Results 1 to 13 of 14
    Apr 2012
    Ottawa,ont
    yellow jacket micron gauge 69075
    I tried starting my micron gauge today. It went to 0 right away and 3 seconds later gave me doted lines ---- i was just wondering why its doing that?
    Aug 2014
    DC suburbs
    I believe it means that the sensor is bad or there is a problem with the sensor plug not making a good connection. Also try a fresh battery.
  3. Likes buford liked this post
  4. #3
    Dec 2013
    Maryland
    Picked up brand new micron gauge today, when I was done using it, removed from circuit and turned it on just for ****s and giggles to see how atmospheric looked. To my dismay, I found that the reading zoomed right down to 600 microns... I left it on and several minutes later it had crept up to 2k microns. Mind you, the sensor had been disconnected from the circuit. I checked to make sure head unit had the correct sensor number in it. Definitely no oil what so ever in the sensor as well. Any suggestions YJ?
    M#69086
  5. #4
    Oct 2012
    Where we mow our own grass
    Quote Originally Posted by KellerW View Post
    M#69086
    Had the micron gauge been exposed to refrigerant?
    If a micron gauge gets exposed to refrigerant they will do that. It's normal. Once the refrigerant clears out it will all be good.
  6. #5
    Nov 2007
    Mississippi
    lightly blow across sensor after removing. Should quickly read atmospheric.
    M#69086
    Have wrench-Will travel
  7. #6
    Dec 2013
    Maryland
    Quote Originally Posted by Mike19 View Post
    No, the gauge was isolated from evacuated circuit and removed.
  8. #7
    Dec 2013
    Maryland
    Quote Originally Posted by socotech View Post
    Whilst that sounds very interesting, the problem I have is that I rely on my micron gauge to determine whether or not my circuit is properly dehydrated and I can't trust a gauge that won't show an accurate rise when its at atmospheric.... much less attached to the circuit I am evacuating.
  9. #8
    Nov 2007
    Mississippi
    I'm just suggesting to blow any residual refrigerant away from sensor when removed from circuit. This is what I do with mine.
  10. #9
    Aug 2011
    Fuquay varina, nc
    I have the 69075. I've had it for 3+ years. Love it and couldn't be happier. Original sensor, never fails. I keep it above any potential oil flow (usually the 1/4" charging port on my 4-way titan manifold). After confirming pressure test with nitrogen, I don't hook it up until the pump has been running for at least 30 mins and has quieted down a bit. I keep a bottle of 91% IPA on the truck. If I'm dealing with a nasty system repair, I clean the sensor with IPA immediately afterward while im changing vac oil... But I clean it no less than every 2 evacuations. If I had to guess, I've probly got 100+ hours on the original sensor. I'd buy it again in a second.
  11. #10
    Jul 2018
    If it's exposed to oil/refrigerant, is the alcohol enough to clean it out? Is there a good process for cleaning a very dirty sensor?
  12. #11
    Aug 2011
    Lewes, DE
    Quote Originally Posted by pafieldtech View Post
    holy cow, 91% IPA! I thought I was hard core drinking 3 Dogfishhead 120s
    Sent from my SM-G965U using Tapatalk
  13. #12
    Athens, Ohio
    Quote Originally Posted by Gross View Post
    Speaking which, my blood type is IPA Positive.
    AOP Rules: Rules For Equipment Owners.
    Free online load calculator: http://www.loadcalc.net/
    There = not here. Their = possessive pronoun. They're = they are
    It's = contraction of it is. Its = the possessive form of it
    Too = also. To = expressing motion. Two = 2
    Then = after that, next. Than = indicates a comparison.
    Questions should end with a question mark "?" Statements end with a period "."
  14. #13
    Nov 2003
    Montreal, Qc.
    My sensor is over 10 years old.
    It’s has been cleaned with IPA a couple of times when it was new.
    I then installed a ball valve on the sensor.