    Measuring Air Flow

    see attached.
    Attached Images Attached Images

  2. #62
    Join Date
    May 2004
    Posts
    14,135
    Post Likes

  3. #63
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    If you do a duct velocity profile and plot the results you will discard Gil's method. In the right situation any number of alternative methods of measuring airflow will look good but will not work more often than they will. NEBB approves two methods of pitot traverse, the equal area method and log Tchebycheff. AMCA rates the accuracy probability of air testing and there is no way to rate accuracy when the only readings are in any spot in the duct. Log Tchebycheff is considered the most accurate but is more work than the equal area method. If you need to rely on your tests and or prove the accuracy of a pitot traverse you have to used industry standard and approved methods.

  4. #64
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Dad,
    I think it should be open in part because there are those that will not find it otherwise.

  5. #65
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Donut shop pencil balancers are out there and honest TAB people hate them more than anyone else. Try to compete with their price. I was ask to determine the problem with a office space that was added to the basement of a building. The balance report couldn't have looked any better. I couldn't find airflow any where. I traced the problem back to the main duct and discovered that the hole in the main duct at the tap in had never been cut. I urged the owner to take action but he didn't want to which explains in part why that kind of thing happens.

  6. #66
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,453
    Post Likes
    It's not electricity, but there can be rotating equipment.

    Maybe start in the open area, then if need be, a second one could be opened in Pro. Just as there is a General in the open and a General in the Pro.



    Quote Originally Posted by Dad View Post
    Should the new forums be in Pro or open areas guys?


    Recommendations?

  7. #67
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,453
    Post Likes
    I'm guessing if you had good straight air, then okay. After a fitting, maybe not so much.


    Quote Originally Posted by tridiumtech View Post
    I do energy studies (ex DDC tech) and often you got to do a "TAB" to get a chiller plant or air distribution system back
    'on it's feet'.

    We did a functional review of a process AHU for a pharmaceutical. How's this for 'wringing out the water': Design OAT: 98F DBT, 82 WBT (140 gr/lb). AHU Supply: 50F DBT, 34 WBT (3 gr/lb)!

    So we did an airflow test. The guy I worked for was NEBB qualified. So we did a 80 point test for a square duct. Used a beautiful Alnor 9535A VelociCalc air velocity meter (gives velocity and CFM). Nice piece of gear. The transverse reading took about an hour.


    Later I found an old article by Gil Avery (Kele Assoc) titled "Measuring Air Flow" (see attached). At the end Gil concludes,
    "To obtain an approximate average duct velocity...reduce the center velocity by 10%. This will yield results that should be accurate to with in +/-5%".

    The 80-point method got us 6,582 cfm. I took the average of 4 center points and got 6,592 cfm. Within 10cfm (0.15%)!

    4 points is a heck of lot less than 80 points - big time saver. NEBB is valid when it's necessary, but for general energy or HVAC evaluation the center method looks to be valid.

    Anyone agree?

  8. #68
    Join Date
    Nov 2014
    Location
    Portland, Oregon, United States
    Posts
    539
    Post Likes
    Quote Originally Posted by Dad View Post
    Should the new forums be in Pro or open areas guys?


    Recommendations?
    Pro.


    Sent from my SM-G935T using Tapatalk

  9. #69
    Join Date
    Nov 2014
    Location
    Portland, Oregon, United States
    Posts
    539
    Post Likes
    Wayne makes a good point though.

    Sent from my SM-G935T using Tapatalk

  10. #70
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    Dad, I guess the question might be , who would profit most from the forum.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  11. #71
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,453
    Post Likes
    Ultimately, wouldn't it be our customers?


    Quote Originally Posted by hvacker View Post
    Dad, I guess the question might be , who would profit most from the forum.

  12. #72
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    Quote Originally Posted by BBeerme View Post
    I'm guessing if you had good straight air, then okay. After a fitting, maybe not so much.


    I can see how that measurment method might get close. Like you mentioned, a nice long straight run. With where you measure is important. Air in a duct rubs against the duct material and tumbles causing turbulence. Maybe this guy took the time to see where he measured and got the same numbers as a standard traverse. Did some more tests and determined how to mimic a standard treverse.
    A problem is an engineer might want to look at the job traverse report and for sure doesn't want to see four holes. He expects all the holes. Much more if his system has too much system effect.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  13. #73
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    technocratic, Was my coil write-up written well enough to get the message across without turning off someone with minimal knowledge of the subject? If not criticize it and I will try to improve. Don't be afraid to ask questions. Someone here will know the answer.

  14. #74
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,453
    Post Likes
    If you read the entire doc, it accounts for turbulence.


    Quote Originally Posted by hvacker View Post
    I can see how that measurment method might get close. Like you mentioned, a nice long straight run. With where you measure is important. Air in a duct rubs against the duct material and tumbles causing turbulence. Maybe this guy took the time to see where he measured and got the same numbers as a standard traverse. Did some more tests and determined how to mimic a standard treverse.
    A problem is an engineer might want to look at the job traverse report and for sure doesn't want to see four holes. He expects all the holes. Much more if his system has too much system effect.

  15. #75
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    One huge problem with the 4 hole traverse is that there are instances where the airstream is so turbulent with swirl that pitot traverse is not possible. Many times some areas of the duct will have negative pitot readings which are recorded as zero airflow. One reason for mandating the minimum number of readings is to determine if the traverse is valid. 75 % of the readings must be greater than 10 % of the maximum value measured or the traverse is not valid. Readings taken in the center of the duct are seldom negative even when many other readings are. The 4 hole method will get you burned and when it does the engineer will not give you the benefit of doubt. You will be branded a liar no matter how honorable your intentions are.

  16. #76
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    I hope my response to the 4 hole traverse didn't sound harsh because it was only meant to help. Over the years I have done an estimated 12,000 to 15,000 pitot traverses. The leading edge of the velocity profile varies with what ever causes the airflow turbulence in the duct. To make initial airflow adjustment in ducts that had high airflows I ran a pitot traverse and calculated the average velocity pressure. By knowing the average velocity pressure you can take velocity pressure readings across the duct until you find the location closest to the average (we call that the sweet spot). Airflow was then adjusted until you obtained the new desired velocity pressure at that location. That method almost always gets you pretty close to the airflow you want but when you re-traverse the duct the sweet spot is usually in a different location which indicates the velocity profile changes with the velocity of the air.
    Disclaimers on a balance report are meant to alert everyone concerned that the readings are dependent on tested conditions and will not repeat if those conditions are not replicated. One example of that is systems with diversities. Some of the VAV's cannot be calibrated unless some of the boxes are closed enough to force air to the remote VAVs. The balancer should be able to re-establish balanced conditions in most cases and demonstrate airflows to be within about 5% of that balanced. Occasionally that can't be done.

  17. #77
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    Quote Originally Posted by Dad View Post
    Should the new forums be in Pro or open areas guys?


    Recommendations?
    Pro
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  18. #78
    Join Date
    Jul 2014
    Posts
    455
    Post Likes

    4 Point Traverse

    We didn't drill holes for the 80-point traverse - went inside the AHU & measured the air coming out of the cooling coil (we were positioned on the outside of the coil so not to disturb the air flow - still 'tight' conditions).

    The attached PDF shows the actual cfm results for all 80 points (equal spacing method). You can definitely see some odd disturbance values. Maybe that's the argument for taking a lot of readings. I'm not entirely convinced that my capture of the 4 "center' points (or a few more) will always work - but Gil's prediction did work for this particular AHU coil.

    Again, there's the NBEE way & a 'quick & reasonably' accurate way that's appropriate for general cfm discovery.
    Attached Images Attached Images

  19. #79
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    tridiumtech
    Did you measure airflow at the coil with the vel-grid?

  20. #80
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    Quote Originally Posted by BBeerme View Post
    If you read the entire doc, it accounts for turbulence.
    I did read it all and when I accounted for turbulence I could understand how his numbers were arrived at. He just averaged the probability of how much turbulence would affect he average.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

+ Reply to Thread
Page 4 of 5 FirstFirst 12345 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •