    Hmm 2 Phase Roof Top Units?

    Presently an HVAC Contractor, I remember many years ago I was involved with removing 5 ton RTU that where not single or three phase. I believe the electrician called them two phase units. I vaguely remember they had to run another wire from the main distribution center to hook up to the new 3 phase RTUs. Can someone here explain how they where wired, how many line voltage wires where needed. Did those types of system use a 2 pole contactors for the compressor, or a standard 3 pole contactor. What was the common voltage used for those type of units.

  2. #2
    Join Date
    Aug 2013
    Location
    Visalia California 93291
    Posts
    7,915
    Post Likes

  3. #3
    Join Date
    Jan 2014
    Location
    New England/Florida
    Posts
    14,310
    Post Likes
    Thread Starter
    Quote Originally Posted by lkapigian View Post


    " This type of service happens to exist in Hartford, Connecticut. It does serve a few buildings in that city."

    Thank you for the general info on two phase , Interesting, that the info you sent me mentioned Hartford CT. as still being used in a small area of town, as those RTU where located in that general vicinity. Hopefully some old timer electrician here can fill me in on the details. I vaguely remember they where Carriers with possibly Carlyle semi hermetic compressor.

    Kind of makes me wonder what type of power was feeding Dunham-Bush factory, as it was based in Hartford Ct. years ago, single,two, and three phase?

  4. #4
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    The two wires are out of phase... Not a mirrored sine

  5. #5
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Two phase was fairly common in some places. All of it that I ever worked on required four wires.

    I saw lots of those Carrier water-cooled self-contained units which were two phase but never a RTU.

    Where was this job you remember?

    PHM
    --------

    Quote Originally Posted by Bazooka Joey View Post
    Presently an HVAC Contractor, I remember many years ago I was involved with removing 5 ton RTU that where not single or three phase. I believe the electrician called them two phase units. I vaguely remember they had to run another wire from the main distribution center to hook up to the new 3 phase RTUs. Can someone here explain how they where wired, how many line voltage wires where needed. Did those types of system use a 2 pole contactors for the compressor, or a standard 3 pole contactor. What was the common voltage used for those type of units.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  6. #6
    Join Date
    Jan 2014
    Location
    New England/Florida
    Posts
    14,310
    Post Likes
    Thread Starter
    Quote Originally Posted by Poodle Head Mikey View Post
    Two phase was fairly common in some places. All of it that I ever worked on required four wires.

    I saw lots of those Carrier water-cooled self-contained units which were two phase but never a RTU.

    Where was this job you remember?

    PHM
    --------
    Post #3 mentions where the units where located, apparently they are still around in a very few buildings in Hartford Ct. and more so in Philly PA.

    " There remains, however, a two-phase commercial distribution system in Philadelphia, Pennsylvania; many buildings in Center City are permanently wired for two-phase[citation needed] and PECO (the local electric utility company) has continued the service. This type of service happens to exist in Hartford, Connecticut. It does serve a few buildings in that city."

    OK, if you worked on it and it used four wires ,then they pulled one line voltage wire out instead of adding one wire, ( as I mentioned ) as the new replacement RTU's where three phase. That time frame was in the later 70's . Did they use four pole contactors For the compressor ? What phase where the blower motors and outdoor motor, can you get single phase from two phase to run those motors?

  7. #7
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Philadelphia is where I saw it. Around D and Erie Streets. It's not everywhere in the city - but I know it was there. We would just have the compressors and motors rebuilt as they failed. As manufacturing closed up out there there was lots of two-phase shop equipment available for dirt cheap. Welders, machine shop equipment, etc. Of course it was all useless anywhere else. <g>

    PHM
    -------




    Quote Originally Posted by Bazooka Joey View Post
    Post #3 mentions where the units where located, apparently they are still around in a very few buildings in Hartford Ct. and Philly PA.

    There remains, however, a two-phase commercial distribution system in Philadelphia, Pennsylvania; many buildings in Center City are permanently wired for two-phase[citation needed] and PECO (the local electric utility company) has continued the service. This type of service happens to exist in Hartford, Connecticut. It does serve a few buildings in that city.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  8. #8
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    The motors take 4 wires? Ph1,2,n,grand???

  9. #9
    Join Date
    Jan 2014
    Location
    New England/Florida
    Posts
    14,310
    Post Likes
    Thread Starter
    " they may use a four wire delta connection to supply both 120:240 Volt single phase loads and 240 volt three phase loads."

    Maybe that's what those units where? The 240 volt three phase for the compressor and for the blower motor and outdoor fan motor it was the 120 volt single phase ?


    On a side note:

    " Years ago large air conditioners were not available in single phase. Large homes in the south could have a four wire delta service fed from such an arrangement to power large air conditioners.
    The 208 Volts to neutral on the third phase is called the wild leg or the high leg."
    Last edited by Bazooka Joe; 01-21-2016 at 09:45 PM.

  10. #10
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    3,419
    Post Likes
    Its actually 3ph 240v power, but it only uses 2 transformers. The middle B phase is grounded so you have 240v from A and C phase's to ground but no voltage reading from B phase to ground, it will read 240v between any 2 conductors but no 120v available. Doesn't seem like it would work but it does.

  11. #11
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    3,419
    Post Likes
    Quote Originally Posted by Bazooka Joey View Post
    "

    " Years ago large air conditioners were not available in single phase. Large homes in the south could have a four wire delta service fed from such an arrangement to power large air conditioners.
    The 208 Volts to neutral on the third phase is called the wild leg or the high leg."
    Different type of 3 phase than what the OP ran into, but your right what your referring to is a wild leg 3ph. 2 legs read 120v to ground but 3rd leg reads 208v to ground. You get 208v between any 2 feed conductors. Here in KC we have four types of 3 phase, 240v delta, - 240v grounded B phase delta (what used to be called 2 phase, - no usable 120v on either types of 240v delta's.
    Also standard 120v - 208v Wye that is most common, and the 120v - 208v wild leg Wye configuration your talking about. ( I have burnt out 2 vacuum pumps by hooking them up to the 208v to ground wild leg.

    I'm an old Master Electrician and my dad was a KCP&L lineman for 40 years and I still don't fully understand the 4 different types of 3 phase power we have here.

  12. #12
    Join Date
    Aug 2015
    Location
    Pensacola
    Posts
    116
    Post Likes
    https://en.wikipedia.org/wiki/Two-phase_electric_power. Good luck in finding 2 phase equipment.

  13. #13
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    2 phase power requires four power conductors and a grounding conductor.

    It is still produced from the generated 3 phase for Center City Philadelphia using Scott-T transformer arrays, for feeders that run mostly along Walnut Street.

    So if those rooftop units were 2 phase, each one would have four conductors and a ground going to it.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  14. #14
    Join Date
    Jan 2008
    Location
    LEHIGH VALLEY, PA
    Posts
    858
    Post Likes
    Yes me to lost a recovery machine to a wild leg , on a compressor change out , make sure to check in future the voltage of phase to ground before using my cheater cord.

  15. #15
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    What is the two-phase power used for these days?

    PHM
    -------



    Quote Originally Posted by timebuilder View Post
    2 phase power requires four power conductors and a grounding conductor.

    It is still produced from the generated 3 phase for Center City Philadelphia using Scott-T transformer arrays, for feeders that run mostly along Walnut Street.

    So if those rooftop units were 2 phase, each one would have four conductors and a ground going to it.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  16. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    What is the two-phase power used for these days?

    PHM
    -------
    There are two answers.

    The first answer is that newly remodeled stores with new panels will get their own Scott-T transformer to produce a three phase source to run RTU's and such.

    The other use is to power an existing 2-phase power panel, where each phase pair is a 240 volt feed that can power 240 volt loads. There are very likely some old elevators that run on the 2-phase.

    Mostly, the feeds power a transformer. I think all of the motor-generator sets are gone, but I could be wrong.

    This is done to avoid having to pay for a new 3-phase conductor set to be brought in from the street. With permits and excavation costs, that be well in excess of $10 - 15k, and most of the corporates that rent store spaces along Walnut will do anything to avoid a complete service replacement. On top of that figure, there are metering cabinets and CT transformers that can raise the cost to $20k.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •