    Stupid dual fuel question

    When setting up dual fuel, I normally set the lock out at 35 degrees F. Should I disable the W/W1/W2 wire to not turn on the furnace during defrost?

    I have not done many dual fuel systems.

    Any help appreciated.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

  2. #2
    Join Date
    Jan 2010
    Posts
    18,708
    Post Likes
    Single, Duel, or modulating furnace ?

  3. #3
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    2,970
    Post Likes
    Thread Starter
    Single
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

  4. #4
    Join Date
    Jan 2010
    Posts
    18,708
    Post Likes
    I believe you can run the furnace during defrost to temper the air. With a low fire furnace option I see no problem. Seeing how your furnace is single stage I can't say it would be fine but I'm sure the residential pros will chime in and confirm. Which t-stat will you be using ?

  5. #5
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    2,970
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    I believe you can run the furnace during defrost to temper the air. With a low fire furnace option I see no problem. Seeing how your furnace is single stage I can't say it would be fine but I'm sure the residential pros will chime in and confirm. Which t-stat will you be using ?
    Thanks for the response.

    T-stat is Honeywell 6000 Focus Pro
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

  6. #6
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    40,603
    Post Likes
    Focus Pro? Do you have a dual fuel kit?

    We always hook up W or W1. Takes my friggin' furnace so long to fire that I get a blast of 40 air every defrost. I have a friggin' timed defrost which even at 90 minutes, goes in way too many times.

  7. #7
    Join Date
    Feb 2015
    Location
    Ohio
    Posts
    1,168
    Post Likes
    There are a few variables I take into consideration when making this call. One of them includes your backup heat source. If it is electric, I prefer to have one stage kick in with defrost. If it's gas or oil, it depends on how many stages your furnace is, 2 stage, I'll kick in low fire, if it's single stage I usually do not use backup for defrost unless the heat pump is running unrestricted or with a low lockout for whatever reason. This also relies on the defrost demand, if it's a timed defrost you have to weigh the value of firing so frequently. One thing I'm picky about is always using a worthy thermostat with dual fuel setups. Always use an outdoor temp sensor.

  8. #8
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    2,970
    Post Likes
    Thread Starter
    Quote Originally Posted by taylor2 View Post
    There are a few variables I take into consideration when making this call. One of them includes your backup heat source. If it is electric, I prefer to have one stage kick in with defrost. If it's gas or oil, it depends on how many stages your furnace is, 2 stage, I'll kick in low fire, if it's single stage I usually do not use backup for defrost unless the heat pump is running unrestricted or with a low lockout for whatever reason. This also relies on the defrost demand, if it's a timed defrost you have to weigh the value of firing so frequently. One thing I'm picky about is always using a worthy thermostat with dual fuel setups. Always use an outdoor temp sensor.
    Thanks. Good info.

    I always use and outdoor sensor as well.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •