    Trane Tracer Summit v.11 to Tridium

    Any way (LON, BACNET, OPC, etc.) I can monitor a Trane Tracer Summit system from Tridium, SoftJACE or otherwise?

    Thanks!

  2. #2
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,780
    Post Likes
    Quote Originally Posted by kaz72 View Post
    Any way (LON, BACNET, OPC, etc.) I can monitor a Trane Tracer Summit system from Tridium, SoftJACE or otherwise?

    Thanks!
    I could be wrong, but...You can by using a JACE and mapping in the points you want via Bacnet from a BCU. I haven't done it yet, but I'm told it's not too hard.
    jogas

  3. #3
    Join Date
    Feb 2007
    Posts
    7
    Post Likes
    Thread Starter
    Quote Originally Posted by jogas View Post
    I could be wrong, but...You can by using a JACE and mapping in the points you want via Bacnet from a BCU. I haven't done it yet, but I'm told it's not too hard.
    jogas
    Recently I spoked to past Trane regional sales manager. He's indicating that Trane may need to be hired to map points in the local controller to be available via the BACnet access out of the BCU. Was hoping to avoid using Trane if possible.

  4. #4
    Join Date
    Oct 2003
    Location
    Hanging out in the brewhouse
    Posts
    820
    Post Likes
    Any AI,AO,BI and BO created in the Summit database will be broadcast via Bacnet/IP and the Jace will be able to see them.
    Beware of the prophet trying to make a profit.

    There is less oxygen from knee level to the floor! Check it out next time you tie your boots.

  5. #5
    Join Date
    Jun 2007
    Location
    Sydney, Australia
    Posts
    50
    Post Likes

    Wink Learn the BCU

    qtip is correct, using JDE (if using R2 Tridium) or AX quivalent you can learn the BCU and this will give you all the AI, AO, BO and BI. It is very straight forward. You should only need the Network ID used in the BCU which from memory defaults to 1.

    Regards

  6. #6
    Join Date
    Feb 2007
    Location
    Cullowhee, NC
    Posts
    30
    Post Likes
    These guys have you on the right track, I have done the same thing on a college campus with a Tridium and Summit 16 system. However, not all points in Summit are created as Bacnet objects, a lot are points in devices without object IDs. For these, you can just create the appropriate (AI, BO, etc) object in the BCU and then Tridium willl pick them up on Bacnet. Let us know how it works!

  7. #7
    Join Date
    Dec 2007
    Posts
    89
    Post Likes
    You will need to create points that have not already been created as AI AO BO BI, THis is due to the proprietary points, they are not broadcast as bacnet points, but instead comm 3, comm 4, or Lon. I would pull points into the Jace and then see if you are getting what You want. You however will need some one with summit access, to create the points and map them in. If there is a summit work station on site you can do this your self. Good luck it is not hard to pull it into the Jace using AX, the Jace sometimes is tricky getting all the settings to take, but once you do it works good.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •