    Measuring Static Pressure

    35-Ton Vertical Packaged unit. Has a factory supplied plenum with 8 equal sized grills for outlets. Return is wide open to the filter rack, no ductwork.
    Can I simply place my manometer in front of the filters then drill a hole in the side of the plenum to take an ESP reading? Does it matter the location
    in the plenum (it's 9 feet long) ?

  2. #2
    Join Date
    Jan 2012
    Location
    Dallas
    Posts
    597
    Post Likes
    Static pressure would build on the supply side any where on the supply side. So think about it this way in the RTU you would still be on the supply side. Drill a tap into RTU cabinet and your still on the supply side just make sure it's after the blower wheel cabinet. Return side yes you can take measurement before filters same thing drill Into cabinet just mark where to not hit anything you shouldn't. These are good place to use for your delta t and static pressure.

  3. #3
    Join Date
    Apr 2015
    Posts
    14
    Post Likes
    Quote Originally Posted by jman2794 View Post
    Static pressure would build on the supply side any where on the supply side. So think about it this way in the RTU you would still be on the supply side. Drill a tap into RTU cabinet and your still on the supply side just make sure it's after the blower wheel cabinet. Return side yes you can take measurement before filters same thing drill Into cabinet just mark where to not hit anything you shouldn't. These are good place to use for your delta t and static pressure.
    External statics should be taken outside of the RTU...such as in ductwork where possible. Delta T's should be taken before & after coil which may require more holes being drilled in unit.

  4. #4
    Join Date
    Jan 2012
    Location
    Dallas
    Posts
    597
    Post Likes
    Quote Originally Posted by Ray Esquivel View Post
    External statics should be taken outside of the RTU...such as in ductwork where possible. Delta T's should be taken before & after coil which may require more holes being drilled in unit.
    Good catch Ray. I'm missed ESP; I don't use that or have in the past. Now it be nice to see how the original question is answered since it seems you may use this formula and apply it more than most of us. If not at least you helped defined the difference

  5. #5
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    I am not a TAB or NEBB certified guy and if someone needs or an engineer requires such exhaustive reporting, then they can obtain the services from such entities or we can sub-contract one for them.

    However, if I am troubleshooting or performing a BASIC commissioning of a particular piece of equipment, and I am searching for a relatively close/approximate ESP of a unit/system I am sometimes limited to where I can take such readings. A residential furnace/air-handler is really not to complicated with the exposed SA and RA duct work, along with rooftop units that utilize horizontal duct. But when it comes to rooftop equipment that sets on a curb with vertically installed and usually unaccessible duct locations, I will utilize the compartment most closely associated with the RA and SA duct.
    If one needs more exact measurements then one will need to access the main trunk lines about 5 feet aft of any turning elbows and prior to any take-offs. If we are talking about concentric kits, these can become a bit tough since you may need a very deep pitot/static tube to reach through into the inner RA duct.

    To become even more exact, one would need to utilize duct tranversing methods.

    So on a rooftop unit setting on a curb I will remove the filters and utilize the engineering manual to verify that their blower performance charts include the evap coil, heat exchangers, steam coils, electric heat strips, or whatever is in there. If the charts do not include some or all of these possible points of static drop, then I am utilizing the engineering to find their listed static drops to add to my over-all calculations.

    It is important to also know exactly which blower package and drive package was either factory or field installed. You have low, normal, and high static options with a myriad of drive kits to achieve specific cfm needs based on the calculated static across the over-all system. By knowing which blower chart to reference will assist dramatically.

    There are a few basic links that I guess are appropriate for the OPEN forums:
    http://contractingbusiness.com/comme...atic-pressures
    http://contractingbusiness.com/enews...s/cb_imp_69579
    http://contractingbusiness.com/archi...ressure-part-2

  6. #6
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    The system you described is not really conducive for measuring static pressures. The air balance certification agents consider field measured static pressures as approximate. There are several reasons for this which include access to the best place to measure, fan blast area and airflow is dynamic. I'm not saying to not take them but don't bet your entire pile of chips on static pressures alone. Temperature measurements have similar problems with almost all including stratification.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •