Thread: If you have alerton questions

  1. #21
    Join Date
    Dec 2008
    Location
    Dallas, Tx
    Posts
    99
    Post Likes
    Thread Starter
    The picture is clearer now.

  2. #22
    Join Date
    Dec 2008
    Location
    Rescue Calif
    Posts
    1
    Post Likes

    Adding a TX-SA in IBEX

    Im the only HVAC tech in a small school distric (7 sites)
    Their all Alerton controled ( 3 with Bactalk 4 with Ibex)
    Im using Envision for bactalk v1.30A
    I want to add a TX-SA 651 on one of the Ibex sites
    Ive installed the Tx - addressed it -set it up in program Manager -
    added its zone and schedual - and its responding.
    in Envisions I went Tools>DDC>Visio>subcaller - added its sub routine
    in the the correct BCM-Tux program and addressed Using copy and edit.

    I cant get it it respond to OSA. it contantly reads 87deg

    Help

  3. #23
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Quote Originally Posted by ph33r View Post
    The picture is clearer now.

    OK...I put the subroutine in bldg A BCM
    I put the heartbeat in bldg B BCM

    It seems to work but I have 1 issue.

    I see the heartbeat with BV 30.

    Then I removed the power to bldg B BCM

    As the BCM is powering down BV 100 switches to
    show comm fail but once the BCM is completely
    powered off, BV100 switches back to normal.

    Is this correct?

  4. #24
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Quote Originally Posted by mechinc View Post
    OK...I put the subroutine in bldg A BCM
    I put the heartbeat in bldg B BCM

    It seems to work but I have 1 issue.

    I see the heartbeat with BV 30.

    Then I removed the power to bldg B BCM

    As the BCM is powering down BV 100 switches to
    show comm fail but once the BCM is completely
    powered off, BV100 switches back to normal.

    Is this correct?


    Anything ph33r ?

  5. #25
    Join Date
    Dec 2008
    Location
    Dallas, Tx
    Posts
    99
    Post Likes
    Thread Starter
    Im the only HVAC tech in a small school distric (7 sites)
    Their all Alerton controled ( 3 with Bactalk 4 with Ibex)
    Im using Envision for bactalk v1.30A
    I want to add a TX-SA 651 on one of the Ibex sites
    Ive installed the Tx - addressed it -set it up in program Manager -
    added its zone and schedual - and its responding.
    in Envisions I went Tools>DDC>Visio>subcaller - added its sub routine
    in the the correct BCM-Tux program and addressed Using copy and edit.

    I cant get it it respond to OSA. it contantly reads 87deg

    Help

    Well you are going to be doing a couple points transfers here. One from a zone custom or ibex point to a logical ai which will be then read by your program and edited. If I remember correctly (its been a while since I did tuxes) TX-sa is an application specific tux and not an aplc so you are going to need to get the help file or call alerton support and see what logical ai it references for the outside air.

  6. #26
    Join Date
    Dec 2008
    Location
    Dallas, Tx
    Posts
    99
    Post Likes
    Thread Starter
    Quote Originally Posted by mechinc View Post
    Anything ph33r ?
    Sorry was taking a break for a while I'll get to it in just a second. I have to reread through my code.

  7. #27
    Join Date
    Dec 2008
    Location
    Dallas, Tx
    Posts
    99
    Post Likes
    Thread Starter
    Quote Originally Posted by mechinc View Post
    OK...I put the subroutine in bldg A BCM
    I put the heartbeat in bldg B BCM

    It seems to work but I have 1 issue.

    I see the heartbeat with BV 30.

    Then I removed the power to bldg B BCM

    As the BCM is powering down BV 100 switches to
    show comm fail but once the BCM is completely
    powered off, BV100 switches back to normal.

    Is this correct?
    Ok well when the bcm that has bv-100 is off you should get an unreliable reading because the bcm it references is off.

  8. #28
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Quote Originally Posted by ph33r View Post
    Ok well when the bcm that has bv-100 is off you should get an unreliable reading because the bcm it references is off.
    I believe I setup the BV as off=normal, on= comm-fail

    So when it goes completely offline, the BV stays on Normal.

    If I can get it to go NR, is there a way to flag the NR
    and email that out?

    Also,

    I noticed whomever setup the programming performed
    all logic in visio and are using BVs and AVs.
    Why would one use the global BVs / AVs when you can cut down
    network traffic by using the local device's logical BIs /AOs

    This way all logic is in the local controller and the only thing that
    is going through the global is OA-share, etc.?

  9. #29
    Join Date
    Dec 2008
    Location
    Dallas, Tx
    Posts
    99
    Post Likes
    Thread Starter
    Quote Originally Posted by mechinc View Post
    I believe I setup the BV as off=normal, on= comm-fail

    So when it goes completely offline, the BV stays on Normal.

    If I can get it to go NR, is there a way to flag the NR
    and email that out?

    Also,

    I noticed whomever setup the programming performed
    all logic in visio and are using BVs and AVs.
    Why would one use the global BVs / AVs when you can cut down
    network traffic by using the local device's logical BIs /AOs

    This way all logic is in the local controller and the only thing that
    is going through the global is OA-share, etc.?
    I don't know maybe they were doing a global process such as determining the lowest cooling signal and reseting a chiller? There could be many reasons, now if they wrote basic code like hot water valve control or vfd pi loops then that doesn't make sense.

    There is no way to monitor and dial out if your bcm-eth craps out as it is your connection to the net. You could have a dedicated vlc that monitors a point from the bcm and have a bo connect through a relay to a modem that has terminal blocks to monitor alarms but that is allot of work.

    Unfortunately if the bcm goes well your sol in MOST cases.

  10. #30
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Quote Originally Posted by ph33r View Post
    I don't know maybe they were doing a global process such as determining the lowest cooling signal and reseting a chiller? There could be many reasons, now if they wrote basic code like hot water valve control or vfd pi loops then that doesn't make sense.

    There is no way to monitor and dial out if your bcm-eth craps out as it is your connection to the net. You could have a dedicated vlc that monitors a point from the bcm and have a bo connect through a relay to a modem that has terminal blocks to monitor alarms but that is allot of work.

    Unfortunately if the bcm goes well your sol in MOST cases.

    Is there a way to flag NR?

  11. #31
    Join Date
    Jan 2010
    Posts
    2
    Post Likes
    Hi All, I have been reading through the previous postings relating to Bactalk but have not seen any topics relating to removing of staff from the alarms. Here's my predicament:

    My Data Centre manager has retired, I have removed him from the SMS alarms but he but is still receiving the Voice alarms.

    Can somebody please explain to me how to remove his name from the Voice alarms? I am using Envision BACtalk V1.30A

    Thanks
    Geordie09

  12. #32
    Join Date
    Mar 2009
    Location
    VB
    Posts
    323
    Post Likes
    Georgie , Check your post....


    Ph33r, Sorry beat you to it

  13. #33
    Join Date
    Dec 2008
    Location
    Dallas, Tx
    Posts
    99
    Post Likes
    Thread Starter
    Hehe, well I got the BCM-TUX one :-D

  14. #34
    Join Date
    May 2006
    Posts
    334
    Post Likes
    Hi Ph33r and other experts,

    I am new to Alerton. What programming software from Alerton I should use/purchase, if I only use Alerton field controllers with non-Alerton BACnet frontend (say, Niagara AX)? Thanks!

  15. #35
    Join Date
    Aug 2009
    Location
    England, UK
    Posts
    58
    Post Likes
    Quote Originally Posted by leaflying View Post
    Hi Ph33r and other experts,

    I am new to Alerton. What programming software from Alerton I should use/purchase,!
    Hi All, I have a similar question - I have some used/removed Alerton controllers, including an 'IBEX' hardware lock. Rather than dump the lot, I was interested in learning about the programming/software routines, etc.

    The Alerton product is quite rare in the UK due to the Honeywell tie in with other products, so getting any information is not easy.

    Many thanks.

  16. #36
    Join Date
    Dec 2008
    Location
    Dallas, Tx
    Posts
    99
    Post Likes
    Thread Starter
    You will need envision for bactalk to develop the graphics and frontend and the ebt will come with the visio macro for programming or you could use the blue screen in the ebt program. Alerton is one of the easiest programming langauges I have found. This is all BACtalk Ibex is a different beast.

  17. #37
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    2,634
    Post Likes
    ph33r,

    Would you happen to have any technical documentation on the LSI?
    I am also looking for the latest ROC files for it as well.
    My email is in my profile.
    Thanks.

    kontrol out
    "Good" - Jocko
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Interoperability? You can't handle interoperability!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora Watch it here!

  18. #38
    Join Date
    Mar 2009
    Location
    VB
    Posts
    323
    Post Likes
    Email sent>>>>

    ph33r , I hope you dont mind, I dont want to over step my boundries...

  19. #39
    Join Date
    Nov 2006
    Location
    New Hampsha'!!!
    Posts
    365
    Post Likes
    Quote Originally Posted by berg2666 View Post
    Having to change graphics for a new controller and chaging user privs and passwords but getting an error stating "Sharing Violation" and "DB Error"

    Bactalk 2.3 front end with Alerton BTI's and Alerton devices in two buildings, Delta Controls devices in another building with one FEC, Delta Controls devices in another building.

    The graphics need to be changed for the one device were a delta DAC was taken out and FEC installed.

    Do not have any manuals except the two boardsmoker sent me recently.

    LTBT-TM-PRGRMR and
    now I can not find the other
    can i get a copy of whatever he sent you?????

  20. #40
    Join Date
    Oct 2007
    Location
    Northeast
    Posts
    29
    Post Likes

    Share the wealth.

    Your gona share that? Right refrige-nate?

+ Reply to Thread
Page 2 of 35 FirstFirst 12345678912 ... LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •