003
    Location
    Montreal, Qc.
    Posts
    917
    Post Likes
    I can beat that without breaking a sweat.
    5 ton York rooftop 220V single phase unit with a 20 kw electric duct heater.
    Commercial building management company.
    My first call to this location.
    The Teck cable comes from the disconnect switch mounted to the unit.
    The Teck cable only supplies the duct heater.
    The compressor and supply air blower are supplied by the 6/2 NMWU which has no disconnect and no markings.
    I did not know this at the time.

    I was called for a loud noise coming from the unit.
    I turned off the disconnect and tested the 3 legs with my meter which naturally showed no voltage.
    I opened the panel and touched the motor which was hot to the touch.
    I was about to turn the pulley to see if the bearings were done when the thermal overload protection on the motor closed and the motor started spinning.
    Someone was looking out for me that day.

    As you can see the unit is getting a grease shower from the kitchen exhaust.
    ΜΟΛΩΝ ΛΑΒΕ

  19. #15
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Aerovox View Post
    Had a neutral on a job the other day that would spark a little bit every time you touched it to ground
    That's why we carry a meter!

  20. #16
    Join Date
    Mar 2017
    Location
    Rockwall, TX
    Posts
    1
    Post Likes
    I'm a newbie in the business, but I can confidently say, that there is not properly grounded, doubt this has been inspected.

    edit: not sure if this comment made it to the right post. still just checking out this website. -Dave

  21. #17
    Join Date
    May 2006
    Posts
    3,768
    Post Likes
    Glad your ok but that is why i never touch a belt or pulley unless i know the motor is un powered

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •