    JCI A350R Electronic Reset Control

    I have an A350P Discharge Air Control, D350 Discharge Air Display and a Y350 Power Pack 115Vac to 24Vac on a Cooling only AHU. Can I use an A350R Electronic Reset Control, to reset discharge temperature based on OutdoorAir temperature? All I see in JCI Literature is for resetting boiler temperatures.

  2. #2
    Join Date
    Feb 2008
    Location
    Pacific Coast
    Posts
    177
    Post Likes
    Given the built in limits of the Minimum Supply Temperature of the A350R:

    We recommend using an A350S (JCI LIT-930035) with a S350P (JCI LIT-930086) to accomplish the task.