    Feb 2014
    S4 Group VS Field Server
    Thoughts on what is better for N2 integration?
    S4Group
    http://www.thes4group.com/building-a...cnet-n2-router
    Or Field Server
    http://www.fieldserver.com/products/...Metasys_N2.php
    Apr 2005
    2444 Washington Blvd, Suite 100 Ogden, UT
    Let me know if you need any additional information about the S4 Products. You'll find that each product has a sweet spot depending on the size and complexity of your project.
    Steve Jones, Managing Partner, The S4 Group, Inc.
    Do you know BACnet? Visit https://www.bacnetinternational.org/ or ask me for information.
    Hello,
    I've done several jobs with fieldserver (JCI N2\MSTP to OPC, modbus, MSTP) and the only thing which I have to input, is the work that is requried on the configuration file.
    They always say that it's PNP, but you need to configure that sucker. The tools are free, and once it's pretty simple once you look into it.
    It's recommend to obtain tech support cost (I think it was 500) as it's worth every penny when it doesn't work and you need to change things.
    Apr 2005
    Top 10 Reasons to use the S4 Open : BACnet-N2 Router
    1. The N2 Router supports any N2 device that you will find on a N2 bus including N2 Open, VMA, Vendor Devices, Metasys Integrator, and Centaurus Integrator; direct Read, Write, Override, and Release transactions for any point limited only by the programming in the N2 device.
    2. The Upstream Interface enables the co-existence with the Metasys® head end. This is a key feature in cases where minimal (or zero!) down time is mandated.
    3. Auto discovery and configure wizard, facilitated by our robust library of Device Type Templates which predefine point mapping for each Metasys® device and application (custom templates can also be generated from Metasys® resource files) – all minimize the man hours required to integrate your N2 devices to BACnet.
    4. Use all of the features of HVAC Pro and GX-9100, including uploading and downloading devices. The N2 Router can provide a replacement for the Metasys® "Passthrough" option for the configuration and commissioning utilities.
    5. In buildings with older, and potentially less reliable, N2 devices, the BACnet-N2 Router automatically resets N2 devices when multiple retries of an operation fail; it also logs the number of times that this action is taken.
    6. The N2 Router products expose all N2 device points to the new head end, even those that JCI doesn’t normally expose to their operator workstation, such as tuning parameters.
    7. The N2 Router products work independently of any database, priority, or security settings in the Metasys® supervisory controller.
    8. The N2 Router products establish a very cost effective gateway to BACnet IP in the short term, quickly adding value and extending the life of legacy systems. Facilitates the migration away from Metasys® N2 devices in the longer term.
    9. The N2 Router can force the N2 data stream from legacy Metasys® supervisory controllers (NCM, for instance) to participate in the BACnet priority array mechanism, giving the integrator complete control over which head end is commanding each point. No other product has this "supervisory controller as a BACnet client" capability.
    10. Publish each N2 device as its own BACnet device within a virtual BACnet network.
    On the bay fishing
    Looks like S4 it is.
    Beware of the prophet trying to make a profit.
    There is less oxygen from knee level to the floor! Check it out next time you tie your boots.