+ Reply to Thread
Results 1 to 3 of 3

Thread: Xlt recovery machines liquid vs vapor

  1. #1
    Join Date
    Jun 2008
    Posts
    300
    Post Likes

    Xlt recovery machines liquid vs vapor

    Just wondering, what is the difference between these two settings? Does the liquid setting just restrict/throttle the inlet more than the vapor setting?

  2. #2
    Join Date
    Jan 2014
    Location
    Bloomington, MN
    Posts
    148
    Post Likes
    If you have a moment, please watch this video...
    http://yellowjacket.com/videos/effec...ry-techniques/

  3. #3
    Join Date
    Jan 2014
    Location
    Bloomington, MN
    Posts
    148
    Post Likes
    The liquid setting on the recovery machine throttles refrigerant slowly into the suction port of the compressor thus preventing “liquid-slugging” the compressor.

    The proper procedure for recovering refrigerant is:
    When the Low Pressure Gauge starts going down, during recovery, that is when the selector valve should slowly be turned from Liquid to Vapor setting.