    As far as the EPA is concerned, they don't recognize any refrigerants as drop-in substitutes.

  2. #22
    Join Date
    Sep 2002
    Posts
    27,713
    Post Likes
    They lied to you. Not only is it wrong - what you describe is Doubly wrong.

    PHM
    -------


    Quote Originally Posted by bkaras View Post
    That is exactly what I was told.... it is ok if you charge in vapor. I still think this is unacceptable. I would never mix refrigerants just to save $$$.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  3. #23
    Join Date
    Sep 2002
    Posts
    27,713
    Post Likes
    What about feelings? Can I still mix them?

    PHM
    ---------



    Quote Originally Posted by yaytech View Post
    mix drinks... not refrigerants...
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  4. Likes epmiller, hydra, Turtleman liked this post.
  5. #24
    Join Date
    Feb 2010
    Location
    Newnan Ga,
    Posts
    301
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    What about feelings? Can I still mix them?

    PHM
    ---------
    i can decide... Yup your Wrong do not mix!

  6. #25
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    What about feelings? Can I still mix them? PHM ---------
    Not sure, I'm having mixed feelings about that

  7. #26
    Join Date
    Jul 2012
    Posts
    2,372
    Post Likes
    I paid extra for a 5/8 suction line on a 5 ton package. Mineral oil flows well with the hfc

  8. #27
    Join Date
    May 2016
    Location
    DeKalb, IL
    Posts
    154
    Post Likes
    In situations like this, I always just think about what I would want.

    Not only is mixing gases irresponsible, it's not what I would want for my home system, and thus I won't do it.

  9. #28
    Join Date
    May 2017
    Posts
    1
    Post Likes
    I work for a management company and a client is arguing that 422D can be used to top off R22 systems. I know its a general rule not to mix refrigerants and some say that its illegal. I've searched the EPA website and nothing about it being Illegal. I'm searching for something in writing....Government wise, that says its illegal so I can present to this client. Anybody come across anything in writing? Thanks

  10. #29
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    28,740
    Post Likes
    Quote Originally Posted by VROD View Post
    I work for a management company and a client is arguing that 422D can be used to top off R22 systems. I know its a general rule not to mix refrigerants and some say that its illegal. I've searched the EPA website and nothing about it being Illegal. I'm searching for something in writing....Government wise, that says its illegal so I can present to this client. Anybody come across anything in writing? Thanks
    Safety Tips #1
    https://www.honeywell-refrigerants.c...07c&download=1

  11. #30
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    28,740
    Post Likes
    It is illegal knowingly mix refrigerants.
    They cannot be separated
    There is no PT chart to follow for SH & SC readings
    You pay to dispose of it
    NO Refrigerant Manufacture allows it. All the retro fix papers state "Do Not Mix Refrigerants"

  12. Likes James Alexander, hydra liked this post.
  13. #31
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    20,329
    Post Likes
    Quote Originally Posted by VROD View Post
    I work for a management company and a client is arguing that 422D can be used to top off R22 systems. I know its a general rule not to mix refrigerants and some say that its illegal. I've searched the EPA website and nothing about it being Illegal. I'm searching for something in writing....Government wise, that says its illegal so I can present to this client. Anybody come across anything in writing? Thanks
    I've always heard it's illegal to mix refrigerants, but I have never seen anything from the EPA site or any other site to confirm this. I would never personally condone mixing refrigerants, because I don't see how you would ever charge a system correctly, unless you have a chart for mixed refrigerants, or a crystal ball, and I don't have either.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "When the teachers become unteachable we're all in trouble"

    "It's what you learn after you know it all that counts." ~ John Wooden



  14. #32
    Join Date
    Sep 2002
    Posts
    27,713
    Post Likes
    I think they use a beer can somehow or other.

    PHM
    ------

    Quote Originally Posted by Mr Bill View Post
    I've always heard it's illegal to mix refrigerants, but I have never seen anything from the EPA site or any other site to confirm this. I would never personally condone mixing refrigerants, because -

    I don't see how you would ever charge a system correctly -

    , unless you have a chart for mixed refrigerants, or a crystal ball, and I don't have either.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  15. Likes Core_d liked this post.
  16. #33
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    21,625
    Post Likes
    There was a thread on this a while back. I emailed the EPA and they said to not do it. Additionally, someone found a rule in the IMC that makes it against code to do so.

  17. #34
    Join Date
    Aug 2012
    Posts
    3,773
    Post Likes
    if the freon leaks out, eventually, if you keep adding, you will flush out all the bad stuff and wind up with the good stuff.

  18. #35
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    21,625
    Post Likes

  19. #36
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    20,329
    Post Likes
    Quote Originally Posted by HVAC_Marc View Post
    There was a thread on this a while back. I emailed the EPA and they said to not do it. Additionally, someone found a rule in the IMC that makes it against code to do so.
    They said not to do it?
    Do you or anyone have a direct link to a rule on the EPA site, that directly addresses this? I did find this from the IMC.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "When the teachers become unteachable we're all in trouble"

    "It's what you learn after you know it all that counts." ~ John Wooden



  20. #37
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    21,625
    Post Likes
    Quote Originally Posted by Mr Bill View Post
    They said not to do it?
    Do you or anyone have a direct link to a rule on the EPA site, that directly addresses this? I did find this from the IMC.
    I used to have the email some place. I cant find it right now

  21. #38
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    21,625
    Post Likes
    Quote Originally Posted by Mr Bill View Post
    They said not to do it?
    Do you or anyone have a direct link to a rule on the EPA site, that directly addresses this? I did find this from the IMC.
    Here's the link to my embedded copy of the EPA email:

    http://hvac-talk.com/vbb/showthread....1#post23911711

  22. Likes kdean1 liked this post.
  23. #39
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    20,329
    Post Likes
    Quote Originally Posted by HVAC_Marc View Post
    Here's the link to my embedded copy of the EPA email:

    http://hvac-talk.com/vbb/showthread....1#post23911711
    Thanks Marc! that will work!

    Edit: As I re-read this, it only says it would void the mfg. warranty. Well if you have a 20 year old system and your dropping in another refrigerant to top off the 22, there would probably be no warranty to worry about, right? This is very confusing for a only High School grad.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "When the teachers become unteachable we're all in trouble"

    "It's what you learn after you know it all that counts." ~ John Wooden



  24. Likes HVAC_Marc, jacob-k liked this post.
  25. #40
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    21,625
    Post Likes
    Quote Originally Posted by Mr Bill View Post
    Thanks Marc! that will work!

    Edit: As I re-read this, it only says it would void the mfg. warranty. Well if you have a 20 year old system and your dropping in another refrigerant to top off the 22, there would probably be no warranty to worry about, right? This is very confusing for a only High School grad.
    If you mean this part:

    Quote Originally Posted by EPA person
    as well as voiding the equipment manufacturer's warranty.
    I think the warranty part would be a secondary concern. If the new blend has not gone through SNAP testing then according to the EPA it's prohibited for use.