    Curious Solution.

    I had a T&B some time back in a three story building where the third floor was being rehabbed for a brokerage firm.
    An AH was installed and when on line and confirming the fan and motor were maxed out the air flow at the last few terminals was not even close.

    I called the engineers (another State) and told them what I had. Their solution was one I hadn't seen.
    They sent drawings to the mech contractor telling him to extend the discharge plenum and make a tap, send the new run around the space, (think doughnut) and connect the run to the end of the original run. In other words, feed air from both ends.
    I remember this was sometimes done in houses way back (not often) in plans I've seen in books. Not sure why because of extra duct needed but it should lessen pressure looses.

    It did work in fact fairly well. I never knew why the original duct design fell short but has anyone seen this solution done after the fact not being part of the original design. Sort of a static regain of sorts.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  2. #2
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    2,028
    Post Likes
    That's how a lot of city water loops are done in the streets it helps balance the pressure from one side of the loop to other.
    It really should be done that way on duct work as well but nobody wants to pay or give up to space for the extra duct.
    It really screws up a neighborhood if a pipe breaks in the street no one in the city water authority remembers were all the valves are, so the water flows till someone finds the last magical hidden valve.


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    It seems to me that each terminal now has 2 parallel paths for air flow.
    Assuming that resistance to air flow has similar characteristics as resistance to electrical current flow, then the total resistance is less than the lesser of either of the two paths.
    I don't know how to write an equation here, but the total is equal to the product of the two (multiply the two) divided by the sum of the two (add the two).

  4. #4
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,456
    Post Likes
    Makes me wonder if the original ducting was larger, if there would have been a problem on those taps at the end of the run.

  5. #5
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    Quote Originally Posted by BBeerme View Post
    Makes me wonder if the original ducting was larger, if there would have been a problem on those taps at the end of the run.
    That would have been the correct thing to do originally, but once the mistake was made, another small run was probably faster, and cheaper.

  6. #6
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    Quote Originally Posted by BBeerme View Post
    Makes me wonder if the original ducting was larger, if there would have been a problem on those taps at the end of the run.
    If the duct was sized properly, all probably would have been fine.
    Most know if when questioning an engineer, their answer might be any number of things.
    Usually it's better to just lay the results in their lap.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  7. #7
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    Quote Originally Posted by Nuclrchiller View Post
    It seems to me that each terminal now has 2 parallel paths for air flow.
    Assuming that resistance to air flow has similar characteristics as resistance to electrical current flow, then the total resistance is less than the lesser of either of the two paths.
    I don't know how to write an equation here, but the total is equal to the product of the two (multiply the two) divided by the sum of the two (add the two).

    Because the two ducts are unequal total resistance might be the reciprocal
    1/ ((1/r1)+(1/r2)) If I remember that right.
    Probably the TEL total equivalent length of both ducts gives the total friction would equal total resistance then the static pressure represents voltage and velocity = current.
    Never thought of it that way but seems valid. Might be the way the Ductalator was created.
    Often it seems "Laws" like Fan Laws and Ohms law cross over in a similar way.
    I don't know what went South with the original duct sizing or how they arrived at the new duct size. By some of the other things that went wrong it would be a guess at best.
    I might have looked at the terminal totals, see where the air went short, then size the new duct to offset those values. Or just use the SWAG (Scientific Wild A$$ Guess) method.

    The space was originally served by one large unit 100 ton. As with many buildings like this, renters wanted their own units/controls so the original unit was drastically oversized and noisy. When the engineers called me asking about the noise complaint in the space and how loud it was my answer was "Do you remember the Engine Room on the Starship Enterprise?" Not wanting to be a smart a$$, just wanted to drive a point home and what happens when a 100 ton unit morphs into a 12 ton.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  8. #8
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    Quote Originally Posted by Nuclrchiller View Post
    That would have been the correct thing to do originally, but once the mistake was made, another small run was probably faster, and cheaper.
    Yes. I thought, given the problem, it was a good solution for both the reasons you mentioned.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  9. #9
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    This has been an interesting discussion, and an interesting thought exercise. Thanks.

  10. #10
    Join Date
    May 2015
    Posts
    338
    Post Likes
    When I run compressed air lines in a shop I hook the ends together. It helps with the volume tremendously.

  11. Likes Nuclrchiller liked this post.
  12. #11
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,456
    Post Likes
    I totally get it.

    I guess you could say that I'm mildly impressed that the engineer came up with a reasonable solution.

    I was actually going to run the duct that way in my house years ago. Then figured any benefit out weighed the extra work and design. One duct goes this way, and the other goes that way. Each with its own branches or take offs.

    In my case with the ducting, I went with an alternative, I chose to go one size over to reduce velocity and noise. Small house, so any extra heat gain through ducting not that big of a deal. And it is quiet!

    I can't stand noisy air conditioning. Air conditioning should be felt, not heard.


    Quote Originally Posted by joeysmith View Post
    When I run compressed air lines in a shop I hook the ends together. It helps with the volume tremendously.

  13. Likes Nuclrchiller liked this post.
  14. #12
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    2,028
    Post Likes
    Have had to run a parallel control air lines down thru multi- story to boost air pressure at the bottom, starting off with 20 psi in the penthouse and only have 15 psi ten stories lower was causing a lot of control issues. The straight shot of air got all the floors running and cooling.


    Sent from my iPhone using Tapatalk

  15. Likes Nuclrchiller liked this post.
  16. #13
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,456
    Post Likes
    Hmmm, sounds like pneumatics. But the concepts are all the same.


    Quote Originally Posted by Chev5372 View Post
    Have had to run a parallel control air lines down thru multi- story to boost air pressure at the bottom, starting off with 20 psi in the penthouse and only have 15 psi ten stories lower was causing a lot of control issues. The straight shot of air got all the floors running and cooling.


    Sent from my iPhone using Tapatalk

  17. Likes Nuclrchiller liked this post.
  18. #14
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    Fluid dynamics VS frictional loss.
    I once was trying to explain friction losses. My example was saying if you have a water hose with pressure on one end and the hose was long enough, nothing would come out the other.
    He said "Some must come out." So I said " imagine a level hose going around the world, would you expect any water to come out the other end then?"
    Sometimes exaggeration is the only way to drive a point home.
    Chevy: good example, especially as touchy pneumatics are about even tiny deviations in pressure.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  19. #15
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by hvacker View Post
    Fluid dynamics VS frictional loss.
    I once was trying to explain friction losses. My example was saying if you have a water hose with pressure on one end and the hose was long enough, nothing would come out the other.
    He said "Some must come out." So I said " imagine a level hose going around the world, would you expect any water to come out the other end then?"
    Sometimes exaggeration is the only way to drive a point home.
    Chevy: good example, especially as touchy pneumatics are about even tiny deviations in pressure.
    I think you're wrong about the water hose analogy (as far as stopping flow completely); friction loss would reduce the flow substantially, yes, but if you were to graph it out, it would be hyperbolic, moving infinitely closer to, but never touching, the "zero flow" line.

    You could, however, achieve zero flow if the hose were run vertically and the height difference caused a pressure loss equal to or greater than the supply pressure at the water source, but that's not friction loss. :grin:

    Sent from my SCH-I545 using Tapatalk

  20. #16
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    I'm sure you know another use of the word hyperbola is an exaggeration of the truth.

    From just the measuring of friction loss in a system we can predict fluid behavior. An assumption could be made that the losses continue until ya just run outa gas.
    We seem to disagree on something nether can prove as I can't find a hose long enough.

    We know that with a given pump head there are limits to how long pipe runs can be to overcome friction before the pump quits.

    Longest run + 50% * constant 0.04 = required pump head.
    100' + 50% = 150' * 0.04 = 6' head.
    So in my head ( the other head) I sill think the water will stop running.

    Limitations are part of everything we do. If my car goes 100mph on 100 hp and I want to go 200mph I'll need to increase my HP on average times 8.
    Like our pump, it won't make it w/o more power.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  21. #17
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by hvacker View Post
    I'm sure you know another use of the word hyperbola is an exaggeration of the truth.
    From just the measuring of friction loss in systems we can predict fluid behavior. An assumption could be made that the losses continue until ya just run outa gas.
    We seem to disagree on something nether can prove as I can't find a hose long enough.
    Hyperbole, hyperbola; what's the difference?

    Sent from my SCH-I545 using Tapatalk

  22. #18
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    Don't ask me, my degree is in Bovine Scatology.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  23. #19
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,456
    Post Likes
    If you had a hose going around the world, then yes, given enough time, water would come out the other end. Providing all else equal.


    Quote Originally Posted by hvacker View Post
    Fluid dynamics VS frictional loss.
    I once was trying to explain friction losses. My example was saying if you have a water hose with pressure on one end and the hose was long enough, nothing would come out the other.
    He said "Some must come out." So I said " imagine a level hose going around the world, would you expect any water to come out the other end then?"
    Sometimes exaggeration is the only way to drive a point home.
    Chevy: good example, especially as touchy pneumatics are about even tiny deviations in pressure.

  24. #20
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    Quote Originally Posted by BBeerme View Post
    If you had a hose going around the world, then yes, given enough time, water would come out the other end. Providing all else equal.

    OK Your on. Show me the science.
    All else being equal is the problem as the pressure is the same and the friction is the same.
    Just like pump head will only do so much on either a vertical pipe or a horizontal pipe why do you think a hose being horizontal is any different.
    Water pressure is the same as pump head and will only do so much. Like my 100 hp car, I can only go so fast.

    BTW, a 53 Studebaker ( the Beast)with a blown hemi just clocked 275 mph at El Mirage CA.
    I know someone might say a funny car is faster. Ya, but not for long. A funny car will self destruct about 6 seconds after the green light.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

+ Reply to Thread
Page 1 of 4 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •