    Geothermal Multistage Control Finish With High heat stage

    Hello,

    I have a 2 stage Geothermal heat pump (Climatemaster Tranquility 22) paired up with a Honeywell Prestige IAQ thermostat.

    Looking at the settings of the thermostat I see the option of Multistage control in particular:
    3021: Finish With High Heat Stage
    3020: Finish With High Cool Stage

    Honewell's manual says:

    Multistage Control keeps the high stage of the equipment
    running until the desired setpoint is reached. This setting is
    recommended for Geothermal Heat Pumps to allow the loop to
    rest.
    Select Yes to turn on this feature. Default is No
    .

    I see that it is turned off at this point, but the manual is recommending to set it On for Geo Heat Pumps.

    I'm not sure exactly what are the advantages and disadvantages of this. Can anyone please give me a short explanation?

    and

    Shall I set the multistage control to ON for both Heating and Cooling, or is better to just leave it off as the default?

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    I would want it to drop back to low stage. Less cycling, longer run times.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •