Thread: HID MAGNETIC BALLAST

  1. #1
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes

    HID MAGNETIC BALLAST

    So I found something of interest yesterday
    while servicing some parking lot lights utilizing 480v service. A single pole with 4 fixtures and a ballast in each fixture. Typically they are wired 480 to each ballast. Here I found where someone had wired 2 ballast in series across the 480 volts. All 4 fixtures were wired this way. Two and two. Has anyone seen this done. Is it allowed and why ? Personally in over 35 years I have NEVER seen this done. What say you all ?

  2. #2
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    Maybe someone had a bunch of 240 ballasts hanging around. Or got them at a great price.

    Can't imagine it would be a code violation, not like you're messing around using a ground to carry current or something like that. Probably need to have Timebuilder stop by to weigh in.

  3. #3
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thread Starter
    Pretty sure they were multi tap with a 480 tap. I'll have to grab one off the truck. Your thinking could be correct though. Question is if one ballast goes bad how would that affect the second ?

  4. #4
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    Heh heh, that would depend. If one of the series ballasts internally shorted, then it would take out the other one. If it failed open, then the second ballast would not be harmed.


    Quote Originally Posted by VTP99 View Post
    Pretty sure they were multi tap with a 480 tap. I'll have to grab one off the truck. Your thinking could be correct though. Question is if one ballast goes bad how would that affect the second ?

  5. #5
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thread Starter
    Hahaha....I should have used the 120v taps and put all four in series, hehe

  6. #6
    Join Date
    Feb 2008
    Location
    Western Wa.
    Posts
    3,542
    Post Likes
    No disrespect meant at all but why are you servicing lights? Are you a licensed electrician? Do you work a facilities job?
    UA Proud

    "Phfft! Facts. You can use them to prove anything." Homer Simpson

  7. #7
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thread Starter
    Quote Originally Posted by buttwheat View Post
    No disrespect meant at all but why are you servicing lights? Are you a licensed electrician? Do you work a facilities job?
    Been servicing electric signs and lights for about 40 years now. That and I have the equipment to do said work. I've installed high rise signs 80' tall next to 4 lane highways.

  8. Likes buttwheat liked this post.
  9. #8
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thread Starter
    Quote Originally Posted by BBeerme View Post
    Maybe someone had a bunch of 240 ballasts hanging around. Or got them at a great price.
    .
    Well BBeerme, you hit the nail on the head. I just checked the ballast and the taps are 120/208/240/277 no 480 tap.
    Maybe you should consider a career in criminal investigation

  10. Likes BBeerme liked this post.
  11. #9
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    I sort of already have one. Isn't that one of the things we do? We look at the evidence left behind after a failure, perform our forensic investigation and "once you eliminate the impossible, whatever remains, no matter how improbable, must be the truth."


    Quote Originally Posted by VTP99 View Post
    Well BBeerme, you hit the nail on the head. I just checked the ballast and the taps are 120/208/240/277 no 480 tap.
    Maybe you should consider a career in criminal investigation

  12. #10
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thread Starter
    So my only question left is this an acceptable practice and in violation of any NEC code ?

  13. #11
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    I'm guessing no, but give a shout out to Timebuilder. Send him a link to the thread in a PM.


    Quote Originally Posted by VTP99 View Post
    So my only question left is this an acceptable practice and in violation of any NEC code ?

  14. #12
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thread Starter
    We'll see if he chimes in. If not I'll give a shout out.
    I just have to know if I need this trick in my bag...

  15. #13
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    5,155
    Post Likes
    NEC 410.74 says that the luminaire has to be labeled for the voltage used. The ballasts were not listed for 480 volts
    There are probably others but that one comes to mind.

  16. Likes VTP99, Helenawe liked this post.
  17. #14
    Join Date
    Oct 2020
    Location
    Indianapolis, Indiana
    Posts
    2
    Post Likes
    It is very easy to overload a branch circuit that supplies fluorescent lighting. The most common mistake of making load calculations for fluorescent lighting loads is to use lamp wattage instead of the volt-amperes and total current draw as marked on the ballast's label.

  18. #15
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thread Starter
    Thanks for your post Helenawe
    These particular lights were HID ( high intensity discharge )
    But yes using wattage is a incorrect method.
    Are you involved in the lighting industry ?

  19. #16
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    About coughed up my coffee this morning!!

    Four year old post and some newbie with an Avatar and name that is suspect just magically chiming in?? VTP99 I think you may need to look over your shoulder, got a stalker!

  20. #17
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thread Starter
    Well if that's truly her photo ID she's more then welcome to my phone number

  21. Likes slctech liked this post.
  22. #18
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thread Starter
    Hooah
    Attached Images Attached Images

  23. #19
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thread Starter
    Whoda thunk ?
    Attached Images Attached Images

  24. #20
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    I don't know VTP, don't get your hopes up.

    That pic from this blog is based out of Norway, and the profile says he/she is out of Indianapolis? Got my suspicions here.

    Seems though like a nice enough person, left a homage for HurtinHVAC's father-in-law that recently passed in the memorials section.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •