    Nest Problems

    I installed a nest thermostat. I noticed that my Heat pump condensor fan was constantly running when not being called for heat or when the thermostat was OFF. I Called nest and they walked me through some diagnostics. They said my Y1 was shorted and constantly sending power out of it. They sent me a new base. I installed the new one, and ten minutes later i call for heat, shut it off and check the fan an hour later. Still running. I stuck the green wire in the y1 spot and the blower fan immedietly turned on inside. So it appears that this new base they sent me is also shorted!?

    Is it possible that they really could have send me 2 bad base plate. Or is it possible my system is the one shorting these base plates out.



    These are the wires i have

    Yellow - Y1
    Green - G ( fan )
    Orange - OB
    White - in W2 ( aux )
    Blue - C
    Black - * ( Emergency )
    Red - RH



    ( i put a meter accros my Red and Blue and i am getting 27 volts. I don't think this is enough to do damage )

  2. #2
    Join Date
    Jan 2010
    Posts
    18,044
    Post Likes
    and with Y1 disconnected what happens ?

  3. #3
    Join Date
    Jul 2012
    Posts
    34
    Post Likes
    Thread Starter
    if i disconnect y1 the condesor fan finally shuts off.

  4. #4
    Join Date
    Jan 2010
    Posts
    18,044
    Post Likes
    Do you have the replaced thermostat to reinstall and check the operation ?

  5. #5
    Join Date
    Jul 2012
    Posts
    34
    Post Likes
    Thread Starter
    if i re install the old trane baystat 239. It works fine, when i shut the heat off the heat pump aux and condesnor fan shut right off. ( the issue with this stat was it was not following set point) So it was either full on or off.

    But yes if i re install old stat it works properly.

  6. #6
    Join Date
    Oct 2014
    Location
    Palo Alto, California
    Posts
    64
    Post Likes
    Hi newtohvac13,

    If you could send me an email at hvac-talk@nestlabs.com, I'd be happy to check out your case to see what I can do to help.

    It's unlikely that you got 2 bad bases, and with some of the updates that have been done to the Nest base, it shouldn't be easily shorted out either.

    The 27V reading is fine, anywhere between 20-30V is fine for the Nest.

    ~Faris

  7. #7
    Join Date
    Jan 2010
    Posts
    18,044
    Post Likes
    Name:  BATSTAT 239 untitled.jpg
Views: 3217
Size:  103.8 KBIs this your old stat ?

  8. #8
    Join Date
    Jul 2012
    Posts
    34
    Post Likes
    Thread Starter
    Yes identical

  9. #9
    Join Date
    Jan 2010
    Posts
    18,044
    Post Likes
    Was the Nest Rep. able to resolve your problem ?

  10. #10
    Join Date
    Jul 2012
    Posts
    34
    Post Likes
    Thread Starter
    Not yet. Just sent him some info

  11. #11
    Join Date
    Jan 2010
    Posts
    18,044
    Post Likes
    OK, let us know how it works out. I'm sure he'll be able to assist you.

  12. #12
    Join Date
    Jul 2012
    Posts
    34
    Post Likes
    Thread Starter
    Thank you for your help

  13. #13
    Join Date
    Jul 2012
    Posts
    34
    Post Likes
    Thread Starter
    new base comes today, i do not want to install it until i hear back from nest. The rep is calling me today.