    Mani indigo remote, interesting find

    Thought I'd share what i found today with a quietcube indigo machine today. IY0686C

    No production call and it was off on HP cut out displayed on the board. This unit is only a few months old.
    I restart the unit and it literally energizes the condensing unit for 0.2 seconds and shuts off on HP cutout again.
    Went up to roof, condenser spotless and fan motor is good and head pressure was at static readings.

    Went back down to the head and was checking and checking. I updated the firmware on the board seeing if that would do anything but no dice.
    I removed the CVD low voltage wiring from what I thought was the correct spot and it came out easily, then....it HIT me.
    The wires were installed in the holes to the right of the terminal block screws in the pic below.
    They weren't into the actual part that clamps down on the wires.
    Fixed that...problem gone. Just an odd find. Thought I'd share
    Name:  uploadfromtaptalk1470976756596.jpg
Views: 329
Size:  67.6 KB

    So now theyre in the correct spot and not in those little holes on the right side

    Sent from my SM-N920V using Tapatalk

  2. #2
    Join Date
    May 2006
    Posts
    3,680
    Post Likes
    someone didn't take the time to wire it right but you fixed it

  3. Likes UmmScott liked this post.
  4. #3
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,478
    Post Likes
    You know how they come with the little bushing for the knockout hole on condensing unit, that has a screw to clamp down on the wire? We had several fail due to screw being over tightened and shorting 2 wires together. Weird

    Sent from my SAMSUNG-SM-G890A using Tapatalk

  5. #4
    Join Date
    Mar 2007
    Location
    Where the grass is green and the girls are pretty
    Posts
    16,370
    Post Likes
    Good find
    Low voltage from the loose connection

    Warranty call?

    Hope someone realizes they messed up and pays for your time

  6. Likes UmmScott liked this post.
  7. #5
    Join Date
    Aug 2016
    Location
    PA USA
    Posts
    42
    Post Likes
    Good find on that one. At least you fixed it on site and didn't have to return with parts. Can't count how many fan cycling controls we have replaced in the last 6 months. Not to mention control boards and touch pads.

  8. Likes UmmScott liked this post.
  9. #6
    Join Date
    Mar 2007
    Location
    Where the grass is green and the girls are pretty
    Posts
    16,370
    Post Likes
    I started carrying a control board after years of not having one.

    Had to use one Friday and the effing thing had a model and serial number already programmed. Really pzzzed mehoff and it wouldn't go into harvest!!

    I got my first fan cycling control on a indigo last week that was out of warranty. Felt bad charging them for it since they have been poo for years

  10. Likes UmmScott, Mike19 liked this post.
  11. #7
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    3,030
    Post Likes
    Manitowoc is sure proud of their parts. Their prices are out of sight.
    Doug

  12. #8
    Join Date
    Aug 2016
    Location
    PA USA
    Posts
    42
    Post Likes
    And they can price out of sight because of their kitchen care corporation empire. They add new companies weekly it seems

  13. #9
    Join Date
    Mar 2016
    Location
    Tampa Bay Area
    Posts
    53
    Post Likes
    I haf one of those with a LPC that would cut out intermittently talk about a solid pain in the arse it would run for a different lengths and then the communication light would go off had to to sit there for like 30 min with ohm meter across the different cutouts found the LPC opening just enough to shut it down never at a consistent pressure though

    Sent from my SM-G935P using Tapatalk

  14. #10
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,235
    Post Likes
    Thread Starter
    Yeah ditto there.
    I swear those.stupid fan cycles have been complete garbage lately. IOM and Manitowoc both.

    Once its out of warranty I usually just tee off of that extra high side tap at the CVD unit and put the new one there.
    No sense in recovering all that gas just for that thing.
    Or the pinch off method works as well.

    If its the LPS thats bad I'll just pump it down really low and quickly pop in a new one.
    Of course pinch off works here as well

    Sent from my SM-N920V using Tapatalk

  15. #11
    Join Date
    Mar 2007
    Location
    Where the grass is green and the girls are pretty
    Posts
    16,370
    Post Likes
    Had a CVD low pressure act up too. Both pressures were fine but it would drop voltage to the control circut for a split second and lock out the power to the condencer. Mine was consistently doing it while I was there. I couldnt imagine tracking down one that was intermittent the first time. I've gotten into the habit of tapping on these switches and they usually act up then if they are on the way out.

    Mani has started using a different control that seems better built. Not sure about IOM

  16. #12
    Join Date
    Oct 2012
    Location
    Where we mow our own grass
    Posts
    6,673
    Post Likes
    I think every cvd we've installed in the past couple years has had the low pressure control changed at least once.

    We also have some air cooled self-contained units that have had multiple fan cycling switches changed under warranty.

    Once the warranty is up, I install a ranco/Johnson adjustable control and tee it onto a shrader fitting.

  17. #13
    Join Date
    Oct 2012
    Location
    Where we mow our own grass
    Posts
    6,673
    Post Likes
    At manitowoc school, I mentioned something about doing warranty control board changes on 10 different machines.

    The instructor shunned me for being a parts changer and said there's no way all those boards could have been bad.

    Then a couple other guys spoke up and said they've changed at least 10 indigo boards each also.

    In my 8 year career, I've changed a couple q boards, a couple s boards, and 10 indigo boards, most in the past couple years, lol