    sealright hoses

    I foolishly bought a couple sets of these hoses years ago when I was still in school. Never realizing that they aren't recommended for use with 410a.

    I actually really like the hoses; but they basically all started to leak at the sealright ends.

    I went to the yellow jacket website, and I noticed that the disclaimer about not using the hoses with 410a was gone, and if I'm not mistaken, a new bullet point about the seals being resistant to deterioration from all existing refrigerants and oils.

    Does this mean if I buy the rebuild kits I can expect to see much more durability in the field? Or have I made an incorrect assumption and I just need to purchase some ball valve hoses?

  2. #2
    Join Date
    Mar 2014
    Location
    ohio
    Posts
    23
    Post Likes
    ive had problems with these as well, switched to ball valves and like them better. if its been years tho isn't it fair to say that you would have to replace the o rings from normal wear and age anyways tho? also eventually the ball valves start leaking around where they crimp to the hose, so I would say stick with those if you prefer them.

  3. #3
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Thread Starter
    Quote Originally Posted by ggg333 View Post
    ive had problems with these as well, switched to ball valves and like them better. if its been years tho isn't it fair to say that you would have to replace the o rings from normal wear and age anyways tho? also eventually the ball valves start leaking around where they crimp to the hose, so I would say stick with those if you prefer them.
    Well, I've owned one set since 2008, and then bought another set in 2012. they really weren't put into use until I started in the trade in late 2012. I can accept the older set being dry rotted or something of that nature. They started leaking after daily use for about 9 months I'd say.

    I use them for all refrigerants, 22, 410a, 134a, 404a, etc., so I figured that was my main issue since yellow jacket had that little disclaimer about 410.

    Sent from my DROID BIONIC using Tapatalk

  4. #4
    Join Date
    Feb 2011
    Location
    Tecumseh, ON
    Posts
    143
    Post Likes
    They always leak at the most inopportune time, pressure tests and pulling vacuum!

  5. #5
    Join Date
    Mar 2014
    Location
    ohio
    Posts
    23
    Post Likes
    Quote Originally Posted by shellkamp View Post
    Well, I've owned one set since 2008, and then bought another set in 2012. they really weren't put into use until I started in the trade in late 2012. I can accept the older set being dry rotted or something of that nature. They started leaking after daily use for about 9 months I'd say.

    I use them for all refrigerants, 22, 410a, 134a, 404a, etc., so I figured that was my main issue since yellow jacket had that little disclaimer about 410.

    Sent from my DROID BIONIC using Tapatalk
    its possible...was the warning for 410a or for poe oils? if deteriation from oil is the issue I would have thought they would warn against poe, the oil used in 410a and other newer refrigerant systems. what pressures were they rated for? maybe they were not suitable for 410a due to them not being rated for the higher pressures, and that was the issue?

  6. #6
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Thread Starter
    Quote Originally Posted by ggg333 View Post
    its possible...was the warning for 410a or for poe oils? if deteriation from oil is the issue I would have thought they would warn against poe, the oil used in 410a and other newer refrigerant systems. what pressures were they rated for? maybe they were not suitable for 410a due to them not being rated for the higher pressures, and that was the issue?
    I specifically remember the warning being for 410a, with no mention of oil. The hoses themselves are rated for 800psi operating pressure and 2000psi burst pressure. Or maybe that was 2000psi operating and 8000psi burst. I can believe the fittings not liking that high of a pressure, but based on how mine are leaking, its more on how the spring re-seats itself; which I feel would be a failure different from that of a pressure related failure.

    They really only leak most of the time, not all of the time <g>

    I was hoping a yellow jacket representative would chime in with some wisdom on the subject, but perhaps they only operate on these forums during business hours.

    Sent from my DROID BIONIC using Tapatalk

  7. #7
    Join Date
    Jan 2014
    Location
    Bloomington, MN
    Posts
    148
    Post Likes

    R-410 Designation Change on YELLOW JACKET SealRight Hose

    We used to designate our SealRight Couplers as "not recommended for R-410A systems" because our recommended low-loss hose fitting for R-410A systems is our compact ball valve hose. It is easy to connect to the system port with an adjustable valve opener, and the flow through the hose can be controlled at any time with a simple quarter-turn of the ball valve.

    The use of our PLUS II Hoses with SealRight fittings is an acceptable substitute for R-410 system. R-410A pressures can make this valve a little more difficult to open and close, but when compared to others on the market, we feel ours is the easiest to actuate. This is due mainly to the larger diameter, heavily knurled nut on the SealRight coupler. It also has a higher vapor/liquid refrigerant and evacuation flow rate, depresses valve cores farther, and is part of a UL Recognized hose assembly.

  8. #8
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Thread Starter
    Quote Originally Posted by YELLOW JACKET View Post
    We used to designate our SealRight Couplers as "not recommended for R-410A systems" because our recommended low-loss hose fitting for R-410A systems is our compact ball valve hose. It is easy to connect to the system port with an adjustable valve opener, and the flow through the hose can be controlled at any time with a simple quarter-turn of the ball valve.

    The use of our PLUS II Hoses with SealRight fittings is an acceptable substitute for R-410 system. R-410A pressures can make this valve a little more difficult to open and close, but when compared to others on the market, we feel ours is the easiest to actuate. This is due mainly to the larger diameter, heavily knurled nut on the SealRight coupler. It also has a higher vapor/liquid refrigerant and evacuation flow rate, depresses valve cores farther, and is part of a UL Recognized hose assembly.
    Thank you for responding. I decided to invest in repairing my hoses, and all but a couple are back to their former glory. I just need to order a few more seal kits.

    Sent from my Torque using Tapatalk

  9. #9
    Join Date
    Jul 2011
    Location
    miami
    Posts
    5
    Post Likes
    tried to purchase the rebuild kits for sealrite adapters,yj oil injector o rings,washers for yj hoses the local supply places are not eager to assist,they want to push new, need info where else i can purchase them called yj local office not helpful at all yup in s fla

  10. #10
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Thread Starter
    Quote Originally Posted by gene_kan View Post
    tried to purchase the rebuild kits for sealrite adapters,yj oil injector o rings,washers for yj hoses the local supply places are not eager to assist,they want to push new, need info where else i can purchase them called yj local office not helpful at all yup in s fla
    I always had a tough time finding the parts in the supply houses. There's just no demand for them so the parts guys don't keep more than one or two laying around it seems. Look up the yellow jacket part numbers from the website and order them from Amazon.

    Sent from my DROID BIONIC using Tapatalk

  11. #11
    Join Date
    Jun 2013
    Location
    Central Florida
    Posts
    813
    Post Likes
    Quote Originally Posted by gene_kan View Post
    tried to purchase the rebuild kits for sealrite adapters,yj oil injector o rings,washers for yj hoses the local supply places are not eager to assist,they want to push new, need info where else i can purchase them called yj local office not helpful at all yup in s fla
    I assume you're speaking of the 69562 oil injector? I've always gotten o-rings for my sealrights at Home Depot; I found a kit with assorted green o-rings at Advance Auto. Works as well as the original. Actually, maybe better.

    Any parts house that doesn't have several packets of the hose gaskets on hand is just a pi$$ poor parts house, especially in S FL.

    When a supply house says "We don't have that", the next words out of their mouth should be, "But, we can get it for you". If not, they've lost me as a patron.
    JUST A LITTLE CLOSER AND THE LITTER BOX IS ALL MINE!

  12. #12
    Join Date
    Jan 2014
    Location
    Bloomington, MN
    Posts
    148
    Post Likes
    Gene, please respond with your zip code and we'll see if there are any suppliers in your area who have the rebuild kits in stock. The part numbers can be found on this page - click on the UPC tab and page the bottom: www.yellowjacket.com/product/727.

  13. #13
    Join Date
    Feb 2014
    Location
    Eugene
    Posts
    27
    Post Likes
    From my experience the newer low loss YJ hoses are terrible the older hoses would even hold a vacuum

  14. #14
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Thread Starter
    Quote Originally Posted by hvacguyfrmor View Post
    From my experience the newer low loss YJ hoses are terrible the older hoses would even hold a vacuum
    What's the date threshold for your claim? I just rebuilt my hoses that were from 2008 and another set from 2012 and both sets held a vacuum when I tested that. Didn't throw a micron gauge on them, but I did perform the ol' listen for the pump to change sounds trick. I don't use them for pulling a vacuum anyways.


    Sent from my DROID BIONIC using Tapatalk

  15. #15
    Join Date
    Jul 2011
    Location
    miami
    Posts
    5
    Post Likes

    33162 that's the zip

    Quote Originally Posted by YELLOW JACKET View Post
    Gene, please respond with your zip code and we'll see if there are any suppliers in your area who have the rebuild kits in stock. The part numbers can be found on this page - click on the UPC tab and page the bottom: www.yellowjacket.com/product/727.
    33162 that's the zip

  16. #16
    Join Date
    Oct 2004
    Location
    Yakima, WA
    Posts
    1,847
    Post Likes
    I have always used the seal-right adapter on a standard hi-side hose with good results, and I carry a spare. The most common failure is just the o-ring, and fortunately we have a local supplier that keeps them in 10-packs right next to the packs of regular hose gaskets.

    Usually when the valve itself pukes I have found that the seal has just come unseated - pull it apart, shove everything back home, and it's good for another 100,000. I have put the rebuild kit in once or twice, though.

    The biggest thing for me is that the valve never sees over 400 psi when going on or off - I'll bleed back through the low side as I'm pulling my high side hose off if I need to.

  17. #17
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Thread Starter
    Quote Originally Posted by cjpwalker View Post
    I have always used the seal-right adapter on a standard hi-side hose with good results, and I carry a spare. The most common failure is just the o-ring, and fortunately we have a local supplier that keeps them in 10-packs right next to the packs of regular hose gaskets.

    Usually when the valve itself pukes I have found that the seal has just come unseated - pull it apart, shove everything back home, and it's good for another 100,000. I have put the rebuild kit in once or twice, though.

    The biggest thing for me is that the valve never sees over 400 psi when going on or off - I'll bleed back through the low side as I'm pulling my high side hose off if I need to.
    What are you working on that your hoses see 400psi? The discharge line of a 4 seer 410a unit?

    Sent from my DROID BIONIC using Tapatalk

  18. #18
    Join Date
    Oct 2004
    Location
    Yakima, WA
    Posts
    1,847
    Post Likes
    Quote Originally Posted by shellkamp View Post
    What are you working on that your hoses see 400psi? The discharge line of a 4 seer 410a unit?

    Sent from my DROID BIONIC using Tapatalk
    No... 13 seer or better. 95 or 100 degrees outside in cooling, or a mild to warm day in heating...

  19. #19
    Join Date
    Jan 2014
    Location
    Bloomington, MN
    Posts
    148
    Post Likes

    Marketing Communications Manager

    You should be able to purchase our SealRight rebuild kits at the following wholesalers in your area:

    TROPIC SUPPLY
    SUNRISE FL 33323954/835-6010

    1001 SAWGRASS CORPORATE PKWY


    JOHNSTONE SUPPLY #36FT. LAUDERDALE FL 33309 954/971-9350
    5620 NW 12TH AVESTE 101
    Last edited by YELLOW JACKET; 05-12-2014 at 12:39 PM. Reason: add some text

  20. #20
    Join Date
    Jan 2014
    Location
    Bloomington, MN
    Posts
    148
    Post Likes
    Quote Originally Posted by gene_kan View Post
    33162 that's the zip
    TROPIC SUPPLYSUNRISE FL 33323954/835-6010
    1001 SAWGRASS CORPORATE PKWY



    JOHNSTONE SUPPLY #36FT. LAUDERDALE FL 33309 954/971-9350
    5620 NW 12TH AVESTE 101

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •