    Help with Coleman manufactured home gas furnace

    Gentleman

    I need help with a manufactured home gas furnace. I don't see to many. Attached pics. System lights, but flame just kind of floats. Stays lit, fan pops on but flames just floats, and no real heat comes out of registers. I checked gas pressure its of 6.5" and 3.5" wc coming out. It's got a deflector that flame is supposed to hit in heat exchanger. Cold air out of registers cause not enough of a flame. Heat exchanger ok, turned fan on and off flame didn't change. I think it's just a single office on burner. Not enough flame to do anything. Anyone familiar with this Coleman furnace.Name:  image.jpg
Views: 2376
Size:  71.0 KBName:  image.jpg
Views: 896
Size:  51.5 KB

  2. #2
    Join Date
    Aug 2012
    Location
    Portland, Or
    Posts
    289
    Post Likes
    Thread Starter
    Direct vent, and I opened up system and added air where gas valve mounts. No change. Natural gas. What's the brass fitting with blue rubber on it?

  3. #3
    Join Date
    Mar 2012
    Location
    North Vernon, Indiana
    Posts
    118
    Post Likes
    Spider in orfice

  4. Likes kamersoutdoor liked this post
  5. #4
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    3,275
    Post Likes
    Quote Originally Posted by Brown Tech View Post
    Spider in orfice
    This
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  6. #5
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    7,183
    Post Likes
    X2 on spider since gas pressure is correct.
    AOP Rules: Rules For Equipment Owners.

    Free online load calculator: http://www.loadcalc.net/


    There = not here. Their = possessive pronoun. They're = they are
    It's = contraction of it is. Its = the possessive form of it
    Too = also. To = expressing motion. Two = 2
    Then = after that, next. Than = indicates a comparison.
    Questions should end with a question mark "?" Statements end with a period "."

  7. #6
    Join Date
    Aug 2012
    Location
    Portland, Or
    Posts
    289
    Post Likes
    Thread Starter
    Your probably right. Thanks

  8. Likes kdean1 liked this post
  9. #7
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    11,620
    Post Likes
    Quote Originally Posted by Iceman_pdx View Post
    I need help with a manufactured home gas furnace.
    I emailed you the service manual in case you want to review them.
    Instead of learning the tricks of the trade, learn the trade.

  10. #8
    Join Date
    Jan 2005
    Location
    West Central Illinois
    Posts
    65
    Post Likes
    x3 on spider or spider web in orifice.

  11. #9
    Join Date
    Apr 2011
    Location
    Cayuga, In
    Posts
    78
    Post Likes
    Just had same thing little while ago. It was a spider and web in orfice, same furnace.

  12. #10
    Join Date
    Feb 2004
    Posts
    2,846
    Post Likes
    Spider. Me too. Found many times.

  13. #11
    Join Date
    Dec 2015
    Posts
    3
    Post Likes
    Yep a spider will do it. Also if you don't know what the brass fitting with the blue coating is you probably shouldn't be working on it.

  14. #12
    Join Date
    Aug 2012
    Location
    Portland, Or
    Posts
    289
    Post Likes
    Thread Starter
    YES it was a spider!

    LDD we don't see many manufactured house gas furnaces out here. 99% of all manufactured house units are heat pump systems. First time I've seen this gas valve. I just saw a blue cap and didn't look at it. A little different looking than my regular GV. I just hopped on here asking a question. So thanks for the tip dude. Pressure regulator

    Just got back to job, customer was out of town for holidays and they had a fireplace till I got back. Late night call Xmas eve and I hate when I'm in a hurry and if I can't get back to job at least I can hop on HVAC-TALK till I return. Thanks guys and yes it was a spider and a nest in orfice. Dumbass here always appreciate the help from you guys

  15. #13
    Join Date
    Dec 2015
    Posts
    3
    Post Likes
    Iceman glad you got it working that's whats important. The brass fitting with the blue coating is the gas connection line it is pretty common on most equipment. I will say however it is usually yellow, I would check that one and make sure it as an AGA or UL rating for gas use.