    Refrigeration System Analyzer Problems

    I bought a YJ analyzer last year and im having a couple problems with it.
    1. It will not turn off. If you try to power it off it will only reset. I either have to pull the power pack or let it time out.
    2. The hi and low sides always show inHg when I turn it on which throws off my diagnosis a bitand I can't find a way to zero the unit out.
    Any help would be greatly appreciated.

  2. #2
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    8,096
    Post Likes
    Did you buy it new?

  3. #3
    Join Date
    Mar 2014
    Location
    Palatine, Illinois, United States
    Posts
    17
    Post Likes
    Thread Starter
    Yes from Johnstone Supply last August

  4. #4
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    8,096
    Post Likes
    Should still be under warranty. Take it back to Johnstone, they should be happy to help you.

  5. #5
    Join Date
    Dec 2009
    Location
    Upstate, South Carolina
    Posts
    246
    Post Likes
    To turn it off you have to hit the top of the power button

  6. #6
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    1,021
    Post Likes
    Hit menu and set up then scroll to zero out at bottom

  7. #7
    Join Date
    Oct 2012
    Location
    Where we mow our own grass
    Posts
    6,673
    Post Likes
    Quote Originally Posted by IceWhiteice View Post
    To turn it off you have to hit the top of the power button
    YES! This is true, it took me a while to get the hang of that.

  8. #8
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,705
    Post Likes
    Did you try changing the batterys?

  9. #9
    Join Date
    Aug 2013
    Location
    Tennessee
    Posts
    113
    Post Likes
    New software update I have the same product call yellow jacket tech support they email the file and Wala shut down option in main menu

  10. #10
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,705
    Post Likes
    Quote Originally Posted by jason2117 View Post
    New software update I have the same product call yellow jacket tech support they email the file and Wala shut down option in main menu
    NO, battery. I called it. I want my prize too. Lol, if it was a software issue they would update.

  11. #11
    Join Date
    Aug 2013
    Location
    Tennessee
    Posts
    113
    Post Likes
    I meant for the power off problem i have never seen the other issue on my set

  12. #12
    Join Date
    Sep 2010
    Posts
    2
    Post Likes

    YJ 40812 Vacuum gauge calibration

    I have the YJ Analyzer which is a few years old, works fine, but I rarely used the vacuum gauge. Was doing an install over the weekend and was using my YJ 69075 and decided to compare the two. The readings were way off, so I connected both the Analyzer, YJ 69075 and my Hastings VT-4 to a 1/4" Cu tube manifold on the Vac pump connection. the Hastings and the YJ 69075 were fairly close, but the Analyzer was way off. I recorded the readings of each of the three meters in the attached file. Anyone ever had the Analyzer vacuum calibrated, or can the vacuum sensor be recalibrated?

    Vacuum gauge test 20140714.pdf
    Attached Images Attached Images
    Last edited by Rolled Flare; 07-14-2014 at 09:21 PM. Reason: graphs labeled wrong

  13. #13
    Join Date
    Mar 2017
    Posts
    48
    Post Likes
    Have the analyzer issues been ironed out. Im thinking of buying one of these.