    Cooling tower fan minimum speed

    In general, on a forced draft cooling tower application, do you need to set a minimum speed in drive for motor cooling purposes?
    For example, newer tower and sealed motor run off of drive's PID control on 100 ton chiller.

    I worry that a minimum speed might throw the PID off due to the delay and hope that the PID will keep it from staying at low speed. Low load, low ambient would be a worst case scenario I imagine.

  2. #2
    Join Date
    Jul 2012
    Location
    WA
    Posts
    3,250
    Post Likes
    I'm not an expert on the subject, but its my understanding that all motors have a minimum speed you need program in the drive.

  3. #3
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    X2 and sometimes on tower inverter duty motors, it might be on the motor label.
    UA Local 32 retired as of Jan 2020

  4. #4
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,398
    Post Likes
    Quote Originally Posted by RezAtDorsia View Post
    In general, on a forced draft cooling tower application, do you need to set a minimum speed in drive for motor cooling purposes?
    For example, newer tower and sealed motor run off of drive's PID control on 100 ton chiller.

    I worry that a minimum speed might throw the PID off due to the delay and hope that the PID will keep it from staying at low speed. Low load, low ambient would be a worst case scenario I imagine.
    Look up break out speed, thermal load, carrier frequency, stall speed and start load.

    Typically we never run a tower fan slower than about 12hz, this is a moving target for some systems.

    Give the PID plenty of integration time. you'll be fine. Don't forget to search for critical frequencies if the tower is on islation bases.

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  5. #5
    Join Date
    Aug 2009
    Location
    Huntsville, Alabama.
    Posts
    2,840
    Post Likes
    You need a minimum speed so the motor will cool it's self. If it isn't on the motor the maker or seller should be able to tell you.

  6. #6
    Join Date
    Apr 2016
    Location
    Parts unknown
    Posts
    130
    Post Likes
    Thread Starter
    I watched the drive run at mild ambient, medium load conditions and it didn't stay under 12hz for very long and never stayed low at all. The condenser temp went up fast enough to keep the fan going at a good clip.
    I may set a 12hz min and adjust PID.
    Also need to check for resonance freq, thanks

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •