    Whirlpool Tub Bond / Ground

    I just remodeled my master bath, I did the electrical and ventilation upgrade myself. Permit was pulled by Master Electrician. Inspector failed an existing Whirlpool pump due to no bond wire to a ground rod. I installed this. Master said it wasn't needed and maybe dangerous in certain conditions. BTW all piping to the tub is either PEX or PVC, including to the jets.

  2. #2
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    5,155
    Post Likes
    If you are saying the inspector required a separate ground rod for the pump, I agree with your electrician.
    However, as you know , arguing with an inspector is usually a waste of time.

  3. #3
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    3,419
    Post Likes
    If you put in a separate ground rod just for the pump that is wrong.