    Baffle design to reduce noise of return

    I have an extremely noisy air return located at the entrance to my living room. It drowns out conversation and even the TV. I've looked through some of the posts here and I realize that the ideal thing would be to have a lot of duct between the return and the furnace, but I don't really have that option here. A friend suggested putting a system of baffles in the return to force the air to make some turns, he says it should reduce the noise quite a bit.

    I whipped up a 3D model of a baffle system for my return and attaching it here, along with a photo of the return with furnace sitting directly above it. Im in a 1000 sq ft "shotgun" style house, return is just above floor level, furnace/coil sitting on top of it, all the vents are in the ceiling. The return cavity is quite large - about 20"(w) x 38"(d) x 32" high - but the grill and filter for it are only 16x24. (Yes, about 4" of the 24" grill are obstructed by drywall as seen in photo.)

    I don't know the specs for my system but I do know the model number - it is a Payne PG8DAA. There is another piece of paper showing a model PA10 but I don't know what that is referring to. The filter size for the return is 16x24. It sucks air in like a tornado!

    I wonder:
    1) What do you think of this baffle system, do you have any design suggestions?
    2) I could cut a second intake hole into the wall of the return directly opposite the existing one, would that be beneficial?

    Name:  AC Return Baffle.jpg
Views: 58569
Size:  205.7 KB

    Name:  AC Return.jpg
Views: 47425
Size:  120.9 KB

    Thanks for any advice.
    Dan in New Orleans

  2. #2
    Join Date
    Aug 2011
    Posts
    2,970
    Post Likes
    ,nice drawing with measurements how did you do this?? Sorry I cannot help you with your answers someone will chime in soon I am curious myself if your design will work?

  3. #3
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    With the large return you have, the baffles you are planning should dramatically help. However, metal, or wood will not work. You will need a contractor to build it out of duct materials.
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  4. #4
    Join Date
    Jun 2015
    Posts
    6
    Post Likes
    Thread Starter
    I created the 3D drawing in Google Sketchup - its a free program you can download:
    sketchup dot com / products / sketchup-make
    (take out all the spaces and replace "dot" with "." Since I am new to forum, it won't allow me to post links!)

  5. #5
    Join Date
    Jun 2015
    Posts
    6
    Post Likes
    Thread Starter
    I actually am planning on constructing the baffles out of this 1/2" thick insulating foamboard sheathing they sell at home depot called Foamular, it has R-3 thermal rating but I was told it was the best thing they had for sound absorption. Going to affix it to the inside walls of the return and leave some slots where the baffles, same material, will fit. Maybe Lowes has something better?

    Im really wondering if I should add another inflow grill to the opposite side of the return, if having more draw will help cut down on noise and maybe increase efficiency some? This is where I have absolutely no experience.

  6. #6
    Join Date
    Jan 2008
    Location
    Phoenix Arizona
    Posts
    1,663
    Post Likes
    Just keep in mind a return is only as big as the smallest opening...if your baffle chokes down to a opening smaller then the unit requires for cfm you can starve the system(though it has to be pretty drastic)...
    "If history repeats itself I am so getting a dinosaur"

  7. #7
    Join Date
    Aug 2011
    Posts
    2,970
    Post Likes
    Quote Originally Posted by 504 Tailwaggers View Post
    I created the 3D drawing in Google Sketchup - its a free program you can download:
    sketchup dot com / products / sketchup-make
    (take out all the spaces and replace "dot" with "." Since I am new to forum, it won't allow me to post links!)
    thank you for the info Google SketchUp. very interesting thread learn something everyday.

  8. #8
    Join Date
    Aug 2011
    Posts
    2,970
    Post Likes
    Hrdworkingacguy - return is only as big as the smallest opening. I have heard that before but don't understand it. on a vacuum pump why is it beneficial to have a large hose when it hooks into a small Schrader port? And for 504 tailwaggers would it be a good idea beneficial for him to put in a nother return grille??

  9. #9
    Join Date
    Jun 2015
    Posts
    6
    Post Likes
    Thread Starter
    My existing inflow opening is really only 16"x20" (even though grill is 16x24) because whoever constructed this return obstructed the opening with a 4" thick additional drywall, you can see it in the photo. Maybe it was necessary to support the furnace above it. Anyways, I don't know how to calculate the necessary cfm but I wonder if I put another opening on opposite side, it might slow down the airflow and help reduce noise, not to mention increase efficacy of the unit. Ive heard of returns being too small - can they be too big? Doesn't the size of the "coil" have something to do with this too?

  10. #10
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    Line the cavity with duct board.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  11. #11
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    the noise you are hearing is coming from the blower itself. adding a second inlet grille will not help with the noise. the baffles will, as long as there is good liner in the box, no smooth reflective sides, and the sound has something to bounce off of, and get absorbed by.

    do not make any obstructions that are smaller than twice the furnace opening size. I STRONGLY recommend you get a contractor to do it, with proper ductwork materials.
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  12. #12
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    don't use foam in the return.

    I'd start by lining the return as suggested above,
    with duct board.
    sides & bottom should be covered with ductboard
    with fg side facing into the return to absorb sound.
    paint the mastic on the walls of the return, then set the
    duct board into the mastic. once lined...mastic the
    joints.

    while you are working around in there...seal the sides
    of the return.
    I can see the leakage from here!
    on the right side the opening at the lower
    side of the r/a filter grill. on the left side seal the opening
    between the 2x & whatever is to the left of the 2x.
    take a look at the top of the r/a filter grill. if it is an
    opening into the wall...seal it up.

    sounds like a trip to the hvac supply is in your future.
    I'd use low R-value ductboard...R-4.2 if you can get it
    or R-6. you don't need the R-value but don't want to
    lose too much of the size of the return.
    bucket of paint on mastic & chip brushes should
    set you up...and maybe some caulk.

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  13. Likes captube liked this post.
  14. #13
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,427
    Post Likes
    Does the noise change at all when you take the grill front off?
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  15. #14
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    what size system do you have & what size is the r/a filter grill?

    you have room to increase the r/a filter grill & filter.

    oh I see...16x24. you can't have too much return.
    my 2 ton system has a 24x24 r/a filter grill.

    what is your location?

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  16. #15
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Start off with the concepts:
    1. You want slow air speeds and big ducts / low velocity.
    2. You want a convoluted sound path.

    First: has the system been air balanced with the purpose of reducing the air flow to the lowest correct amount of air volume? Or did the installer just set the blower on high and take the check? Perhaps a lower blower speed can be used? The ideal would be a large blower operating at low speed blower to acheive the required air volume. Too late for that now but keep the concept in mind as you work.

    1. You want to 'confuse the sound waves'.
    2. You do not want to create any pinch-points for the air flow.
    That is: do not make any portion of the air flow path smaller than the opening to the bottom of the furnace.
    3. Angled surfaces are your friend in this endeavor - you want to confuse the sounds waves / bounce them around / make them work to escape.
    4. You want to absorb rather than bounce the sound - so line the plenum with sound absorbing material and cover the baffles with it as well.

    I like the 'build a decorative column' for the air handler - I am going to steal that idea. But I would have returns on all available sides. Is this system for A/C as well? If so I hope you have ceiling fans in all the rooms - that low air return will badly compromise cooling performance.

    I assume this is a rancher style house? Is there a garage? Could the air handler / furnace have been installed out there? That's what I typically do. Are all the air ducts inside the conditioned space? In a soffit? Or do they go up into the attic space?

    PHM
    ----------




    Quote Originally Posted by 504 Tailwaggers View Post
    I have an extremely noisy air return located at the entrance to my living room. It drowns out conversation and even the TV. I've looked through some of the posts here and I realize that the ideal thing would be to have a lot of duct between the return and the furnace, but I don't really have that option here. A friend suggested putting a system of baffles in the return to force the air to make some turns, he says it should reduce the noise quite a bit.

    I whipped up a 3D model of a baffle system for my return and attaching it here, along with a photo of the return with furnace sitting directly above it. Im in a 1000 sq ft "shotgun" style house, return is just above floor level, furnace/coil sitting on top of it, all the vents are in the ceiling. The return cavity is quite large - about 20"(w) x 38"(d) x 32" high - but the grill and filter for it are only 16x24. (Yes, about 4" of the 24" grill are obstructed by drywall as seen in photo.)

    I don't know the specs for my system but I do know the model number - it is a Payne PG8DAA. There is another piece of paper showing a model PA10 but I don't know what that is referring to. The filter size for the return is 16x24. It sucks air in like a tornado!

    I wonder:
    1) What do you think of this baffle system, do you have any design suggestions?
    2) I could cut a second intake hole into the wall of the return directly opposite the existing one, would that be beneficial?

    Name:  AC Return Baffle.jpg
Views: 58569
Size:  205.7 KB

    Name:  AC Return.jpg
Views: 47425
Size:  120.9 KB

    Thanks for any advice.
    Dan in New Orleans
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  17. Likes HVAC_Ryan liked this post.
  18. #16
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    I missed the part where you said you could add another
    r/a on the other side. might be the easiest solution.
    but still...air seal that return!!

    best of luck
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  19. #17
    Join Date
    Jun 2015
    Posts
    6
    Post Likes
    Thread Starter
    Firecontrol, the noise does not change one bit with the grill off. But I did slide in a piece of foamboard, angled down from the top of the grill, as a test to force the air to move down towards the floor and then make a sharp turn upward toward the furnace, and it cut down the noise level quite a bit. Hopefully in combination with insulating the return walls and sealing up leaks, it will cut the sound even more without damaging performance.

    So Im going to go ahead with my baffle plan as illustrated. Will look for some duct board as suggested above by energy_rater_La, but I don't quite understand why I should not use this pink insulation board I bought that people at HD said would be good for sound absorption.

  20. #18
    Join Date
    Aug 2013
    Location
    Visalia California 93291
    Posts
    7,915
    Post Likes
    I would add additional returns on the sides, looks like you could have up to 4, line as mentioned above- install Bar Type returns not stamped faced filter grills raise the furnace and put a base below it--

    Also set your fan taps to the speed needed to match the design CFM

    OR.............Turn up the television , that would be my solution

  21. #19
    Join Date
    Jun 2015
    Posts
    6
    Post Likes
    Thread Starter
    I just realized there was a page 2! Sorry, only now just read the posts on this page.

    I do not know what this system is rated at - bought the house a year ago and HVAC came with it. Got a few quotes for moving it up into the attic but was way too expensive. House is a 1100 sq ft New Orleans "shot gun" style house - no hallways, must travel through every room to get from front to back. No garage.

    I will try to look up the specs on this HVAC tonight if I have time - all I know is the model is Payne PG8DAA and some other booklet by the furnace has Model PA10 written on it but it is so damaged I can't tell what its for!

  22. #20
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    glad you kept the unit out of the attic.
    bad enough that the ducts are up there.

    can you give us the model numbers from the
    condensing unit outside? that will tell us the
    size & thus the amount of return air needed.

    the reason for not using the foam board
    in the return is that it isn't an approved material.

    granted, the return air isn't going to be warm enough
    to cause foam to offgas, but any pro would use
    approved materials.

    attaching the foam board as you show raises questions.
    how would you hold it in place long term?
    if either piece comes lose it could block off the
    air flow to the coil, and that would be a very bad
    thing.

    lining the return with ductboard or creating another
    return air opening within the same r/a area
    would be your best options.

    ductboard is easy to install. measure twice,
    cut & install. all you need is a razor knife, tsquare
    & mastic. a few roofing nails to add extra
    holding...easy peasy.

    always use approved materials.
    astm isn't really just an acronym for
    another stupid testing method.

    and HD knows little about hvac standards.
    not their area of expertize.

    you should also think about sealing the ductwork
    in the attic. once it is cooler that is.
    average duct leakage is 30%.
    if you have a 3 ton unit...that is 1 ton of
    leakage before it even gets into the living space.
    plus your visible return leakage of course.

    thought you might be a New Orleanian when
    you said shotgun house. I've lived in quite a few
    there in the crescent city. good times for the most part.

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •