Thread: Sporlan Modulating 3-Way Valve

  1. #1
    Join Date
    Apr 2016
    Posts
    159
    Post Likes

    Sporlan Modulating 3-Way Valve

    The Sporlan Modulating 3-Way Valve is designed to modulate flow of refrigerant at two ports and divert flow between two separate outlets. The product line features two sizes, the MTW-9 and MTW-17, which cover R-410a flow capacities up to 40 tons (131 kW). These valves are approved for suction, liquid and discharge line uses; including dehumidification, reheat and heat reclaim applications.

    When compared to other modulating options, the Modulating 3-Way Valve requires fewer valves, reducing piping and wiring complexity and cost and reduced installation time.

    The Sporlan Pressure Control and Temperature Control can be paired with the valve to provide precise stand-alone control of fluid temperature and pressure as required.


  2. Likes caheiman30, kamersoutdoor liked this post.
  3. #2
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Is this still test mode ?

  4. #3
    Join Date
    Apr 2016
    Posts
    159
    Post Likes
    Thread Starter
    No this is currently available at your local Sporlan authorized wholesaler.

    Here is a link to the literature http://sporlanonline.com/literature/100/ev/100-40-3.pdf

  5. Likes Robb M., DavidDeBord liked this post.
  6. #4
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Thank You Sporlan !
    & Welcome to HVAC-TALK !!
    Great To See You Here

  7. #5
    Join Date
    Jan 2007
    Location
    Stongsville Oh
    Posts
    1,410
    Post Likes
    I saw Aaon has started using these for hot gas reheat just the other day. No second valve needed. Sweet, and timely video, for me anyway. Tanks
    ckartson
    I didn't write the book I just read it!

  8. #6
    Join Date
    Jan 2013
    Location
    Chicago, IL
    Posts
    11
    Post Likes
    Is Sporland developing other applications for this style valve i.e.

    1 split condenser
    2 modulating pressure differential for H/G defrost

  9. #7
    Join Date
    Apr 2016
    Posts
    159
    Post Likes
    Thread Starter
    The Sporlan Modulating Three Way (MTW) valves can be applied in many different applications for discharge, suction and liquid refrigerant flow. These valves are approved for maximum and minimum refrigerant temperature of -40°F to 240°F. Assuming these temperature limits are not exceded split condenser and defrost differential applications would be possible with the current valves. However these current models may limit system capacity. Capacity charts are shown below:


  10. Likes DavidDeBord liked this post.
  11. #8
    Join Date
    Aug 2016
    Posts
    2
    Post Likes
    I have a built-up air cooled system with a "wild" condenser (where I cannot modulate the condenser fans). This is because the condenser coil is located in a building exhaust duct. Could the MTW valves be used to replace the ORI/ORD valves to perform electronic head pressure control? I would like to control it with a IB-G interface board. Thanks.

  12. #9
    Join Date
    Apr 2016
    Posts
    159
    Post Likes
    Thread Starter
    Quote Originally Posted by Phil Batterson View Post
    I have a built-up air cooled system with a "wild" condenser (where I cannot modulate the condenser fans). This is because the condenser coil is located in a building exhaust duct. Could the MTW valves be used to replace the ORI/ORD valves to perform electronic head pressure control? I would like to control it with a IB-G interface board. Thanks.
    The MTW valve is typically located in the discharge line for dehumidification, reheat and heat reclaim applications. Outlet A is piped to the normal condenser and Outlet B to the reclaim/reheat condenser.

    An IB-G is an interface board and can be used with any of our electronic valves. The IB-G will take a 0-10 V or 4-20 mA signal from a 3rd party controller and convert it to a stepper motor signal to control the valve.

    If you are looking to move to electronic head pressure control, you can use a CDS valve in place of the ORI. The ORD will still be used. A TCB (or IB-G and 3rd party controller) should be used to control the CDS valve.

    We don't have published values for the CDS valve in this application, but we can help you select one if you provide the following information:
    Refrigerant:
    Minimum Ambient Temperature (°F):
    Receiver Outlet Temperature (°F):
    Discharge Temperature (°F):
    Discharge Pressure (PSI):
    Head Pressure Control Setting (PSI):
    Receiver Pressurization Setting (PSI):

    Link to IB-G Bulletin:
    http://sporlanonline.com/literature/...2.1%20IB-G.pdf

    Link to TCB Bulletin:
    http://sporlanonline.com/literature/100/cb/100-50-1.pdf

  13. Likes DavidDeBord liked this post.
  14. #10
    Join Date
    Aug 2016
    Posts
    2
    Post Likes
    Sorry, I left out some details, and mis-spoke a little. I don't currently have an ORI/ORD now, this is being designed now, so I meant "in lieu-of".

    Also, my system is R-410a, so please correct me if I'm wrong, but (according to the literature) the ORD does not have an R-410a rating. Also, my system capacity (~ 25rt), which exceeds the ORD capability.

    So, I'm trying to duplicate the LAC valves application (and simplified piping), which I have used over the years (very successfully). I also usually use a check valve on the inlet to the reciever, to limit off cycle migration back to the condenser in the off-mode.

    In this application, I will monitor the liquid line (receiver) pressure with my control system and then control the output signal to the IB-G, to drive the MTW. The A port would connect to the condenser input, the B port would connect to the liquid line (bypassing the condenser).

    Again, think of a LAC valve, just electronic.

    Wouldn't this work? Or am I missing something?

  15. Likes DavidDeBord liked this post.
  16. #11
    Join Date
    Apr 2016
    Posts
    159
    Post Likes
    Thread Starter
    Quote Originally Posted by Phil Batterson View Post
    Sorry, I left out some details, and mis-spoke a little. I don't currently have an ORI/ORD now, this is being designed now, so I meant "in lieu-of".

    Also, my system is R-410a, so please correct me if I'm wrong, but (according to the literature) the ORD does not have an R-410a rating. Also, my system capacity (~ 25rt), which exceeds the ORD capability.

    So, I'm trying to duplicate the LAC valves application (and simplified piping), which I have used over the years (very successfully). I also usually use a check valve on the inlet to the reciever, to limit off cycle migration back to the condenser in the off-mode.

    In this application, I will monitor the liquid line (receiver) pressure with my control system and then control the output signal to the IB-G, to drive the MTW. The A port would connect to the condenser input, the B port would connect to the liquid line (bypassing the condenser).

    Again, think of a LAC valve, just electronic.

    Wouldn't this work? Or am I missing something?
    The MTW valve isn't designed for this application. You would better off using the ORD/CDS combination.

    The ORD has a 650 psig MRP and is rated for R-410A. To gain capacity on the ORD you will have to run multiple ORDs in parallel. At 25 tons, you will likely need 2 ORDs and one CDS-9. We can nail the selection down better if you can answer the questions in the above post.

  17. Likes DavidDeBord liked this post.
  18. #12
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Quote Originally Posted by Sporlan View Post
    The MTW valve isn't designed for this application. You would better off using the ORD/CDS combination.

    The ORD has a 650 psig MRP and is rated for R-410A. To gain capacity on the ORD you will have to run multiple ORDs in parallel. At 25 tons, you will likely need 2 ORDs and one CDS-9. We can nail the selection down better if you can answer the questions in the above post.
    Hey Sporlan,

    I am getting ready to install some of these valves on some field built up systems that are going to use this valve for hot gas reheat in dehumidification. The circuit that this valve is installed on is 36 tons. Our design evaporator temperature is 40 degrees. I was talking with technical support, and they told me that I may need to consider two of these in parallel because my hot gas reheat coil heating capacity is 582 MBH, and my refrigerant mass flow is 5679 lbm/hr.

    Looking at the sizing chart it states that I can go up to 49 tons if I have a 10 psi pressure drop. What is the disadvantage of allowing a 10 psi pressure drop? Is this saying that if I try to put around 48-49 tons of hot gas through this valve that I will have a 10 psi pressure drop?

    Thanks for the help!
    J. King

  19. Likes DavidDeBord liked this post.
  20. #13
    Join Date
    Aug 2014
    Location
    Washington, MO
    Posts
    28
    Post Likes
    Quote Originally Posted by apprentice3 View Post
    Hey Sporlan,

    I am getting ready to install some of these valves on some field built up systems that are going to use this valve for hot gas reheat in dehumidification. The circuit that this valve is installed on is 36 tons. Our design evaporator temperature is 40 degrees. I was talking with technical support, and they told me that I may need to consider two of these in parallel because my hot gas reheat coil heating capacity is 582 MBH, and my refrigerant mass flow is 5679 lbm/hr.

    Looking at the sizing chart it states that I can go up to 49 tons if I have a 10 psi pressure drop. What is the disadvantage of allowing a 10 psi pressure drop? Is this saying that if I try to put around 48-49 tons of hot gas through this valve that I will have a 10 psi pressure drop?

    Thanks for the help!
    We assume the refrigerant is R-410A. The MTW-17 is rated at 49.2 tons with 10 psi pressure drop at 100 F condensing temperature, 40 F evaporating temperature and 60 F liquid temperature.


    The question: Is this saying that if I try to put around 48-49 tons of hot gas through this valve that I will have a 10 psi pressure drop?


    The answer is: Yes, at the conditions stated in sentence above.

  21. #14
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Quote Originally Posted by Sporlan PM View Post
    We assume the refrigerant is R-410A. The MTW-17 is rated at 49.2 tons with 10 psi pressure drop at 100 F condensing temperature, 40 F evaporating temperature and 60 F liquid temperature.


    The question: Is this saying that if I try to put around 48-49 tons of hot gas through this valve that I will have a 10 psi pressure drop?


    The answer is: Yes, at the conditions stated in sentence above.
    So what tonnage do you look at when sizing these? The circuit tonnage or the MBH capacity of the hot gas reheat coil converted to tonnage?

    The refrigerant is R-410a. Thanks for the reply.


    Sent from my iPhone using Tapatalk
    J. King

  22. #15
    Join Date
    Aug 2014
    Location
    Washington, MO
    Posts
    28
    Post Likes
    Quote Originally Posted by apprentice3 View Post
    So what tonnage do you look at when sizing these? The circuit tonnage or the MBH capacity of the hot gas reheat coil converted to tonnage?

    The refrigerant is R-410a. Thanks for the reply.

    The valve should be sized off circuit capacity/system capacity.

  23. #16
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Quote Originally Posted by Sporlan PM View Post
    [FONT="]We assume the refrigerant is R-410A. The MTW-17 is rated at 49.2 tons with 10 psi pressure drop at 100 F condensing temperature, 40 F evaporating temperature and 60 F liquid temperature.

    [/FONT]
    The question: Is this saying that if I try to put around 48-49 tons of hot gas through this valve that I will have a 10 psi pressure drop?


    The answer is: Yes, at the conditions stated in sentence above.
    I got back with the engineer on this job, and he asked me if we know what the estimated pressure drop would be on this valve at the design refrigerant mass flow rate of 5679 lbm/hr?
    J. King

  24. #17
    Join Date
    Apr 2016
    Posts
    159
    Post Likes
    Thread Starter
    Quote Originally Posted by apprentice3 View Post
    I got back with the engineer on this job, and he asked me if we know what the estimated pressure drop would be on this valve at the design refrigerant mass flow rate of 5679 lbm/hr?
    The mass flow rate of 5679 lb/hr at 100 F condensing, 60 F liquid, 40 F evaporator with R-410A through the MTW17 would have 6.6 psi of pressure drop. (This is equivalent to 40.1 tons)

    Thank you


  25. #18
    Join Date
    Apr 2016
    Posts
    159
    Post Likes
    Thread Starter
    The mass flow rate of 5679 lb/hr at 100 F condensing, 60 F liquid, 40 F evaporator with R-410A through the MTW17 would have 6.6 psi of pressure drop. (This is equivalent to 40.1 tons)

    Thank you

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •