    The facility Im at is looking to up grade the existing Carrier CCN chiller controls to i-Vu. At a resent contractor meeting several items were discussed but mostly it came down to energy savings. Can the i-Vu controls shut down a small chiller before starting a larger one? We were told No, a larger chiller will start on ACR then the smaller one secures.
    This running of 2 machines = a higher KW demand and higher operating costs. (Several thousands of $s a day)

    Other then i-Vu what are our options for chiller controls?

  2. #2
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    2,579
    Post Likes
    I have found the Carrier CCN to be very reliable. The local OEM office has one of the best programmers I know of. Your mileage may vary.
    God Bless our Veterans

    God Bless the USA

  3. #3
    Join Date
    May 2006
    Location
    Western NY
    Posts
    4,377
    Post Likes
    A BEST ++ program can be written to do what you want.
    "Nearly all men can stand adversity, but if you want to test a man's character, give him power."
    -Abraham Lincoln

  4. #4
    Join Date
    Apr 2007
    Location
    uk
    Posts
    287
    Post Likes
    Which CCN controller are you using presently to control both chillers.
    Flotronic System Manager or Chiller System Manager

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    26,045
    Post Likes
    Thread Starter
    CSM

    2-375 Ton 19XRs & 2-500 Ton 19XLs

  6. #6
    Join Date
    Apr 2007
    Location
    uk
    Posts
    287
    Post Likes
    Just configure the lead chiller to 100% before starting the lag chiller this is in the CSM. The I-VU is not a controller but a means of viewing a system remotely either on site or through the web allowing you to be able to change various items in the system control

  7. #7
    Join Date
    Apr 2005
    Location
    n.y
    Posts
    73
    Post Likes
    thats right thoes chillers can do what ever you tell them.you can link all uints.what controller is on the chillers.pic ?

Posting Permissions