Thread: Odd control voltage

  1. #21
    Join Date
    May 2014
    Location
    Springfield , IL
    Posts
    14
    Post Likes
    Thread Starter
    No hostility here, just trying to figure out a problem that has me stumped. I'm actually a pretty laid back guy and I apologize if I came off as rude or aggressive.

  2. #22
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by coltswin88 View Post
    I agree, I am new to this and still have a lot to learn. Another tech from a different company had been out there before me and couldn't fix the problem. I just corrected some pretty obvious errors ( r and g wired together, no neutral going from the gas valve to the secondary side of the transformer) As far as the voltage goes, I've gone to a couple bad transformer calls and yes, when they fry they usually fry open on one side or the other. I took the readings from the wires to a the grounded, non-painted internal casing of the furnace. So yes, it might be some problem with the tstat, but it is making connections.
    This is not how you take proper voltage readings.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. #23
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    If your 120 supply is good, then take the secondary wires off of the xformer and check the voltage. If you have 24 volts, then you have a short in the low voltage wiring.

  4. #24
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by coltswin88 View Post
    No hostility here, just trying to figure out a problem that has me stumped. I'm actually a pretty laid back guy and I apologize if I came off as rude or aggressive.
    I think he was referring to me. I come across as a dick sometimes
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  5. #25
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    Quote Originally Posted by 2sac View Post
    This is not how you take proper voltage readings.
    wow...you guys are harsh..

    What 2sac is saying, is that you should be measuring between the hot leg and the neutral, to get the line voltage. If the furnace is not grounded properly, you wont get correct readings. Measuring to ground is more useful on three phase equipment.

  6. #26
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes

    Odd control voltage

    Quote Originally Posted by 2sac View Post
    I think he was referring to me. I come across as a dick sometimes
    Sometimes...? : D

    What you said though, check control voltage to common and as Harper said on line voltage. Although using the ground can work if present you aren't confirming if neutral is connected all the way to the way to the panel.

    Man if this is DIY he's gotten some good tips so far : ).

  7. #27
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    Quote Originally Posted by 2sac View Post
    I think he was referring to me. I come across as a dick sometimes
    LOL...

  8. #28
    Join Date
    May 2014
    Location
    Springfield , IL
    Posts
    14
    Post Likes
    Thread Starter
    The wiring diagram was lost to ages sometime ago. Most of the wiring was right but there were some obvious errors. The incoming power going into the unit was 120 and there was 120 at the transformer, fan relay and the blower itself. I checked the control voltage at the secondary side of the transformer and got 13v(checked to ground) and checked the tstat and still got 13v to the "O" terminal which was not used on the tstat

  9. #29
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    Quote Originally Posted by coltswin88 View Post
    The wiring diagram was lost to ages sometime ago. Most of the wiring was right but there were some obvious errors. The incoming power going into the unit was 120 and there was 120 at the transformer, fan relay and the blower itself. I checked the control voltage at the secondary side of the transformer and got 13v(checked to ground) and checked the tstat and still got 13v to the "O" terminal which was not used on the tstat
    What did you get checking both terminals on the secondary side, that's how you want to check it.

  10. #30
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    Check the xformer by itself, not with any wires on it. This will rule out line voltage and secondary issues. Then you can look into the wiring. What is most likely happening, is that the 24v line, is making contact with the common. This might be a rubbed through spot on a wire, or a relay that is wired wrong.

  11. #31
    Join Date
    Jun 2013
    Location
    N. Canada
    Posts
    878
    Post Likes
    [QUOTE]... I took the readings to ground and measured across them. 120 to ground, less than 1 across.[ /QUOTE]


    Key sentence here.



    Bet if you grnded the blower neutral it would run.

  12. #32
    Join Date
    Aug 2014
    Location
    DC suburbs
    Posts
    311
    Post Likes
    Quote Originally Posted by Joe Harper View Post
    If your 120 supply is good, then take the secondary wires off of the xformer and check the voltage. If you have 24 volts, then you have a short in the low voltage wiring.
    ^^^ This is what you should do next. You can just remove one wire but measure between the wires on the transformer, not ground.

  13. #33
    Join Date
    May 2014
    Location
    Springfield , IL
    Posts
    14
    Post Likes
    Thread Starter
    Thanks! I checked the ground on the power coming in and it looked fine to me which is why I took readings to the inside. The only part still confusing me is that why it would read so low, like I said earlier, I always thought that pretty much either transformers work or they don't. Unless its burned out in a unusual way, I don't see why it's do that. Also THIS IS NOT DIY! I graduated technical school and am epa certified so I'm not just some guy with a cheap meter and general knowledge.

  14. #34
    Join Date
    May 2014
    Location
    Springfield , IL
    Posts
    14
    Post Likes
    Thread Starter
    Thanks guys! I'm heading back out there in the am so I'll check it out tomorrow ! I have a lot to think about and hopefully I can get it fixed!

  15. #35
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Get your post count up to 15 and apply for professional membership. We can give you a lot more help once you're on the "other side". There are educational forums as well
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  16. #36
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    You will get to learn the secret handshake too!

  17. #37
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by Joe Harper View Post
    You will get to learn the secret handshake too!
    I've been shaking the wrong thing
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  18. #38
    Join Date
    May 2014
    Location
    Springfield , IL
    Posts
    14
    Post Likes
    Thread Starter
    Thank you. I wondered how to become a professional member. I'm really not some guy, I have the student loans and tool bag to back that up haha. Well anyway good night and I'll be on it tomorrow!

  19. #39
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    Quote Originally Posted by 2sac View Post
    I've been shaking the wrong thing
    And you wonder why they punch you on the subway....

  20. #40
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Put down your meter and answer my questions.
    What is the operating voltage listed on the motor ID tag or plate?
    What voltages are listed there on the motor?
    What FLA or RLA number is listed there?

    PHM
    ------

    Quote Originally Posted by coltswin88 View Post
    It needs 120v to operate. I checked the voltage to the fan relay and the blower itself. Both read 120v but the blower isn't operating at all. So I'm pretty confused between the blower not running and the low control voltage.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •