    Quote Originally Posted by timjimbob View Post
    Had an issue that electrified the water pipes, and cast iron pipes in a rent house. We could not bond or add enough grounding rods to eliminate the problem. Two more 6 foot rods, ties to underground copper pipe to back yard hydrant. All existing grounding was proper. Had to have tenants move out because of shocking shower.

    Problem was bad neutral at pole. power company says they are not liable for condition of power quality coming into the residence.

    I felt exposed to a law suit even though I had done everything I can to safeguard my tenants.

    How should I make this situation safer, in future situations.
    Grounding rods are completely useless for preventing shock and that was never their purpose anyway.
    -Marty

  2. #15
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,337
    Post Likes
    Thread Starter
    "Grounding rods are completely useless for preventing shock and that was never their purpose anyway. "


    Why are they required then, what is their role?

  3. #16
    Join Date
    Jan 2010
    Posts
    16,150
    Post Likes
    Lighting strikes

  4. #17
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    30,729
    Post Likes
    Quote Originally Posted by timjimbob View Post
    Had an issue that electrified the water pipes, and cast Iron pipes in a rent house. We could not bond or add enough grounding rods to eliminate the problem. Two more 6 foot rods, ties to underground copper pipe to back yard hydrant. All existing grounding was proper. Had to have tenants move out because of shocking shower.

    Problem was bad neutral at pole. power company says they are not liable for condition of power quality coming into the residence.

    I felt exposed to a law suit even though I had done everything I can to safeguard my tenants.

    How should I make this situation safer, in future situations.

    Have the neutral repaired. Follow up with a call to the utility company ombudsman if the electrician says it is the utiliy's responsibility.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  5. #18
    Join Date
    Aug 2006
    Posts
    3,209
    Post Likes
    I knew someone who had a brand new fiberglass swimming pool they couldn't use, due to getting shocked. It even did this with the meter pulled. Lawsuit went on for over two years, because the utility wouldn't admit the problem was theirs. They finally had to run six miles of neutral wire. The damages trail was in the millions, LOL.
    Retired, after 43 Years

  6. #19
    Join Date
    Jan 2017
    Location
    Rhode Island
    Posts
    156
    Post Likes
    Had to chime in on this old thread.When I worked for the Gas Company I had a Gas Supply line coming in from the Main to the House,was Hot as Hell.Put my volt stick to it,sure enough it was electrified.Was acting as some sort of Neutral or Ground.If you disconnected the Gas pipe,the lights in the House would go dull,and all electrical would start to buzz.Turns out other houses in the Neighborhood had some similar issues,but no one could figure where the problem originated from,untill now!Talk about a hair-raising experience!

  7. #20
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    1,701
    Post Likes
    Requirement is a 25 ohm ground to rod. Do the math. That is a lot of current looking for a place to go if the neutral is defective on the utility or user side..... The farther you are from the substation, the larger the resistance and the greater the potential.

  8. Likes DavidDeBord liked this post
  9. #21
    Join Date
    Apr 2003
    Location
    Greenback, Tennessee
    Posts
    966
    Post Likes
    Quote Originally Posted by timjimbob View Post
    "Grounding rods are completely useless for preventing shock and that was never their purpose anyway. "


    Why are they required then, what is their role?
    Sorry for the very late reply. A PE at a local electrical utility told me that the purpose of a grounding rod is to make the potential at the service entrance to the same as the ground at the transformer. A ground rod is not a low impedance path back to the source and therefore generally will not trip a breaker.


    Mike Holt gives a good explanation starting just after 19:30 min

    https://www.youtube.com/watch?v=3vvvv5QVZoA
    -Marty

  10. #22
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,337
    Post Likes
    Thread Starter
    In my case, pole transformer ground was nothing near zero volts so, in theory, my meter/ service entrance voltage should be jacked up to utility transformers' above zero value. Not buying that.

  11. #23
    Join Date
    May 2006
    Location
    Raleigh,NC.
    Posts
    496
    Post Likes
    had a case where I found there was just over 50 volts on neutral from power company after several hours of a "search and destroy" volt mission. The power co. was sympathetic but said could do nothing, because it was probably someone, up the line, for who knows how many miles, putting the volts on the line.
    remember, with electronics; when its brown,its cooking and when its black, its done!!!

  12. #24
    Join Date
    Apr 2002
    Location
    NW Indiana
    Posts
    1,670
    Post Likes
    I chased a shocking water issue once that only occurred when the wall furnace was on. I had no hair on my head from me pulling it out finding the issue. In the end a Fan wire in between the furnace cabinet that was buried you couldn't see was rubbing and grounding to the cabinet. When the fan would switch on voltage would bleed through the copper LP gas line passing to the water heater.
    "The Bitterness of poor quality remains long after the sweetness of low price is forgotten"

  13. #25
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,337
    Post Likes
    Thread Starter
    Had a long time customer call about an issue with the DISH installer. They had plugged their grounded receiver into the master bath plug. Shower of sparks blew from the plug. Wanted me to figure what was going on.

    DISH antenna coax was well grounded to the outside meter equipment. The house was 10 year old pier and beam with wood floors. I found a romex cable staple that had punctured the insulation and was tying hot to ground conductor in the attic.

    Well this can happen but should have tripped the breaker. That puzzled me. Opened the breaker panel and found the romex ground connector not connected to busbar.
    So all these years the electrical box screws were all 120 volts hot in the bathroom-lucky no one was killed.

    Thinking back, some "don't care" electrician probably kept having the breaker trip and found if he un-connected the ground the breaker would stay on.

  14. #26
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    8,741
    Post Likes
    I had a customer complaining about lights blinking when the compressor started on their heat pump, like that has never happened before right. I dig in to it, it has a start kit that is working properly, the voltage doesn't dip on start up, amp draw on start up was faster than my Fluke would capture at 100/sec recording value. I checked everything I could think of and came up blank at every turn. For some reason, out of desperation I guess, I stuck one probe on the ground wire and put the other probe in the ground, I had 60+ volts, what. How does this happen. I start checking connections all the way back to the panel and had the same results all the way. I called the city and explained the issue. They sent out a couple lineman. I told them what I found, they pulled the meter and checked line-line, line to neutral, line to ground neutral to ground, all readings normal. The guy said I don't see a problem. I said put one probe on ground and give me the other. So he did and I stuck the probe in the dirt. He said what did you do, so I showed him the probe in the dirt. He went WTF. I said that's what I thought. They dug for over an hour and finally found the ground plate was rotted off at the pole. They fixed that, the reading neutral to ground went away and so did the light flicker on compressor start.

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •