    Question New Lennox XC14 + SLP280UHV with Nest

    Hello HVAC-Talk Community!

    I have been reading/learning for the past month - great information here and the knowledge provided by professionals is incredible - thank you!!

    New install completed Friday:
    - 2 stage variable speed gas furnace (indoor)
    - 1 stage a/c condenser (outdoor)

    I have been using the Nest with my previous 20+ year old furnace. I have the following wires connected at the Nest:
    Y1, W1, G, Rh

    This has been working well for me with my previous furnace (single stage only).

    Now that I have a new 2 stage variable speed furnace (which I understand the Nest will support 2 stage furnace but does not have direct control over fan speed), did my installer technician cut a corner by only wiring W1 and connecting a jumper to W2?

    When heat kicks on I am pretty certain it is only using Heat Stage 2 (I can read the Lennox LED panel and it shows the H2 value and I have never seen it show an H1 value unless the W1/W2 jumper gets removed).

    Thanks in advance for your help!
    Scott

    Name:  furnace.JPG
Views: 3491
Size:  83.2 KBName:  tstat.JPG
Views: 3124
Size:  152.8 KB

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    This is not a DIY forum, but you would be better off not trying to use that NEST stat with your current system.
    Training is important!
    Practical Training is a must!

  3. #3
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    It could be wired for thermostat control of both stages of heat.

    If you want to keep your Nest, you really should have them pull a new wire so that both stages of heat can be connected, as well as the common.
    Power robbing type thermostats can sometimes cause odd behavior in equipment with variable speed blowers.

    I'd recommend replacing the Nest with a Honeywell Prestige IAQ, or Ecobee Smart thermostat.
    You would not need to have a new thermostat wire pulled, both are better comfort controls than the Nest, and are much higher quality.
    IMO, unless your house is some kind of modern or Industrial decor, they look better than the Nest too.

  4. #4
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    I see he did not use the blue wire. There is your issue. But I would use a different stat to get the most out of your system.


    The future isn't what it use to be.
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  5. #5
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by mark beiser View Post
    It could be wired for thermostat control of both stages of heat.

    If you want to keep your Nest, you really should have them pull a new wire so that both stages of heat can be connected, as well as the common.
    Power robbing type thermostats can sometimes cause odd behavior in equipment with variable speed blowers.

    I'd recommend replacing the Nest with a Honeywell Prestige IAQ, or Ecobee Smart thermostat.
    You would not need to have a new thermostat wire pulled, both are better comfort controls than the Nest, and are much higher quality.
    IMO, unless your house is some kind of modern or Industrial decor, they look better than the Nest too.
    +1

  6. #6
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    also, I am fairly secure in saying that jumper from Y1 to Y2 is unnecessary.

    NEST has been well marketed but real world operations are less than stellar. As has been stated, other thermostats are better at PROPERLY controlling HVAC equipment.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  7. #7
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by pacnw View Post
    also, I am fairly secure in saying that jumper from Y1 to Y2 is unnecessary.

    NEST has been well marketed but real world operations are less than stellar. As has been stated, other thermostats are better at PROPERLY controlling HVAC equipment.
    Nest says in their install instructions specifically NOT to jumper the outputs.

  8. #8
    Join Date
    Jan 2014
    Location
    Austin, TX
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by pacnw View Post
    also, I am fairly secure in saying that jumper from Y1 to Y2 is unnecessary.

    NEST has been well marketed but real world operations are less than stellar. As has been stated, other thermostats are better at PROPERLY controlling HVAC equipment.
    Hi pacnw - The HVAC technician wired a jumper from W1 to W2 on the furnace controller. (as per pic).
    Name:  furnace.JPG
Views: 2545
Size:  83.2 KB
    As a result the furnace runs at stage2 all the time. It has been identified in this thread that this wiring setup will be a problem for running the furnace at stage1.

    As you can see from the Nest tstat pic, there are no jumpers on the Nest wiring:
    Name:  tstat.JPG
Views: 2529
Size:  152.8 KB

    Thank you all for your suggestions on thermostats. We're going to run with the Nest for now and research some better alternatives.

    Thanks,
    Scott

  9. #9
    Join Date
    Jan 2014
    Location
    Austin, TX
    Posts
    4
    Post Likes
    Thread Starter
    The HVAC tech came back to remove the W1-W2 jumper from the furnace control board and used the existing blue common wire as the W2 line. Connected the same at the tstat and 2 stage heating is confirmed now.

    The question then becomes: what do I lose by not having common? I am not using any additional humidifier or aux heat equipment. I am pretty sure the common was NOT wired on the furnace with my previous configuration. I definitely did not use common at the Nest previously.

    thanks!
    Scott

  10. #10
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    Quote Originally Posted by sedeuce View Post

    Hi pacnw - The HVAC technician wired a jumper from W1 to W2 on the furnace controller. (as per pic).
    <img src="http://hvac-talk.com/vbb/attachment.php?attachmentid=456971"/>
    As a result the furnace runs at stage2 all the time. It has been identified in this thread that this wiring setup will be a problem for running the furnace at stage1.



    Thanks,
    Scott
    That depends if he set the control board up a single stage thermostat or a two stage. If it set to operate on a single stage thermostat then the control board in the furnace will bring on first stage then bump up after a time.

  11. #11
    Join Date
    Jan 2014
    Location
    Austin, TX
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by martyinlincoln View Post
    That depends if he set the control board up a single stage thermostat or a two stage. If it set to operate on a single stage thermostat then the control board in the furnace will bring on first stage then bump up after a time.
    The installer left the dip switch as default (off), which on the Lennox controller board means that it is configured for 2 stage tstat.

  12. #12
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    Call him back then and ask why they're not using that blue wire for w2.

  13. #13
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Keep in mind Nest "stages up" but doesn't stage down. Not sure it's any better than just using the timer built into the furnace.

  14. #14
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    Quote Originally Posted by sedeuce View Post
    Hi pacnw - The HVAC technician wired a jumper from W1 to W2 on the furnace controller. (as per pic).
    Name:  furnace.JPG
Views: 2545
Size:  83.2 KB
    As a result the furnace runs at stage2 all the time. It has been identified in this thread that this wiring setup will be a problem for running the furnace at stage1.

    As you can see from the Nest tstat pic, there are no jumpers on the Nest wiring:
    Name:  tstat.JPG
Views: 2529
Size:  152.8 KB

    Thank you all for your suggestions on thermostats. We're going to run with the Nest for now and research some better alternatives.

    Thanks,
    Scott
    You may want to reread my post more carefully.

    I was referring to the cooling, Y1 and Y2 being jumpered together.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  15. #15
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    Quote Originally Posted by sedeuce View Post

    The question then becomes: what do I lose by not having common?
    thanks!
    Scott
    without a Common wire the stat becomes a power stealing/robbing type. this tends to lead to issues with some stats and definitely leads to issues with the NEST.

    again, NEST is something that is MARKETED to accomplish something that really is not necessary and can be accomplished by other products already on the market, most of the time less expensively.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •