    cook/server line problem

    Asking for input with 2 issues I'm really scratching my head on with this remote setup here..

    I've posted about this before, the restaurant is tired of fiddling with this setup and wants it fixed...but of course "we're spending too much money..blah blah blah"

    So... Randell custom cook line with many drawer base units with raised cold rails. They are all Remoted to one single condensing unit. A BZT025M6C. There's 1 liquid line and 2 suction lines. All the rails are on one line and the boxes go through the 2nd suction line to an EPR valve set at 53psi to keep the box evaps at roughly 20F because the main SST is -10F (24-21psi) at the condensing unit for the cold rails.

    Problem #1. All 4 of their cold rails are keeping the product in the low 40's. What I found was the temp controls cycle the damn things off so early. I think the original control was an HDCNT9901 or something like that.
    Its cut in at 20F and out at 15F. That seemed way way too warm for my liking especially for a cold rail. I ordered an HDCNT100 control which cuts in at 2F and out at -5F.:"
    I applied that to one rail and that seemed to help alot, on time was much much longer and off time was much shorter...but...

    I'm still having the same issue, the air temp under the pans only gets to the low 30's and to 29 at the lowest. Randell says should be 20 to 23F. All TXVs for rails have 10F superheat running on the 23psi suction at the condensing unit.
    What can I do here? any ideas?

    2nd issue...talked about before...
    1 drawer unit on the line won't temp right. What happens with this particular box is as soon as the stat energizes the LLSV, the evap gets really really cold really really fast, down to like almost 0F in 30 seconds.
    So....this makes my A12700 cut out really early, the off cycle is long...and box temp never really gets there.
    Its weird...sometimes it temps fine, sometimes it freezes up, I'm really scratching my head on this one.

    I have a "hunch" that this box may be accidentally piped in with the cold rails running 21psi instead of on the circuit with the EPR valve running 53psi.
    How can I confirm this without splitting the line apart (NOT happening LOL) There's no way to trace the lineset, it comes up in 5 different spots underground of all places.
    It can't be a bad TXV could it? its the whole coil that gets cold and frosty but I could be wrong.

    Sorry I know this is alot of info to process, but I'm just trying to come up with ideas, mainly with this one box. The rails...ehh...may just take the temp controls out and have them use the on/off switches only
    Thanks for any input

  2. #2
    Join Date
    Aug 2016
    Location
    PA USA
    Posts
    42
    Post Likes
    Airflow moving in the right direction? A 12 700 constant cut in is 37 degrees I believe. Is the bulb sensing coil temp or air? I have had issues before when bulb inserted inside coil and unit shutting down prematurely with longer off cycles like you state. Try mounting bulb in discharge air stream to see if cycle time and box temp change.

  3. Likes UmmScott liked this post.
  4. #3
    Join Date
    Jan 2016
    Location
    The triangle in the Keystone
    Posts
    1,265
    Post Likes
    As for issue #1 that could be down to operator error. Might be leaving gaps in the pans or filling it with product that's not below 40 deg. Etc etc. If it were me I might jump the stat out and let her rip to see if it's actually capable of getting down to 20deg. If it can and it does so on a reasonable time then I'd look at changing the location of the bulb or type of stat. I'm not totally against the on/off switch idea. If it were a 24/7 type of place I'd say no but as long as they **** them off at night then I may at least give it a try.

    Issue #2... is the TXV properly sized? I like using a coil sense stat on drawer coolers but in your case maybe an air sense would be better. You'd probably have to play with the bulb location a few times to find the sweet spot. If you can't separate the line and confirm/fix your suspicion then this may be your best option.

  5. #4
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,360
    Post Likes
    Quote Originally Posted by UmmScott View Post

    I have a "hunch" that this box may be accidentally piped in with the cold rails running 21psi instead of on the circuit with the EPR valve running 53psi.
    I would raise the EPR setting way up and note which evaps stop working.

  6. Likes UmmScott, VTP99 liked this post.
  7. #5
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,234
    Post Likes
    Thread Starter
    Quote Originally Posted by icemeister View Post
    I would raise the EPR setting way up and note which evaps stop working.
    My god...


    Genius

    Sent from my SM-N920V using Tapatalk

  8. #6
    Join Date
    Jan 2016
    Location
    The triangle in the Keystone
    Posts
    1,265
    Post Likes
    Quote Originally Posted by UmmScott View Post
    My god...


    Genius

    Sent from my SM-N920V using Tapatalk
    Hahahahaha I know right!


    Sent from my iPhone using Tapatalk

  9. Likes UmmScott liked this post.
  10. #7
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,234
    Post Likes
    Thread Starter
    Ok..so lets say in theory...

    In theory i find out that it is indeed piped in wrong..ie, in the cold rail circuit and not on the epr like its supposed to be...
    Install epr for that box...hell no, no room period so thats not an option.

    What could i do?
    Ke2Therm?
    Air sensing stat with clock?
    Any other ideas?

    Now...if it is piped correctly and is 100% on the Epr circuit then i have another problem and will go further


    Sent from my SM-N920V using Tapatalk

  11. #8
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    3,653
    Post Likes
    Issue 1....you positive there is no air infiltration?

    Sent from my SM-N910W8 using Tapatalk

  12. #9
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,234
    Post Likes
    Thread Starter
    Quote Originally Posted by BALloyd View Post
    Issue 1....you positive there is no air infiltration?

    Sent from my SM-N910W8 using Tapatalk
    Pretty positive, their drawers are in ok shape.

    Beings they seal decent for now.

    They even have a low boy under the grill thats missing the dividing piece that seals between the bottom of the top drawer and the top of the bottom drawer. They say its been like that for a while. And this one doesnt have any freeze up or temp problems

    Sent from my SM-N920V using Tapatalk

  13. #10
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,234
    Post Likes
    Thread Starter
    I will confirm the issues with the box and how its piped monday...

    As for the rail...what are other things i can check?
    They are only open 11am till 10pm. So ive thought and thought and thought some more about just getting rid of the temp controls...because thats the problem, they cycle off so soon.

    The control i put in that closes at 5F and opens at -5F, the customer said its working much better on that particular rail but another rail has an etc1111111000000000000 on it set to cut in at 5F and out at -10.
    The original controls were an HDCNT9904 i think and they close at 20 and open at 15 at the midsetting. That seemed too warm for my liking so i chose the other control

    All rails frost evenly and completely along the back and sides but the air temp under them is in the low 30s.

    Sent from my SM-N920V using Tapatalk

  14. #11
    Join Date
    Jan 2016
    Location
    The triangle in the Keystone
    Posts
    1,265
    Post Likes
    We service a local chain that has maybe 50 stores in the tri-state area. They have similar systems to this and they use a low pressure control to cycle the rails. I personally don't like it but it works. It's touchy and sometimes needs adjusted seasonally. It could be an option for you. Something to consider at least.

  15. #12
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,234
    Post Likes
    Thread Starter
    Quote Originally Posted by VanMan812 View Post
    We service a local chain that has maybe 50 stores in the tri-state area. They have similar systems to this and they use a low pressure control to cycle the rails. I personally don't like it but it works. It's touchy and sometimes needs adjusted seasonally. It could be an option for you. Something to consider at least.
    Its a remoted line with many cold rails.
    Pressure control wont work here

    Sent from my SM-N920V using Tapatalk

  16. #13
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    3,653
    Post Likes
    Stupid question but they keep all the pans in the rail all the time right?