Thread: Goodman heat pump defrost problem

  1. #1
    Join Date
    Nov 2002
    Posts
    95
    Post Likes

    Goodman heat pump defrost problem

    Goodman Model VSZ130630.
    Won't go into defrost. I shorted test pins on board. Compressor and Fan stop. Compressor comes back on but fan does not. Changed board. Same problem. Any ideas?

  2. #2
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by ralph View Post
    Goodman Model VSZ130630.
    Won't go into defrost. I shorted test pins on board. Compressor and Fan stop. Compressor comes back on but fan does not. Changed board. Same problem. Any ideas?
    Is it running in defrost mode when it comes back on?
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Is that the model that does the quiet shift into defrost.

  4. #4
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Sounds like quiet shift defrost to me. How long are you waiting for the fan to energize?
    Perhaps you should have read the instructions before calling.

  5. #5
    Join Date
    Nov 2002
    Posts
    95
    Post Likes
    Thread Starter
    In will not come back on at all. The compressor is off for about 30 seconds. I don't think reversing value shifts, but fan never does come back on.

  6. #6
    Join Date
    May 2003
    Location
    Sarasota. Fl
    Posts
    1,496
    Post Likes
    You did not wait long enough...
    It is the job of thinking people not to be on the side of the executioners.

    ~Albert Camus

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    May take 14 minutes before it will come out of defrost. the compressor will stop again, and then the compressor and fan will both start.

  8. #8
    Join Date
    Oct 2013
    Location
    Mobile, Alabama, United States
    Posts
    325
    Post Likes
    I suggest keep a cheap stopwatch. When waiting for something to happen, time goes by slow and i have found that this keeps me on track while waiting. Does not seem to take as long waiting.

    Sent from my DROID RAZR using Tapatalk

  9. Likes R600a liked this post.
  10. #9
    Join Date
    Nov 2002
    Posts
    95
    Post Likes
    Thread Starter
    why would the fan stop when the unit goes into defrost in the test mode??

  11. Likes bill labronte liked this post.
  12. #10
    Join Date
    Feb 2013
    Location
    north georiga
    Posts
    2,998
    Post Likes
    to build heat for defrosting the coil.
    Quote Originally Posted by ralph View Post
    why would the fan stop when the unit goes into defrost in the test mode??

  13. #11
    Join Date
    Nov 2002
    Posts
    95
    Post Likes
    Thread Starter
    I meant compressor, not fan. sorry

  14. #12
    Join Date
    Jan 2014
    Posts
    45
    Post Likes
    Sounds like maybe defrost sensor

  15. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by ralph View Post
    I meant compressor, not fan. sorry
    Quiet shift into defrost.

  16. Likes bill labronte liked this post.
  17. #14
    Join Date
    Jan 2014
    Posts
    45
    Post Likes
    Well then like was said maybe didn't wait long enough? Do u know anything bout buderus GB142

  18. #15
    Join Date
    Jan 2014
    Posts
    45
    Post Likes
    I haven't heard of that

  19. #16
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by Dennis-2 View Post
    Well then like was said maybe didn't wait long enough? Do u know anything bout buderus GB142
    lol, what?

    That defrost cycle is normal.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  20. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Dennis-2 View Post
    Do u know anything bout buderus GB142
    Not really.

  21. #18
    Join Date
    Jan 2014
    Posts
    45
    Post Likes
    No quiet shift! I'm dumb but I idn't stupid

  22. #19
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Dennis-2 View Post
    No quiet shift! I'm dumb but I idn't stupid
    Are you sure it doesn't have quiet shift.

    If it doesn't, what have you checked with a meter.

  23. #20
    Join Date
    Jan 2009
    Location
    Etters PA.
    Posts
    776
    Post Likes
    Sounds like a proper "quiet defrost" to me.

    Sent from my SPH-L720 using Tapatalk

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •