Carrier WSHP Open Zone Sensor
This board uses rnet sensor. I need to use a duct mount sensor on a few units. Carrier rep seems to be giving me the run around. I also need to mount zone sensors in a jail. The existing sensors are flat plates with tamper screws. Any thing like this for rnet? Or can I use a RTD?
-
-
You should be able to us a RTD but the controller will have to be modified to read it possibly. The RNET sensor are communicating and are not available in a wall plate that you need. The duct sensor can also be converted to a RTD if needed. But again it may need the settings modified using field assistant.
-
You can do that, you'll just have to set the space temperature source to T55 and then connect a standard 10K wall plate or duct mount sensor. I'm pretty sure that has to be set via Field Assistant though as it's not a writable network point if I remember correctly.
-
Post Likes - 1 Likes, 0 Dislikes
-
Originally Posted by
bacnet>CCN
You can do that, you'll just have to set the space temperature source to T55 and then connect a standard 10K wall plate or duct mount sensor. I'm pretty sure that has to be set via Field Assistant though as it's not a writable network point if I remember correctly.
This, you may be able to do it over the network depending on access etc.