    YVAA high IGBT temperatures

    Hi folks,

    Just been looking at a YVAA chiller on a site and the IGBT temperatures are running high.
    It's not causing a problem just yet, but its heading that direction.

    When the chiller is running system # 1 IGBT temp could be about 80+ DegC and System # 2 would typically be at about 60 DegC.
    Its strange that both systems are different when they are on the same loop.
    Internal ambient temp is 30 to 35 DegC.

    Glycol has been changed and there is no air in the system. Both cooling coils are very clean.
    Pump is running fine so no problems there. You can actually feel the high temp differential entering and leaving the IGBT's on the pipe fitting on the back of the panel.

    Only thing I can think of would the heat compound on the plates be causing an issue?
    Any come across this problem before?

    It seams to be getting steadily worse over time, and he heading toward the trip point.

    Any help greatly appreciated.

  2. #2
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,554
    Post Likes
    "Glycol has been changed and there is no air in the system"

    Are you absolutely certain of that? We needlessly replaced a pump on a YS before we realized air was the problem. We were certain it was the pump.

    "... high temperature differential entering and leaving the IGBT's ..."

    Low coolant flow will result in a high differential. Higher than normal. Numbers here (actual temperature readings of coolant in and coolant out) would be helpful.

  3. #3
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,000
    Post Likes
    If a newer chiller , 3-4 years old, the cooling loop is now separate coils hanging on the side of condenser coil "V" and fans are driven off VFDs . So if subcooling is at set point fans will be running slower and glycol temps. could higher then what was seen with straight driven fans.
    Get some temps. in and out. The copper block that the IGBTs are sitting on is a single pass of coolant and the pipe connections are only 3/8 inch. I would drain out coolant and try back flushing the plate use water not a lot of pressure top of plate is held on with a lot of small screw and a thin o-ring. Try to catch the out flow in a clean bucket to see if something was in there.


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Feb 2004
    Location
    Northwest GA
    Posts
    624
    Post Likes
    80*C is a little high, curious what was outdoor ambient and machine load when you saw 80*C? Interesting, cabinet temps were ok. I had a pair of YVAA's that the VSD cooling loop became contaminated by some substance that caused complete fouling. We suspect someone added something other than JCI/York coolant or contaminated coolant. Wound up cleaning loops and changing out the coils. I wouldnt suspect the heat compound unless this is a new machine and the issue has been a problem from the start or the plates have been pulled for some reason.
    I have seen where the coolant has been changed and needed to be topped off after a few days.
    Superheat, that must be REALLY hot.

  5. #5
    Join Date
    Jun 2003
    Location
    Gulf Coast
    Posts
    244
    Post Likes
    Have IGBT been removed? If so was fresh transfer paste used
    I recently worked on a YCIV with the same issue turns out the another company remover IGBT for a visual inspection not sure why
    after i removed old paste and used new no more temp issue

  6. #6
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,000
    Post Likes
    Wow that's a lot of work just to look at the IGBTs. Really wonder about people sometimes.


    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Jul 2015
    Location
    Ireland
    Posts
    225
    Post Likes
    Thread Starter
    Thank you for all the feedback. Best to take it one step at a time..

    Nuclrchiller - Definitely no air in the glycol system. When the machine in running, glycol level is about 6 - 8 inches below the filler cap. The pump was run as soon as coolant reached the top of filler tank to circulate it throughout the system.
    I will try and get you actual number today and post later this evening.

    Chev - Correct, the chiller is about 3 years old and does indeed have the separate coils hanging on the V and fans are all variable speed.
    I'll get actual numbers and suggest back flushing the system. Might tell us if there is a blockage in it.

    Turbomaster - Over here yesterday was about 10*C so pretty cold. Which should even help lower the coolant temp albeit if the fans are running slower due to subcooling at setpoint. What would you use to flush out the system if fouling is suspected?

    Waltervan - No IGBT's never removed. This issue has been getting steadily worse over the past 6 - 12 months I guess. So its telling me that its either fouling or a blockage in the system somewhere.

    I will try and get actual temperatures and load conditions today and report back.

    Thank you all. Have a good one.

  8. #8
    Join Date
    Jul 2015
    Location
    Ireland
    Posts
    225
    Post Likes
    Thread Starter
    OK guys,
    Quick update.
    Apparently the wrong coolant has been used in this machine. The result is that the coolant is mixing into a sludge type liquid in the micro channel coolant coils on the side of the chiller.
    This is then causing flow issues and heat transfer problem as you might imaging through the tubes in the coils.

    Looks like it need to be drained out and coils taken off and flushed clean.

    I'll keep you posted and thanks again for your help.

  9. #9
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,000
    Post Likes
    What did they mix to make it foul up so bad? Would be a help for others to know, keeps people from droping in to site and only reading part of the story. Might save someone else a headache.

  10. #10
    Join Date
    Jul 2015
    Location
    Ireland
    Posts
    225
    Post Likes
    Thread Starter
    Trying to find out some more history from the site guys. As soon as I do I will let you know.

  11. #11
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,000
    Post Likes
    Thanks


    Sent from my iPhone using Tapatalk

  12. #12
    Join Date
    Nov 2013
    Location
    Texas
    Posts
    590
    Post Likes
    FYI, there are several types of antifreeze that are not compatible. This is something run into with cars and trucks, more than chillers I suppose. But, in case I'm referencing, green is not compatible, with blue, red, or orange. It turns to sludge.

    Not suggesting that is the case here, just a thought: Maybe someone topped it off with some anti freeze from a parts store?

    Otherwise, sub'd..... I'm curious as well.

    Chase


    Sent from my iPad using Tapatalk

  13. #13
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,000
    Post Likes
    The lengths people will go to not to buy , yes we charge a lot for the glycol, the right stuff has now cost way more due to repairs.