Thread: The Air Generate Heat Pump Water Heater

  1. #1
    Join Date
    Jan 2015
    Location
    Bellevue, Washington, United States
    Posts
    2,388
    Post Likes

    The Air Generate Heat Pump Water Heater

    I thought I'd share my experience with the Air Generate ATI66. First, you should know I live in a solar powered house so I try to minimize my power consumption. Since the Air Generate only used 1600 KW compared to an electric tank that uses 5000 KW it seemed like a great option. I really liked the quality of the heat pump unit. It used an R410a Panisonic compressor that achieved a 2.5 cop rating. It also used a reversing valve for occasional defrost and so the heat pump could heat the water even if my garage was 20 degrees.

    I used the ARI66 for 1,5 years but then one day the blower quit working and gave an A5 trouble code. I did a little investigating and found the pressure switch was throwing this code because the coil was icing over due to the fan not working. I did more checking and found Air Generate was having to warranty replace a lot of their tanks for this very same problem. I have friends who work at a water heater specialty installation company in Seattle and they literally have dozens of old Airgenerate tanks sitting in storage waiting to go back under warranty.

    What's unique about this issue is that most plumbers don't know how to work on heat pumps. The marriage of heat pumps to water heaters created a unique problem where Air Generate could not find qualified techs to repair their tanks in the field so the plumbers were replacing these $2000 tanks all together. When I diagnosed this problem I traced it back to a bad start capacitor located in the black control box. The part only costs around 2 dollars and only took about 10 minutes to replace.

    Later I sent an email to Air Generate and told them about my experience. A few hours later I got a call from the president of the company. He thanked me at least 10 times and told me how this information is going to save his company a small fortune. From my end as a HVAC contractor it didn't seem like such a big deal to just correct the problem. I hope this information is helpful in case any of you get calls on this product.

    BTW the start capacitor is a 2 uf and it's located in the black control box. If you want to make it easier to replace you can install the new unit on the outside of the black box and attach the harness from the fan motor. I hope this is helpful.

  2. Likes Ben14 liked this post.
  3. #2
    Join Date
    Mar 2013
    Location
    East Concord, NY
    Posts
    22,646
    Post Likes
    it sounds like the president of the company is (insert preferred adjective here) for not having smart engineers or techs who could figure out this little issue.

    So do you get a cut of all that money saved?
    Nest is POO!!

  4. #3
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    They need to look a little harder to find a warranty repair co, at least to try to fix, instead of replacing.

  5. #4
    Join Date
    Jan 2015
    Location
    Bellevue, Washington, United States
    Posts
    2,388
    Post Likes
    Thread Starter
    When they first started getting this code problem they tried having their plumbers replace the control board, and even the blower motors to no avail. The tanks are made overseas and it seemed like their engineers in the US weren't aware at first that their are 2 different capacitors for this unit: 1 for the compressor, and 1 for the blower motor.

  6. #5
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    Easier to troubleshoot than to just throw parts at it, but its their money. In the northwest area around seattle, we have lots of service providers that would like inside dry work, I know i do!

  7. #6
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,398
    Post Likes
    Quote Originally Posted by James Colver View Post
    I thought I'd share my experience with the Air Generate ATI66. First, you should know I live in a solar powered house so I try to minimize my power consumption. Since the Air Generate only used 1600 KW compared to an electric tank that uses 5000 KW it seemed like a great option. I really liked the quality of the heat pump unit. It used an R410a Panisonic compressor that achieved a 2.5 cop rating. It also used a reversing valve for occasional defrost and so the heat pump could heat the water even if my garage was 20 degrees.

    I used the ARI66 for 1,5 years but then one day the blower quit working and gave an A5 trouble code. I did a little investigating and found the pressure switch was throwing this code because the coil was icing over due to the fan not working. I did more checking and found Air Generate was having to warranty replace a lot of their tanks for this very same problem. I have friends who work at a water heater specialty installation company in Seattle and they literally have dozens of old Airgenerate tanks sitting in storage waiting to go back under warranty.

    What's unique about this issue is that most plumbers don't know how to work on heat pumps. The marriage of heat pumps to water heaters created a unique problem where Air Generate could not find qualified techs to repair their tanks in the field so the plumbers were replacing these $2000 tanks all together. When I diagnosed this problem I traced it back to a bad start capacitor located in the black control box. The part only costs around 2 dollars and only took about 10 minutes to replace.

    Later I sent an email to Air Generate and told them about my experience. A few hours later I got a call from the president of the company. He thanked me at least 10 times and told me how this information is going to save his company a small fortune. From my end as a HVAC contractor it didn't seem like such a big deal to just correct the problem. I hope this information is helpful in case any of you get calls on this product.

    BTW the start capacitor is a 2 uf and it's located in the black control box. If you want to make it easier to replace you can install the new unit on the outside of the black box and attach the harness from the fan motor. I hope this is helpful.
    Not trying to sound like I am knocking on you, but why do you have the water heater installed in a cold zone? It would seem to me you could pick up quite a lot of performance from the heat pump if it were in a warmer spot.

    I too am in the planning stages of building an off grid home, we plan on having a heated/cooled mechanical room for all the equipment.

    Just food for thought.

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  8. #7
    Join Date
    Jan 2015
    Location
    Bellevue, Washington, United States
    Posts
    2,388
    Post Likes
    Thread Starter
    GT Jets: I strictly follow the manufactures recommendations when I install a system and this is why I rarely have problems. Most of the issues people raise on this site are due to installer error. It says in the install manual that it must be installed in a location that receives outside air.

  9. #8
    Join Date
    Nov 2001
    Location
    Seattle, WA
    Posts
    8,352
    Post Likes
    I use to work on my share of ETech's HW heat pumps. Almost the same thing happened in that most problems I found were problems any basic HVAC guy/gal could find and solve. One had a leaking schrader & most has some sort of electrical problems such as a bad start/run cap.

    The problem was & still is that most users call plumbers. And most manufacturers use the lowest cost companies which typically means they have to be shown what a HW heat pump looks like.
    "The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
    - Alexis de Toqueville, 1835

  10. #9
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,398
    Post Likes
    Quote Originally Posted by James Colver View Post
    GT Jets: I strictly follow the manufactures recommendations when I install a system and this is why I rarely have problems. Most of the issues people raise on this site are due to installer error. It says in the install manual that it must be installed in a location that receives outside air.

    Really not trying to be an ass. but no, it doesn't.

    They can be indoors and only the exhaust air needs to go outside... The manual says in plain English that the temperature range is 20-120°F. It was only because of the 20°F comment that I made the earlier statement. I was just thinking that if you could feed it 60-70°F air in the winter, it would be more efficient.

    No offense intended.

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  11. #10
    Join Date
    Nov 2001
    Location
    Seattle, WA
    Posts
    8,352
    Post Likes
    Quote Originally Posted by GT Jets View Post
    Really not trying to be an ass. but no, it doesn't.

    They can be indoors and only the exhaust air needs to go outside... The manual says in plain English that the temperature range is 20-120°F. It was only because of the 20°F comment that I made the earlier statement. I was just thinking that if you could feed it 60-70°F air in the winter, it would be more efficient.

    No offense intended.

    GT
    There has always been an interesting technical argument concerning the installation location of these heat pump HW tanks. If installed inside such as the basement or laundry room even with an exhaust that room get cold due to the air conditioning effect of these systems causing many home owners to complain. I've had my share of these calls.

    If installed in the garage then the loss of "free heat" as some call it is defeated cause it's mainly in outside air. The only benefit I tell my customers is that when you pull you car in the garage and close the garage door the hot car gives off lots of "free heat" that can then be used by the heat pump...if it's calling for heat.
    "The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
    - Alexis de Toqueville, 1835

  12. #11
    Join Date
    Jan 2014
    Location
    Southwest Iowa
    Posts
    109
    Post Likes
    Just finished an install/service 3 day class in Topeka last week for geo systems. My house burnt in '09 and I have it built again but am taking time. I built a 1200sqft cabin, now is time for my hvac installation but before I do that, i'm considering off grid power supply, solar and wind. Ideas and thoughts are welcomed.

  13. Likes Ben14 liked this post.
  14. #12
    Join Date
    Feb 2009
    Location
    Portland OR
    Posts
    2,620
    Post Likes
    Quote Originally Posted by GT Jets View Post
    Really not trying to be an ass. but no, it doesn't.

    They can be indoors and only the exhaust air needs to go outside... The manual says in plain English that the temperature range is 20-120°F. It was only because of the 20°F comment that I made the earlier statement. I was just thinking that if you could feed it 60-70°F air in the winter, it would be more efficient.

    No offense intended.

    GT
    So where do you get 60-70 degree air from in Seattle in the winter? If your answer is inside the house then where does that heat come from? There is no benefit unless outside air is being used. I HATE heat pump water heaters because about 90% are installed wrong. If it's in a conditioned space, it will never get more than a 1 COP, regardless of its it vents to the outside. If it's a conditioned space and vents out then where does the conditioned space replace its air from? Outside! So now you use your primary heat source to heat outside air so your water heater can use the heat? Bunch of BS, unless you can put it in a garage in Arizona that brings in outside air, it cools the garage in the summer and there is usually enough heat in the air in the winter for a 1.5 to 2 COP.
    Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
    Like us on FACEBOOK if you like our advice here!

  15. #13
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,398
    Post Likes
    Quote Originally Posted by SkyHeating View Post
    So where do you get 60-70 degree air from in Seattle in the winter? If your answer is inside the house then where does that heat come from? There is no benefit unless outside air is being used. I HATE heat pump water heaters because about 90% are installed wrong. If it's in a conditioned space, it will never get more than a 1 COP, regardless of its it vents to the outside. If it's a conditioned space and vents out then where does the conditioned space replace its air from? Outside! So now you use your primary heat source to heat outside air so your water heater can use the heat? Bunch of BS, unless you can put it in a garage in Arizona that brings in outside air, it cools the garage in the summer and there is usually enough heat in the air in the winter for a 1.5 to 2 COP.
    Dude,

    Don't take it so personal...

    My simple statement was that if you are in a 20°F environment, having it in the garage is foolish. Why store your HOT water in a 20°F space? You lose quite a lot of the heat you just spent a long time trying to generate. Add to that, in a 20°F space, the heater will have to go into a defrost, would not have to in a 60°F space. You seem to be ignoring the fact that the duty cycle on this device will be quite low, especially when the storage tank is in a space only 30° cooler than the tank.

    All I was trying to say is that if it were in a utility closet fed by the warm zone, the heater would be more efficient than if in a 20°F garage (even though I know the OP was just using the 20°F comment as an extreme example). Your clothes dryer will use about the same amount of air...

    Chill. It was just an observation. Don't get so serious.

    I plan on having the remote condenser to my refrigerator and the ground source heat pump all in the same mechanical area and keep all heavy electrical users near each other, it will back up to the laundry area/mudroom. That was all I was saying.

    BTW, if you have a house in Arizona and you don't have solar water heat, you are a sufferer of mental instability.

    Relax.

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  16. #14
    Join Date
    Feb 2009
    Location
    Portland OR
    Posts
    2,620
    Post Likes
    Sorry GT, didn't mean for that to come off towards you, its our utility down here, they incentivize improper installation. They tell people with baseboard electric to put them in a conditioned space, in which case the baseboard is really heating the air, so it has a zero net benefit and they give away tax dollars to do it. When i asked them where the heat comes from they told me "from the space around the water heater" and I said ok so thats heated by baseboard, they said "ya" and I said so if you exhaust the air into the room, what reheats the air and they said "the resitance heat which is why this one is approved because it vents outside" So I told them, then where does the makeup air come from that goes outside "uhh, what do you mean" well if you take 100 CFM's out of the house it will pull 100 CFM's of outside air back in which then gets heated by baseboard so it doesn't help "no thats wrong because the heat pump uses warm air to heat the water"
    So it was the stupidity of the tax credits that I as a taxpayer and rate payer in Oregon have to pay into, because some analyst only thought one dimensionally.
    Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
    Like us on FACEBOOK if you like our advice here!

  17. Likes Ben14 liked this post.
  18. #15
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,398
    Post Likes
    Quote Originally Posted by SkyHeating View Post
    Sorry GT, didn't mean for that to come off towards you, its our utility down here, they incentivize improper installation. They tell people with baseboard electric to put them in a conditioned space, in which case the baseboard is really heating the air, so it has a zero net benefit and they give away tax dollars to do it. When i asked them where the heat comes from they told me "from the space around the water heater" and I said ok so thats heated by baseboard, they said "ya" and I said so if you exhaust the air into the room, what reheats the air and they said "the resitance heat which is why this one is approved because it vents outside" So I told them, then where does the makeup air come from that goes outside "uhh, what do you mean" well if you take 100 CFM's out of the house it will pull 100 CFM's of outside air back in which then gets heated by baseboard so it doesn't help "no thats wrong because the heat pump uses warm air to heat the water"
    So it was the stupidity of the tax credits that I as a taxpayer and rate payer in Oregon have to pay into, because some analyst only thought one dimensionally.
    Anytime I see the terms "government funded" or "government incentive" my head nearly explodes. Since when does the government agencies have anybody smart enough employed to come up with such rules? Answer; They don't. Just pet projects by a bunch of lifetime politicians that couldn't have a clue if they had proper help.

    Smoke and mirrors.

    It should, if at all feasible, be installed in a mechanical closet with other heat generating equipment.

    Thank you for the reply. I meant no disrespect, I was simply trying to offer a better alternative, not start a "heated" debate. Please pardon the pun...

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  19. Likes Ben14 liked this post.
  20. #16
    Join Date
    Feb 2016
    Posts
    1
    Post Likes
    Advice please:
    If this were a bicycle tire, I'd know whether and how to patch a punctured inner tube. I'd also know when a patch wouldn't be enough, and replacement would be advisable. Also I'd know whether to replace the tire too. However my problem is a leaky, complex, expensive water heater, so your advice would be very helpful!

    I purchased an Air Generate ATI66 heat-pump water heater for my home, but the inner, stainless steel tank leaks (diagnosed by a plumber very familiar with heat-pump type water heaters). Since the manufacturer went out of business, the "Lifetime Limited Warranty" is void. Any advice?
    1. See if I can get a qualified person to repair the leak?
    2. Try to find a tank from another ATI66 to replace mine?
    3. Get rid of the ATI66, and buy a less expensive, probably less efficient but reliable water heater from a company that has been around for years?
    BTW, this is not a quiet machine, as was advertised.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •