    Ground wire

    A co-worker wired two fluorescent ceiling lights together and left the ground wire like this? He told me I'm stupid
    Attached Images Attached Images

  2. #2
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    8,097
    Post Likes
    It would appear that you are not the stupid one.

  3. Likes kdean1, buford, DavidDeBord liked this post
  4. #3
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    30,744
    Post Likes
    In fact, that green wire is the ECG, or less mysteriously, the Equipment Grounding Conductor.

    It must be attached to the metal body of the lighting fixture or appliance to which its brothers are providing power. The other end of the green wire connects to what is usually a bare copper conductor in NM-B, or Romex. In a commercial environment., it connects to a metal raceway, the metal of which provides the path back to the OCPD, or breaker.

    The ECG's purpose is to assist the overcurrent device to open in the event that the metal fixtures, cabinet, etc, become energized by a short circuit to metal by the ungrounded power conductor (the "hot wire") or a failed device in the appliance. It provides the assistance by being a low impedance path for the fault current so that the current flow can rise to the point that the breaker opens. We call this "clearing the fault."

    Your friend is not just stupid. He is ignorant of these requirements.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI