    I'm hoping this will help others avoid my trials with getting our LXiH back up and running.
    LXi/ AM15 Controller Initial Programming (00-89932 rev G)

    This is from the perspective of a LxiH ML-130017

    To enter initial programming mode short the "FACTORY" Jumper (J5-1 and J5-2) while pushing the on switch.

    To select a parameter push "SELECT", it will advance to the next parameter. To change the option push the up arrow button.

    When finished power down.

    After initialization the display will alternately flash Ty /and a type name – Sd (works for LxiH) begin programming from here. Listed below are the options and what I know about several of them.

    I learned a great deal from these posts (related to the LX30, the predecessor to the Lxi):
    look for the Hobart-LX30H-programming thread (I'd post a link but the forum rules won't let me)

    I replaced a rev E card with a rev G and found a few new options.
    Symbol Meaning Option LXiH Comments
    tY Type Sd, Fd, GL, AS, HL Sd Guessing that Sd is standard, GL is Glassware
    Id Class or ID H (high temp), C (chemical sanitizer) H Options shown are for Type Sd (changes with Type)
    tC ? Ye, no Ye Unclear what does but took the default
    FL Fill Level Sd, PS Sd Sets rinse level to either timed or fill to high sump. Do not us an LxiH on PS the rinse aid can back siphon
    dG ? 1,2 1 Took the default
    SH ? SP, no SP Took the default
    dP Drain Pump Ye,no Ye If "no" tries to empty using wash pump. Default here is no which is wrong for my model.
    Cr

  2. #2
    Join Date
    Dec 2016
    Posts
    1
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Hobart LXi Programing Manual

    I ran across this and figured the actual manual would be worth attaching
    scan0001.pdf

  3. #3
    Join Date
    May 2020
    Location
    Alabama
    Posts
    4
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by miramax281 View Post
    I ran across this and figured the actual manual would be worth attaching
    scan0001.pdf
    I know this is quite old but do you or someone else possibly have page 2 of that manual?

  4. #4
    Join Date
    Oct 2008
    Location
    In a kitchen with my head stuck in an oven
    Posts
    1,550
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Wdunlap89 View Post
    I know this is quite old but do you or someone else possibly have page 2 of that manual?
    I finally accessed this after a three month furlough due to COVID. It's all three pages.

    FWIW: This is also included in the box containing each new control board (part number 00-892932-00002), so...it's NOT a secret:
    Attached Images Attached Images


    "You never know what others don't know." -

    If I can't laugh at myself...then I'll laugh at YOU! -

  5. #5
    Join Date
    May 2020
    Location
    Alabama
    Posts
    4
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    They forgot to include it with mine and hobart acted like it didnt exist when I questioned them about it

  6. Likes ECtofix liked this post.
  7. #6
    Join Date
    May 2020
    Location
    Alabama
    Posts
    4
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks!

  8. Likes ECtofix liked this post.