  1. #81
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    At least not the orange pumpkins, with rotolocks.

  2. #82
    Join Date
    Oct 2005
    Location
    USA
    Posts
    615
    Post Likes
    Prolly a recip compressor your installing. I believe it's just another port to your suction side of the compressor. You can either braze it shut or braze a fitting on so u can gauge up there.
    RTFM!!!

  3. #83
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    The old Tranes are a GE design. Many of those compressors are similar to later Trane compressors, and look like a large inverted acorn. Not your typical Bristol recip.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  4. #84
    Join Date
    Jul 2009
    Location
    new york
    Posts
    928
    Post Likes
    Thread Starter
    Update on using 5ton compressor. The old compressor was 7.5 and we replaced with 5 ton and used same txv used for 7.5 ton and also used 422d instead of r-22. The system works great as all was need was a temp to 68-65 and the running compressor on a 90 degree day got the rooms down to 69. It seemed when I was charging system which called for 14 pounds I have to charge 17 pounds and finally stopped after an hour with superheat of 13.6 degrees. I was thinking it would have taken less refrigerant

  5. #85
    Join Date
    Jan 2010
    Location
    Heat Pump Belt
    Posts
    92
    Post Likes
    Quote Originally Posted by timebuilder View Post
    One more thing.

    Confirm voltage using my recommended method before you replace anything.

    One possibility is that you are missing a phase, and you are reading the voltage through a winding from another leg.

    Confirm all three 460 phases by using the steps I outlined above. First check the line side of the contactor and then the load side while the contactor is energized.

    Let's keep the electrical stuff in the closed areas, like Pro Commercial next time.
    Just reading through.. My thoughts exactly!! I maybe not pro but have seen that before.

+ Reply to Thread
Page 5 of 5 FirstFirst 12345

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •